Samsung 5kW R32 Monobloc Gen 6 ASHP
In August 2022, we moved into our new two-bedroom house in Pembrokeshire. The bungalow, originally built sometime in the 1800s, was of solid stone construction. It had been extended in the 1970s with a new kitchen and front room featuring double breeze block construction with loose-fill insulation. The EPC was an optimistic C, but it did have 2.66 kW of solar panels on the highest FIT tariff.
I had installed a 5 kW Mitsubishi Ecodan ASHP in my previous house, a self-build from 2012, and wanted to use a heat pump again in this one. This property currently had a quite nice, newish gas combi boiler, but I knew I could reuse it in a rental property I owned.
I had been happy with the Mitsubishi and considered purchasing one again, but was tempted by the cheaper, newer, higher-temperature Samsung Gen 6, which I had heard good things about and seen that the controller was easier to set up. It also had some interesting communication options via Modbus.
I considered applying for the government grant, but for various reasons, decided to install it myself. It would be cheaper that way, and I was confident that I could do a better job than many of the installs I saw complaints about.
In preparation for the heat pump, I beefed up my loft insulation and ran my gas boiler at a low temperature to see where I needed radiator upgrades. I was able to shuffle radiators about to smaller bedrooms, purchasing only two very large radiators for the living areas. I also fitted a Mixergy hot water cylinder and MyEnergi Eddi solar diverter to enable us to have hot water once the gas combi was removed.
In February 2023, I bit the bullet and ordered my Samsung 5kw R32 Monobloc Gen 6 heat pump from The Heat Pump Warehouse. It arrived as promised, and I set about installing it with the help of some YouTube videos. In my previous house, I was frustrated that I could not monitor how my heat pump was performing, so I decided to stump up for an OpenEnergyMonitor system that would do the job.
Installation went relatively smoothly until it was time to switch it on. At this point, an error code popped up. After much frustration and fault-finding on a Sunday, I found the problem. The fan hadn't been plugged into the main circuit board. Needless to say, I was a bit miffed about this and later discovered that the heat pump had, in fact, been supplied by Joule, who denied all responsibility for the fault and even went so far as to accuse me of sabotaging it myself.

I encountered some other issues along the way, and these are described fully in my blog, The Greening of Rose Cottage, for those interested. The Samsung controller was used as the only thermostat for the system.
Once the heat pump was up and running, I set about adjusting the weather compensation settings to give us the appropriate heating temperature. We prefer 22C in the living rooms and cooler in the bedrooms. All thermostatic radiator valves were opened to their maximum, and the manual radiator valves were used to adjust flow. Further adjustments were made as the outside temperatures got colder later in the year. We tend only to heat the house during daytime hours.
The heat pump performed well, with heating SCOPs between 4.65 in September to 3.97 in December. After purchasing an electric vehicle and moving to the Intelligent Octopus tariff, I made the decision just to heat the water cylinder via the immersion heater at night for 7.5p/kWh and not to purchase a heat exchanger to enable it to be heated via the heat pump.

To complement the heat pump, I had an additional 4.65 kW of solar panels fitted, along with a 5kWh battery. This helps keep the electricity costs down greatly, and so far, bills have been lower than they would have been had we still been using gas. I expect to see a significant income from export in the summer months to help offset the costs of the improvements.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I'm super impressed with your initiative to self-install your system, and shocked in equal measure by Joule's sabotage accusation. That's really crazy. But kudos to you for seeing it through and getting it up and running.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Well done, impressed wish i could have done my own, spent years with the loans/grants fiasco never got a penny. I used an MCS, RECC, approved company, in 2014 still solving issues, had another Napit Inspector this month!!
As was I Mars. TBH the whole telephone conversation was bizarre, I was expecting at least an apology but got a full scale nuclear attack!
I have used a thin layer of an insulating lime render on one bedroom wall, more for damp control really and it is expensive. I aim to frame and insulate another wall with insulated plasterboards.
I'm curious how your measured SCOP compares to the "generated" and "consumed" energy totals reported by the Samsung itself? I have an oversized Gen6 Samsung 8.5kW in a super-insulated house (peak heat demand 3.3kW, which delivers an average generated / consumed ratio (SCOP?) of 2.75. This includes hot water use with legionella killing switched on. Very frustrating. I know it's crazy to have such a big HP, it came before the insulation before I knew the word "heatgeek", sized on the old EPC, and cycles like crazy! One cheer for the installer.
Sorry for the delayed reply, there was no notification of your question and I just happened across it. The Samsung COP is vastly less than my openenergy monitor COP. For example on the 27th Samsung reported 4.2 whereas OEM reported 5.2. Given the fact I am using a certified heat meter, I am confident it is Samsung that is wrong.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodySorry for the delayed reply, there was no notification of your question and I just happened across it. The Samsung COP is vastly less than my openenergy monitor COP. For example on the 27th Samsung reported 4.2 whereas OEM reported 5.2. Given the fact I am using a certified heat meter, I am confident it is Samsung that is wrong.
@bontwoody I don't have a heat meter, but I do have a MID-approved electricity meter measuring the consumption of the heat pump (heat pump only, so excludes MIM controller and pumps), and the Samsung reported figures are more than the MID meter, even allowing for pump usage, measured at 35W each (two pumps, 70W combined). I have to rely on the Samsung figures for generation to calculate (S)COP as that's all I have, but at least I know my electricity usage is low.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
I'm curious how your measured SCOP compares to the "generated" and "consumed" energy totals reported by the Samsung itself? I have an oversized Gen6 Samsung 8.5kW in a super-insulated house (peak heat demand 3.3kW, which delivers an average generated / consumed ratio (SCOP?) of 2.75. This includes hot water use with legionella killing switched on. Very frustrating. I know it's crazy to have such a big HP, it came before the insulation before I knew the word "heatgeek", sized on the old EPC, and cycles like crazy! One cheer for the installer.
Hi @Nick Owens, welcome to the forum.
My Samsung is the 12kW (gen6) model, and last winter my heat loss was just over 4kW on the coldest day... so welcome to the over-sized ASHP club!
I get reasonably good COPs by trying to extend run times using batch heating. You are never going to be able to run continuously low and slow, and the cycling will kill efficiency. I use an external room thermostat (FSV #2091/2) and run in "continuously on" mode (FSV 2093 = 1) to prevent the heat pump cycling, and then just try to extend run times. This does result in significantly more temperature fluctuation but we do achieve good COPs (currently over 5 on a heating run). At the moment we may run the heating for around 30-45mins and then turn off and allow the house to cool by 1-2C before another short batch of heating. We run with a flow temp of 32-33C at the moment, which is the minimum we can achieve in order for our radiators to be able to dissipate the 4kW plus of heat that is the minimum output of my ASHP.
So we can potentially just about achieve continuous running once the outside temp hits 0C, but as soon as the temp rising above freezing, we are cycling or switching off (and we only seek to heat to 20C)
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
-
Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
5 days ago
-
British Gas Heat Pump Installation Complaint
3 months ago
-
Heating Turned Off but Radiators Still Warm
3 months ago
-
Samsung Heat pump with Yonos Pico circulating pump running all the time
3 months ago
-
Vaillant AroTherm Plus 7kW
7 months ago
- 27 Forums
- 2,433 Topics
- 55.3 K Posts
- 418 Online
- 6,118 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help needed with Grant Aerona 3 issues
Just to update the thread, I now have a new heat pump!!...
By fleurcules , 49 minutes ago
-
RE: Is it normal to use power from the grid when running off the battery?
Well, the Huawei CT clamps I have are 100amp and 230V. ...
By Batpred , 3 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor condensate drain worries me, Ive wondered why t...
By Papahuhu , 4 hours ago
-
RE: A Smarter Smart Controller from Homely?
@johnnyb I think so. It’s a UPM4xL that takes its sp...
By Papahuhu , 5 hours ago
-
RE: A Single Voice for Heat Pumps, But Will It Finally Raise Industry Standards?
Great question - I don't know for sure, but I would ass...
By Mars , 6 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Actually, I came across the list of batteries that this...
By Batpred , 7 hours ago
-
RE: Say hello and introduce yourself
Hi all, my name is Julian, and I’m new to the forum. We...
By JLeyland , 7 hours ago
-
RE: Heat pump not reaching flow temperature
@davec that's good news! Thanks for sharing Dave.
By johnd , 8 hours ago
-
RE: Renewables & Heat Pumps in the News
@toodles this industry lacks accountability. That's one...
By Mars , 10 hours ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@prunusk I guess I was being generic with PV The pipe...
By HeyMikey , 15 hours ago
-
RE: Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
@jamespa previously it was so noisy, it was like hav...
By Papahuhu , 15 hours ago
-
RE: Running from backup generaor in powercut?
Fortuitously, I've just posted here on another topic ab...
By Transparent , 16 hours ago
-
The Myth of the MCS Performance Guarantee
As the editor of Renewable Heating Hub, I dedicate a si...
By Mars , 17 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Yes, I agree that the dearth of public knowledge of ene...
By Transparent , 17 hours ago
-
RE: UK Heat Pump Problems: A Complaint Process That's Irreparably Broken
Why do they not get replaced by NICEIC, assuming they w...
By Batpred , 1 day ago
-
RE: Volumiser required on Grant R290?
Bold move, and welcome to the forums @Patrick. I’ve h...
By Mars , 1 day ago
-
RE: R290 Heat Pump and Foundation Air Bricks
@l8again I agree fully, so what we would do is offer yo...
By ASHP-BOBBA , 1 day ago
-
RE: Setback savings - fact or fiction?
I agree, I have even been known to call some of the 'op...
By cathodeRay , 1 day ago