Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsung 5kW R32 Monobloc Gen 6 ASHP
In August 2022, we moved into our new two-bedroom house in Pembrokeshire. The bungalow, originally built sometime in the 1800s, was of solid stone construction. It had been extended in the 1970s with a new kitchen and front room featuring double breeze block construction with loose-fill insulation. The EPC was an optimistic C, but it did have 2.66 kW of solar panels on the highest FIT tariff.
I had installed a 5 kW Mitsubishi Ecodan ASHP in my previous house, a self-build from 2012, and wanted to use a heat pump again in this one. This property currently had a quite nice, newish gas combi boiler, but I knew I could reuse it in a rental property I owned.
I had been happy with the Mitsubishi and considered purchasing one again, but was tempted by the cheaper, newer, higher-temperature Samsung Gen 6, which I had heard good things about and seen that the controller was easier to set up. It also had some interesting communication options via Modbus.
I considered applying for the government grant, but for various reasons, decided to install it myself. It would be cheaper that way, and I was confident that I could do a better job than many of the installs I saw complaints about.
In preparation for the heat pump, I beefed up my loft insulation and ran my gas boiler at a low temperature to see where I needed radiator upgrades. I was able to shuffle radiators about to smaller bedrooms, purchasing only two very large radiators for the living areas. I also fitted a Mixergy hot water cylinder and MyEnergi Eddi solar diverter to enable us to have hot water once the gas combi was removed.
In February 2023, I bit the bullet and ordered my Samsung 5kw R32 Monobloc Gen 6 heat pump from The Heat Pump Warehouse. It arrived as promised, and I set about installing it with the help of some YouTube videos. In my previous house, I was frustrated that I could not monitor how my heat pump was performing, so I decided to stump up for an OpenEnergyMonitor system that would do the job.
Installation went relatively smoothly until it was time to switch it on. At this point, an error code popped up. After much frustration and fault-finding on a Sunday, I found the problem. The fan hadn't been plugged into the main circuit board. Needless to say, I was a bit miffed about this and later discovered that the heat pump had, in fact, been supplied by Joule, who denied all responsibility for the fault and even went so far as to accuse me of sabotaging it myself.

I encountered some other issues along the way, and these are described fully in my blog, The Greening of Rose Cottage, for those interested. The Samsung controller was used as the only thermostat for the system.
Once the heat pump was up and running, I set about adjusting the weather compensation settings to give us the appropriate heating temperature. We prefer 22C in the living rooms and cooler in the bedrooms. All thermostatic radiator valves were opened to their maximum, and the manual radiator valves were used to adjust flow. Further adjustments were made as the outside temperatures got colder later in the year. We tend only to heat the house during daytime hours.
The heat pump performed well, with heating SCOPs between 4.65 in September to 3.97 in December. After purchasing an electric vehicle and moving to the Intelligent Octopus tariff, I made the decision just to heat the water cylinder via the immersion heater at night for 7.5p/kWh and not to purchase a heat exchanger to enable it to be heated via the heat pump.

To complement the heat pump, I had an additional 4.65 kW of solar panels fitted, along with a 5kWh battery. This helps keep the electricity costs down greatly, and so far, bills have been lower than they would have been had we still been using gas. I expect to see a significant income from export in the summer months to help offset the costs of the improvements.

House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I'm super impressed with your initiative to self-install your system, and shocked in equal measure by Joule's sabotage accusation. That's really crazy. But kudos to you for seeing it through and getting it up and running.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Well done, impressed wish i could have done my own, spent years with the loans/grants fiasco never got a penny. I used an MCS, RECC, approved company, in 2014 still solving issues, had another Napit Inspector this month!!
As was I Mars. TBH the whole telephone conversation was bizarre, I was expecting at least an apology but got a full scale nuclear attack!
I have used a thin layer of an insulating lime render on one bedroom wall, more for damp control really and it is expensive. I aim to frame and insulate another wall with insulated plasterboards.
I'm curious how your measured SCOP compares to the "generated" and "consumed" energy totals reported by the Samsung itself? I have an oversized Gen6 Samsung 8.5kW in a super-insulated house (peak heat demand 3.3kW, which delivers an average generated / consumed ratio (SCOP?) of 2.75. This includes hot water use with legionella killing switched on. Very frustrating. I know it's crazy to have such a big HP, it came before the insulation before I knew the word "heatgeek", sized on the old EPC, and cycles like crazy! One cheer for the installer.
Sorry for the delayed reply, there was no notification of your question and I just happened across it. The Samsung COP is vastly less than my openenergy monitor COP. For example on the 27th Samsung reported 4.2 whereas OEM reported 5.2. Given the fact I am using a certified heat meter, I am confident it is Samsung that is wrong.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodySorry for the delayed reply, there was no notification of your question and I just happened across it. The Samsung COP is vastly less than my openenergy monitor COP. For example on the 27th Samsung reported 4.2 whereas OEM reported 5.2. Given the fact I am using a certified heat meter, I am confident it is Samsung that is wrong.
@bontwoody I don't have a heat meter, but I do have a MID-approved electricity meter measuring the consumption of the heat pump (heat pump only, so excludes MIM controller and pumps), and the Samsung reported figures are more than the MID meter, even allowing for pump usage, measured at 35W each (two pumps, 70W combined). I have to rely on the Samsung figures for generation to calculate (S)COP as that's all I have, but at least I know my electricity usage is low.
Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero
I'm curious how your measured SCOP compares to the "generated" and "consumed" energy totals reported by the Samsung itself? I have an oversized Gen6 Samsung 8.5kW in a super-insulated house (peak heat demand 3.3kW, which delivers an average generated / consumed ratio (SCOP?) of 2.75. This includes hot water use with legionella killing switched on. Very frustrating. I know it's crazy to have such a big HP, it came before the insulation before I knew the word "heatgeek", sized on the old EPC, and cycles like crazy! One cheer for the installer.
Hi @Nick Owens, welcome to the forum.
My Samsung is the 12kW (gen6) model, and last winter my heat loss was just over 4kW on the coldest day... so welcome to the over-sized ASHP club!
I get reasonably good COPs by trying to extend run times using batch heating. You are never going to be able to run continuously low and slow, and the cycling will kill efficiency. I use an external room thermostat (FSV #2091/2) and run in "continuously on" mode (FSV 2093 = 1) to prevent the heat pump cycling, and then just try to extend run times. This does result in significantly more temperature fluctuation but we do achieve good COPs (currently over 5 on a heating run). At the moment we may run the heating for around 30-45mins and then turn off and allow the house to cool by 1-2C before another short batch of heating. We run with a flow temp of 32-33C at the moment, which is the minimum we can achieve in order for our radiators to be able to dissipate the 4kW plus of heat that is the minimum output of my ASHP.
So we can potentially just about achieve continuous running once the outside temp hits 0C, but as soon as the temp rising above freezing, we are cycling or switching off (and we only seek to heat to 20C)
Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero
-
Heat pump done right first time? Installation in Kent.
5 months ago
-
Vaillant AroTherm Plus 7kW
6 months ago
-
Microbore heat pump installs
6 months ago
-
Hot water tank lose heat rapidly on random days
7 months ago
-
Mitsubishi Ecodan 11.2kW review
8 months ago
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 3,098 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 7 minutes ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 52 minutes ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 1 hour ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 1 hour ago
-
RE: Why don't people choose heat pumps?
With a heatpump tariff, it should be cheaper to operate...
By Batpred , 1 hour ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 2 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 5 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 9 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 3 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 3 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago