Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
We’re really excited to be recording a landmark Homeowners’ Q&A podcast next week:
“UK Heat Pump Heavyweights: British Gas vs Octopus Energy vs Heat Geek vs Aira vs EDF.”
We’ll be unpacking what sets these major players apart, from their installation models and consumer protections to how each maintains quality, consistency and trust at scale.
Our goal is simple: to help homeowners cut through the noise and understand where true value, reliability and long-term performance really lie.
Got a question you’d like us to ask the panel?
Drop it as a reply below, DM or email me directly at editor@renewableheatinghub.co.uk… we’ll try to include as many as we can.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Here are my suggested questions:
- In your designs, how do you trade off the up-front cost of the system versus ongoing running costs?
- What level of efficiency (seasonal coefficient of performance - SCOP) do you design for?
- Do you offer performance guarantees - e.g. the room temperature that can be achieved, SCOP, annual heating bills? What recompense does the customer have, if your system doesn't meet those guarantees?
- Under what circumstances do you recommend buffer tanks or low loss headers? Do you warn customers that they will lower the efficiency of their systems?
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
@grahamf good set of questions. Can I suggest just one minor refinement to Q1:
- In your designs, how do you trade off the up-front cost of the system versus ongoing running costs? Do you offer customers a choice of these trade offs?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I wanted to provide an update in regards to the insulation visit today, which may prove relevant to heat loss assessments.
He used cameras to look inside the walls and a large thermal camera to look around the property, frankly it was scary. My property is a 2004 one, however he told me that he recently did an assessment on a new built, that had the same issues as mine, with the new owners making a claim on their NHBC to get the insulation up to spec.
In my case there are huge gaps where there is no insulation between the walls, so I have cavity wall insulation randomly placed around the walls, I would estimate only around 50% coverage. In addition there are section where I could see pretty much blue on the camera. Same for the loft insulation, made it look like it was covering the loft, but with large gaps where it wouldn't be picked up.
I strongly believe that the UK has serious issues rolling out heat pumps. I don't think our houses are actually fit for them and the first step for home owners is to insulate the property as much as they can. In my case, I think I am looking at £5000+ costs.
Posted by: @dreiI wanted to provide an update in regards to the insulation visit today, which may prove relevant to heat loss assessments.
He used cameras to look inside the walls and a large thermal camera to look around the property, frankly it was scary. My property is a 2004 one, however he told me that he recently did an assessment on a new built, that had the same issues as mine, with the new owners making a claim on their NHBC to get the insulation up to spec.
In my case there are huge gaps where there is no insulation between the walls, so I have cavity wall insulation randomly placed around the walls, I would estimate only around 50% coverage. In addition there are section where I could see pretty much blue on the camera. Same for the loft insulation, made it look like it was covering the loft, but with large gaps where it wouldn't be picked up.
I strongly believe that the UK has serious issues rolling out heat pumps. I don't think our houses are actually fit for them and the first step for home owners is to insulate the property as much as they can. In my case, I think I am looking at £5000+ costs.
Yes but...
The evidence is that many heat loss surveys overestimate the loss quite significantly, and there are relatively few reports of heat loss surveys that underestimate loss. Your house may well be an exception, of which there will of course be many in absolute terms but likely a very small percentage. What do we do, deconstruct every house? I dont think so.
Unfortunately we have to deal with a legacy of dodgy builders going back centuries and as we know dodgy builders are still out there. Thats the real world and, given that its been like that for centuries it would be an extreme optimist that thinks this may change.
We could of course conduct heat loss measurements on homes, in fact I have been advocating for over a year and a half that we do just that in the most cost effective way possible ie by using consumption as a sanity check. Sadly few people in the industry want to hear this, because it disturbs the certainty (that they cant be blamed) that the fabric GIGO spreadsheet gives them. And sadly few outside the industry have thought about it enough to care.
The fact is that we have to deal with the world as it is, not some idealised world that we would all love to live in. The world as it is contains buildings that catch fire, fall down, aren't insulated in the way that they should be, have the wrong materials installed, get damp when they shouldn't and many other horrors. So shall we stop doing anything until all that is fixed?
We need to face the fact that a proportion of the construction industry is basically sh1t, always has been and almost certainly always will be. Then we need to deal with that whilst not paralysing ourselves. Difficult I know, but how it is.
Of course I wish it were otherwise and I am sure you do to.!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
It would explain the difference between different heat loss assessments, so the person doing it, will most likely be either accurate enough, or overestimate, which seems to be the case, better safe than sorry.
I think my heat loss assessment was pretty accurate too, taken in consideration the current insulation state. I couldn't really see any heat escaping through the outside walls, but did see some dark areas inside the house, I am not sure if it was anything to worry about. My main issue is the loft, and is something I will need to get on straight away. A few rolls of insulating loft wool should do.
When insulating lofts, how do you cover spot lights? Is there something I can put around them or just leave enough space? I was thinking like making some kind of protective shield out of mesh, so the insulation won't fall or get pushed on it. Being LEDs, they shouldn't get that hot. I think quite a bit of heat is escaping around the spot lights, maybe there is some sort of rubber seal that you can put around them.
Posted by: @dreiWhen insulating lofts, how do you cover spot lights?
try these
Mitsubishi Zubadan 14kW with Mixergy 210l DHW in 220m2 barn property. 24 solar panels = 9kWp with GivEnergy 5.0kW Hybrid inverter and 19kWh GivE batteries. Jaga Strada fan-assisted rads throughout. Landvac vacuum glazing/triple glazed windows.
Posted by: @dreiIt would explain the difference between different heat loss assessments, so the person doing it, will most likely be either accurate enough, or overestimate, which seems to be the case, better safe than sorry.
Very definitely.
I think the market has changed a bit since mine were first done now nearly three years ago. There are clearly loads of installers out there who still religiously use the default assumptions, dialled into opaque tools, which can lead to large overestimates that have a material effect on the design - eg 16kW 'surveyed' vs 7kW actual in my case. The same installers will often refuse to account for invisible fabric upgrades, like IWI for example. There is also another class of installers who use experience more, often with much simpler (and thus much more transparent and if necessary flexible) spreadsheets/tools, to arrive at figures which are usually more realistic, but much more dependent on installer skill. The most recent podcast about the heat geek 'zero disrupt' offer refers to this obliquely but quite extensively.
The two which I eventually shortlisted for my install fell firmly into the latter category. Simple tools (bordering on crude) combined with experience and (hopefully) bolstered by my own consumption data, leading them to propose 7kW designs rather than 'safe' (for them not the customer) 16kW designs. Perhaps they have made mistakes along the way, but have learned from them.
I can accept installers making mistakes, we all do from time to time and we all have to start somewhere with our learning processes. What I cant accept is installers who ignore solid evidence that what they are proposing is wrong or who, having made mistakes, resist fixing them!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jords
One thing that surprised me the most was the differences in heat loss between the three. Heat Geek and British Gas used LiDAR on an iPad. Octopus did it the old fashioned way with a laser tape measure and app.
Heat Geek
Octopus
British Gas
Kitchen
2280
2223
2233
Playroom
550
667
533
WC
160
185
105
Living Room
1530
2004
1938
Entrance Hall
300
487
Shower Room
650
1167
705
Landing
190
166
Bedroom 3
360
346
473
Bathroom
360
630
408
Bedroom 2
450
371
530
Bedroom 1
660
674
873
Loft Landing
320
565
484
Office / Bedroom 4
640
869
934
Same rooms are very similar. Others very different. They also all chose different outside design temps. Heat Geek: -2, Octopus: -2.4, British Gas: -2.9
Radiator changes. Heat Geek: 4, Octopus: 8, British Gas: 10 plus a plinth heater for the kitchen.
Anyway just thought I would share my experience with the 3. Maybe I’m being too picky. But if I’m going to spent £10k (after the bus grant) I would like to make sure it’s just right.
Thank you, this is very useful. We are just about to embark in the survey stage.
I am wondering whether installers are able to reuse the surveys others did (as they are presumably all aiming to apply the same MCS "best practice")
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredI am wondering whether installers are able to reuse the surveys others did (as they are presumably all aiming to apply the same MCS "best practice")
In my experience no!
I think the figures show the extent to which heat loss surveys are what-iffery, all depending on the assumptions you (or rather they) make. Thats why I always advise sense checking against a measured figure for the total if the information is available. The variation in individual room performance shows why you should balance for room temperature not equal deltaT, although in practice rooms share heat a lot so this is somewhat smeared out.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa There is also the ‘blame factor’, if one installer were to use another’s heat loss calculations, they would have a reinforced concrete excuse were the results ‘disappointing’ imagine the litigation! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodles@jamespa There is also the ‘blame factor’, if one installer were to use another’s heat loss calculations, they would have a reinforced concrete excuse were the results ‘disappointing’ imagine the litigation! Regards, Toodles.
On the litigation, I would not go there and definitely not around heat loss calculations. It would be straight to the installer, of course.
Anyway, the cynic in me says that as is usually a chargeable service, they have no incentive to miss out. 🙂
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,623 Topics
- 61.3 K Posts
- 716 Online
- 7,004 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Is Traditional Radiator Balancing Tosh?
@markspencersmith Before I offer my thoughts I am...
By JamesPa , 10 hours ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
@editor i'm SEPA Registered with a waste license, we du...
By Aventus Eco , 13 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
what controller are you using?
By Grantmethestrength , 15 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Manufacturer: appliances direct/superheat Model: 7Kw ...
By Adrian , 16 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
As a final update on this thread from me; Ribble Valley...
By DaveC , 16 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Fantastic. This is all I needed. Afew planning applic...
By Batpred , 20 hours ago
-
RE: Renewables & Heat Pumps in the News
Commentary on DCs and the grid in the EU. A bit on some...
By Jeff , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
If you put a fan in a pipe you get a much more efficien...
By bobflux , 1 day ago
-
RE: Mitsubishi ecodan settings
As the owner of a 8kW Ecodan R290 maybe I can help. ...
By RobS , 1 day ago
-
Wall mounting makes sense. We are now looking for an in...
By Batpred , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you, watson did allow me to find this one! Our ...
By Batpred , 2 days ago
-
RE: Our 10 year old Grant heat pump failed
Sorry to hear. Grant seem to be selling the R290 pump...
By Batpred , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
.. apparently with american fuel. 🙃
By Batpred , 2 days ago
-
RE: The Watchdog That Watched and Waited
Spot on. The watchdog that knows how to never take the ...
By Batpred , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Yes, the cost difference may be marginal, if you are lu...
By Batpred , 2 days ago
-
RE: Don’t Install a Heat Pump Until You Read This
In our latest update, we attempt to show what a poor he...
By Mars , 2 days ago
-
RE: Heat Pump Pipe Sizing Question
No the retrofit strategy is already published. It's on...
By JamesPa , 2 days ago
-
RE: Ecodan spells out end of R32 for real environmental alternative
I think I saw the answer to this on another thread but ...
By Batpred , 2 days ago
-
RE: Mitsubishi Ecodan FTC6, Evohome & Economy 7. Getting Two Zones to Work Together
This is what we are trying to avoid if we go Ecodan, mu...
By Batpred , 2 days ago
-
Great points, I agree it is overused. It is also a grea...
By Batpred , 2 days ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
On old (non inverter) compressors there’s sometimes a ‘...
By robl , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor It's available here -
By HarrisonC , 3 days ago
-
@painter26 i am in Lightwater and midea trained. Sounds...
By Wizard , 3 days ago