Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Sticky] Struggling to Find a Top Heat Pump Installer? We Can Connect You With the Best Installers in the UK
Posted by: @little-lightsOil: Approx 1,250 litres. Bit of a guesstimate. We supplement with electric heating and kettles for hot water when the oil boiler fails (not infrequent maybe approx. 2.5 weeks in total across the past year, in fits and starts, during the winter months).
OK thats indicative more of 4kW than 7kW, although given you let the house cool a lot and use supplemental heating one might stretch it to perhaps 5kW or even 6. 7kW is a lot for a 80sq m or even a 100sq m well insulated house, mine is about double the size, 1930s, tolerably well insulated (but floors uninsulated) and 7kW.
What Im saying is that you may well be able to get away with a good 5kW machine and if you can you may get slightly better performance (because it will modulate down further). It might be worth getting a quote from a heat geek if you havent already, they tend to keenly spec albeit they tend to be pricy. Also Octopus who seem almost invariably to get good reports (other than the recently introduced Cosy 12 which was/is noisy at least when first released). Mostly I would do that to be certain you have covered all bases.
You wont want to operate your heat pump on/off, it will be very inefficient.
With the EDF quote I would check
'heating controller' - you do not want any third party controls, this is probably just the Daikin one but check
'250L PRE PLUMBED R32 CYLINDER' - check that does not include a low loss header or a buffer tank
What flow temp are they designing for? If >45 dont go there.
I cant speak for the Daikin controls but I can speak for the Vaillant ones which are definitely good.
You may be able to get a cheaper quote if you shop around and I believe the grant will go up shortly as you are replacing oil. Personally I would get some more quotes. A good technique with Vaillant (and some others) is to ask them for local certified installers. There may be people who dont advertise because they dont need to! Those can be a good bet.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Perfect thanks - because we're doing an extension and it isn't built yet there's a few won't look at it until all the building work is done. Which is a tad annoying because if it's planned now before foundations are dug out and laid it may make the actual install easier overall. Also - we will be removing the boiler as part of the work we're doing, so would need some form of replacement, for hot water mainly, before the extension is completed.
Heat Geek were going to charge £800 for their planning stage, which seems a decent % of the overall cost of a heat pump, so I'd counted them out. Octopus and British Gas won't look at it until the extension is built. Aira did quote for us, they offered Aira Heat Pump 6kW, with the Aira Indoor Unit (All-in-one) 250L, and a Buffer Tank 40L. I decided against them because of the buffer tank and advice I've seen on here regarding that. I've asked for Ovo to contact me a couple of times, but they haven't as yet.
Are there any other companies you'd recommend?
Thanks so much - with installation and planning being such an important part of the process, I really do appreciate the input and advice!
Posted by: @little-lightsAre there any other companies you'd recommend?
I cant, but @editor probably can if you tell him roughly where you are.
I wouldn't ignore the smaller operators in your vicinity. I found my installer through Vaillant. I had never heard of him and he doesn't advertise widely because he doesnt need to. As it turned out excellent. He was literally a one man band - even the electrics with the exception of the power feed which had been done by an electrician in advance. Worked long hours to get the job done and did a very neat job. I do agree that they can be unknown quantities though so need more due diligence, but if you find a good one then they can also be very good.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaA good technique with Vaillant (and some others) is to ask them for local certified installers. There may be people who dont advertise because they dont need to! Those can be a good bet.
I second that. The third time I tried using the Vaillant list I found one possible mid size installer - and they were happy to install Grant and Bosch as well.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @little-lights@jamespa Perfect thanks - because we're doing an extension and it isn't built yet there's a few won't look at it until all the building work is done. Which is a tad annoying because if it's planned now before foundations are dug out and laid it may make the actual install easier overall. Also - we will be removing the boiler as part of the work we're doing, so would need some form of replacement, for hot water mainly, before the extension is completed.
Heat Geek were going to charge £800 for their planning stage, which seems a decent % of the overall cost of a heat pump, so I'd counted them out. Octopus and British Gas won't look at it until the extension is built. Aira did quote for us, they offered Aira Heat Pump 6kW, with the Aira Indoor Unit (All-in-one) 250L, and a Buffer Tank 40L. I decided against them because of the buffer tank and advice I've seen on here regarding that. I've asked for Ovo to contact me a couple of times, but they haven't as yet.
Are there any other companies you'd recommend?
Thanks so much - with installation and planning being such an important part of the process, I really do appreciate the input and advice!
It seems odd these companies don't design and plan for you before the build, I would say this is at least half our work load, in fact I quite like these jobs as they seem to have a 6-9 month lead in time, we also often will fit the cylinder way before the heat pump for the exact reason you mention, you need hot water sooner than heating. I find that providing you build the home to the specification, it is easier for us to desk top design from your build documents as they normally have very detailed fabric specs so no fabric assumptions on our part. If you are in Kent I would be very happy to help you.
Also worth noting if you are not in Kent and need to find someone, the Vaillant list works, we are on the Vaillant register and its right that some of us don't advertise loudly as we are already booked for a fair few months so what trickles in just keeps topping up ahead. We currently have orders and no space up to July and have planned orders in nearly every month this year and a couple next year, these much longer planned dates are all self builds secured way before ground is broken. It is defiantly a normal thing to plan, design and book once you intend to start your new build.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Hi Mars,
I've sent you a request to connect me with an installer in my area.
Thanks
Currently viewing this topic 6 guests.
Recently viewed by users: Simon_JM 36 minutes ago.
- 26 Forums
- 2,637 Topics
- 61.5 K Posts
- 191 Online
- 7,035 Members
Join Us!
Latest Posts
-
RE: UK warm homes plan - how can it be delivered?
@bobflux My view is that regulation for consumer pro...
By Batpred , 2 hours ago
-
Hi Mars, I've sent you a request to connect me with a...
By sttpd1917 , 2 hours ago
-
RE: Sizing an ASHP; Heat loss and kW
Annual consumption is almost certainly better than an E...
By JamesPa , 6 hours ago
-
Grant Aerona R290 (15.5kW) - How is DHW Target Temp calculated?
Hello all, We have just had a Grant Aerona R290 insta...
By TaffontheTaff , 8 hours ago
-
RE: Setback savings - fact or fiction?
Indeed, I can well imagine that a heat-pump based syste...
By PeterWurmsdobler , 11 hours ago
-
Loud noises in the night - and one for the toolbox?
I was woken at 5am on Sunday to a very loud noise, akin...
By JamesPa , 12 hours ago
-
RE: Advice on Vaillant Sensocomfort
The latest Vaillant announcement I saw said that they w...
By JamesPa , 12 hours ago
-
RE: Debugging my legionella immersion heater
I notice this (66 is rather hot) with my legionella cyc...
By JamesPa , 1 day ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
@transparent I thought you would spot that wind turbine...
By Batpred , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils there is no logic to oversizing a heat pump. It...
By AgentGeorge , 1 day ago
-
RE: Vaillant Sensocomfort Time
Thank youy for the pointer. I think I have managed to ...
By ispookie666 , 2 days ago
-
RE: Forum updates, announcements & issues
I have been doing a lot of work on the site lately and ...
By Mars , 2 days ago
-
@majordennisbloodnok good advice, thanks for that.
By David999 , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
I am following this thread with great interest and than...
By TaffontheTaff , 2 days ago