Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Surge Protection Devices
Posted by: @transparentPosted by: @batpredSo would the presence of DC components require RCDs to be fit?
Erm... I can interpret that question in more than one way, so I'm unsure of the angle you're taking.
All Type-B RCDs and RCBOs will correctly trip ii there is an element of Direct Current superimposed onto the mains 50Hz waveform.
I've deliberately changed the wording to clarify the concept.
The reasons that earth-leakage devices are fitted to circuits is usually to
- protect the cable in the event of fire / over-heating
- prevent death in the unlikely event of a person touching a live wire or connector
- prevent the metal casing on an appliance becoming live due to a short-circuit fault
That decision is the same irrespective of whatever aberrations are present on the sine wave.
In the case of our installation site, I see value in having the RCD fit, so we will have it. In many other cases, since I understand isolators are typically installed near the heatpump (EST guidance), unless the RCD would remove the need for such isolator, it seems to mostly add to costs without significant value.
But my angle was actually on whether an RCD could be justified solely based on the likely DC components?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredBut my angle was actually on whether an RCD could be justified solely based on the likely DC components?
No.
The shape of the waveform has no bearing on the decision to use an RCD.
BTW. I'm still unsure why you're making "DC Component" into a plural.
Could you give an example for me please?
Save energy... recycle electrons!
- 26 Forums
- 2,670 Topics
- 62.5 K Posts
- 198 Online
- 7,079 Members
Join Us!
Directory
Degrees of Separation
Latest Posts
-
@transparent Thank you very much! Toodles.
By Toodles , 10 minutes ago
-
Many messages back and forth later… GOV UK One Login ...
By Toodles , 35 minutes ago
-
No. The shape of the waveform has no bearing on the d...
By Transparent , 2 hours ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@majordennisbloodnok Thanks, this makes sen...
By Bash , 2 hours ago
-
RE: Say hello and introduce yourself
@will-h, this isn't a dig but we would prefer if anyone...
By Majordennisbloodnok , 3 hours ago
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
Thanks for that, @old_scientist. There are several thre...
By Majordennisbloodnok , 4 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Thanks Tim. That SolarEdge data also shows voltages a...
By Transparent , 6 hours ago
-
RE: Configuring third party dongle for Ecodan local control
A few notable developments: I'm working through addin...
By F1p , 19 hours ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
Vehicle to Grid is the further step and here is the IEA...
By Judith , 19 hours ago
-
RE: Renewables & Heat Pumps in the News
Where the grid is heading? Input from Kraken.
By Jeff , 21 hours ago
-
RE: MCS 2.0 - Changes in January 2025
Yes, and by the looks of it, much of the paperwork is n...
By Batpred , 23 hours ago
-
RE: Plug and play solar. Thoughts?
@jamespa Yes, unfortunately our policymakers learned...
By Batpred , 23 hours ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
@l8again It seems you did very well. With our HG h...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
Just wondering how you went in the end? A guaranteed 40...
By Batpred , 2 days ago