Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Mitsubishi Ecodan FTC6 settings

21 Posts
7 Users
6 Reactions
969 Views
 RobS
(@robs)
Estimable Member Member
Joined: 2 years ago
Posts: 138
 

Posted by: @clockworks

Is there a setting on the FTC6 that tells it to keep the heating off if the outdoor temperature is above a certain level?

While @F1p's dongles are great, the FTC can do this itself. It's called Summer Mode and can be found in the Service settings (default password is 0000) then Operation Settings. Summer Mode has two ambient temperature settings (on and off temperatures) and two "judgment times" (how often to check the ambient temperature - 1 hour works well for both).

 



   
🫶
1
ReplyQuote
(@clockworks)
Trusted Member Member
Joined: 2 years ago
Posts: 63
Topic starter  

OK, I bought one of the dongles q couple of weeks ago, finally fitted it this morning.

Powered up the FTC6, and was a bit surprised that the heatpump fired right up, despite the Mitsubishi remote stat being set to 19 degrees?

I connected my iPhone to the "Mitsubishi Bridge AP", entered my WiFi details. I left everything else at the default, and clicked "save".

After a minute, the heatpump took notice of the remote controller, and stopped heating.

Is it normal that the FTC ignores the remote stat until the dongle comes properly online?

 

Looking at the LED on the dongle, I can't really tell if it's Orange or Green - looks Green dead ahead, but Orange from the side.

 

Where can I find detailed instructions of what to do next?

 

 

Edit:

I was using the wrong MQTT credentials!

When I first used MQTT to work with my Sofabaton X2 remote, I followed a guide that said it was best not to use the default credentials, but to set up a user just for MQTT.

I've re-configured the dongle with the correct MQTT credentials, and the LED is now green from whatever angle I look at it.

I can also see a load of stuff in the MQTT integration section, so it all looks good.

 

 


This post was modified 3 weeks ago by Clockworks

   
👍
2
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 10 months ago
Posts: 126
 

I was just replying when i saw your edit drop in! 🙂

 

Posted by: @clockworks

Powered up the FTC6, and was a bit surprised that the heatpump fired right up, despite the Mitsubishi remote stat being set to 19 degrees?

 

The default behaviour after any power loss is the Ecodan will run a hot water cycle - i suspect it was this which started.



   
👍
1
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 10 months ago
Posts: 126
 

@clockworks how have you been getting on? Hopefully not glued to Home Assistant for the last 24hr 🙂

 



   
ReplyQuote
(@clockworks)
Trusted Member Member
Joined: 2 years ago
Posts: 63
Topic starter  

I've not done anything with it, beyond looking at the various entities that are exposed. It's saying that there's an update available, so I'll do that shortly



   
ReplyQuote
(@clockworks)
Trusted Member Member
Joined: 2 years ago
Posts: 63
Topic starter  

OK, I've done the update, and it's still working, so I've had a closer look at what it can do.

Since my basic WC curve works fine on a normal overcast day, I think that I need:

the "temperature offset" function to be automated, triggered by a certain differential between the hallway and (unheated, but massive solar gain) conservatory Tapo temperature sensors.

The main thermostat (the mitsubishi remote) to be lowered if the above temperature differential exists, and I have opened the door from the kitchen to the conservatory, to effectively turn off the heating.

 

Reading through the documentation, I will need to "onboard" the WC curve, define it the same as my existing curve, and put the heatpump into fixed flow temp mode?

 

This is where it starts to go over my head somewhat.

I've done a bit with esphome to create my own devices, but mostly by copying/pasting/modifying existing code, so I'll probably make it work somehow - once I get my head around the basics.

 

Does "publishing" json via mqtt write data permanently to the esp device, or is it just in RAM so it gets lost if there's a power cut?

What happens to the heatpump if the dongle or my HA server dies? Can I simply switch the FTC6 back to WC mode and it carries on like before?



   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 10 months ago
Posts: 126
 

It sounds for your particular use case, yes, onboard curve may be best.

There is an excellent write up here:

https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/configuring-third-party-dongle-for-ecodan-local-control/paged/2/#post-54561

 

 

Posted by: @clockworks

Does "publishing" json via mqtt write data permanently to the esp device, or is it just in RAM so it gets lost if there's a power cut?

What happens to the heatpump if the dongle or my HA server dies? Can I simply switch the FTC6 back to WC mode and it carries on like before?

On these specific questions:

1. Publishing WC will subsequently be saved to the nonvolatile storage, so it will be retained on power loss. This is the case for most parameters, unless there was a specific reason not to

2. Well if your HA dies, the dongle carries on with the saved curve. If the dongle dies then it will remain in fixed flow. In both cases you can swap your settings via the main controller as it overrules in the Ecodan design 



   
ReplyQuote
(@clockworks)
Trusted Member Member
Joined: 2 years ago
Posts: 63
Topic starter  

Thanks for that link. I've had a quick read of it, and it makes it a lot clearer.

 

On the issue of what happens if the dongle dies, presumably my existing Mitsubishi remote thermostat (which is now plugged in via the spare port on the dongle) will be offline, so won't work unless I plug it in directly onto the FTC6?

Or, is the extra port on the dongle just a directly wired parallel connection, so the Mitsubishi remote will still work?



   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 10 months ago
Posts: 126
 

Posted by: @clockworks

Mitsubishi remote thermostat (which is now plugged in via the spare port on the dongle)

The Mitsi remote thermostat should not be plugged into the dongle, that should remain connected to the CNRF port located just above the CN105. Therefore the Thermostat should remain unaffected.

It was likely the MELCloud dongle you mean which was consuming the CN105 port

 

Posted by: @clockworks

dongle just a directly wired parallel connection

The Serial communication that FTC speaks over then CN105 would not support multiple devices speaking on the same Tx/Rx lines, clashes, confusion and failure would occur eventually.

So the adapter has act as an active negotiator of communication between itself, the FTC and optionally, MELCloud.

 

Thankfully the chance of failure is very low. There is the possibility for the WiFi version to recover via USB first with the GitHub instructions and open source firmware and failing that, the controller is also a pluggable replacement.



   
ReplyQuote