Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Adding additional Solar Panels to a DC coupled battery system

27 Posts
5 Users
5 Reactions
995 Views
(@old_scientist)
Honorable Member Member
Joined: 2 years ago
Posts: 536
 

@transparent I have a question about the electrical connection for my micro-inverter. It's designed to be a plug-in device, but I'd rather make a properly protected permanent connection to the mains than just plug it in.

The outbuilding is fed by a SWA cable from the main CU in the house on a 32A MCB protected by an 80A (30mA) RCD. I very much doubt the RCD in the main CU is bidirectional.

There is a CU in the outbuilding fed by the SWA with individual MCBs for the chest freezer, lights and sockets. These are only protected by the RCD in the main CU that feeds it. If connecting the micro-inverter into this secondary CU, what type of RCD or RCBO should I specify to best protect that 800W micro-inverter?

Would you recommend we also install a SPD in the outbuilding CU as there in no surge protection at the main house CU?

 


Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1059
Topic starter  

@transparent Hi, so I have already bought the splices, but the hole you refer to is actually a nipple! 🙂 (Bugger, there go the midwifery students again). I would have to drill the section to insert any fixings, so Im guessing its not meant to be fixed. They do supply a much longer rail though so I suppose fixing it isnt going to be the end of the world.

I watched a very interesting youtube video with two sparkies discussing the earthing conundrum. As you say its not mandatory but they did come up with some plausible scenarios where there could be an issue. One of them actually had an arc from his forehead to a scaffold when he bent down to pick up some wet leaves from the gutter! They blamed parasitic coupling (???)

One other point against earthing it is the fact that I cant actually source the correct renusol item, to connect the earthing wire!

image

House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1059
Topic starter  

@old_scientist I got them from Tradesparky. In the end after much debate with ChatGTP, I plumbed for these hooks. The height adjustment is quite useful, and one up from bottom is perfect for my tiles.

 

image

House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
👍
1