Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Problems with sizing a replacement for a Viessmann Vitocal 200-S
Posted by: @transparentDo you have a source reference to Viessman's manuals where this approach is described by them?
The Vitotronic 200 WO1C control unit manual can be downloaded here (link will download the PDF manual): Viessmann Manual
The relevant descriptions are on page 28 (External Heat Generator) and pages 193-197
Posted by: @transparentbut where is the sensor which provides that temperature information to the boiler?
Is that mechanism an integral part of the Viessmann firmware within the heat-pump?
Or is it in a separate "dual fuel" control box which has its own temp sensor?10-mins sounds a very long time interval over which the boiler will continue to operate, especially when the heat-pump is already known to be operating inefficiently.
The mechanism is an integral part of the Viessmann firmware within the heat pump control unit. And yes I agree - I think the default is 20 minutes so I already reduced it, but it sounds like I should reduce it even further.
- 27 Forums
- 2,756 Topics
- 64.8 K Posts
- 265 Online
- 7,160 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
The Vitotronic 200 WO1C control unit manual can be down...
By jon , 5 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
Flow rate is set by pressure created by the circulator ...
By bobflux , 8 hours ago
-
RE: Glass lined Cylinder for private water supply
I have one of those... a Thermal Store. In my case th...
By Transparent , 13 hours ago
-
RE: 7kW EV Charger Options Advice
Yeah that's normal Copper is expensive, and the kettl...
By bobflux , 13 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 15 hours ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 2 days ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@kilgorexv definitely a larger inverter will help and m...
By AndrewJ , 3 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
The installation is almost done! I've written up two ...
By tomasmcguinness , 4 days ago
-
RE: Switch suitable to change between two inverter CT's
Last winter my battery ,32KWh, could run the house com...
By Jancold , 4 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Agree with Major. And even if I was very happy with ...
By Batpred , 4 days ago
-
RE: Is the "divide by 2900" rule still valid?
There is another estimator that you could use, a formul...
By Rob of York , 4 days ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
@penval, really useful update. After all the discussion...
By Mars , 7 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 1 week ago
Members Online
No online members at the moment