Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Vaillant ecoTEC Plus - Flow Temp and Set Up

20 Posts
3 Users
4 Reactions
1,160 Views
trebor12345
(@trebor12345)
Reputable Member Member
Joined: 3 years ago
Posts: 220
Topic starter  

Posted by: @jamespa
↑

Posted by: @trebor12345
↑

Setting a Desired Room Temperature on the sensoComfort Controller has NO effect? (You can set the Desired Room Temperature to 30C and it will have no effect on the flow temperature)

That is not the case.  The heating curve adjustment sets the shape of the curve but the set desired temperature (if set to anything other than  20C) offsets the curve.  This is explained on page 4 of the manual here

JamesPa

The chart explains well how the heat curve and manual temperature adjustment work together.

Screenshot 2026 10 29 at 08.53.37

 


2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3


   
Like
1
ReplyQuote
trebor12345
(@trebor12345)
Reputable Member Member
Joined: 3 years ago
Posts: 220
Topic starter  

Heating been on for 4 weeks now, continuous.  It's 6C outside and had my first ever weather compensation increase in flow temperature from 25C to 25.5C.  I was beginning to wonder if it was going to work.  Happy now.  


2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3


   
ReplyQuote
trebor12345
(@trebor12345)
Reputable Member Member
Joined: 3 years ago
Posts: 220
Topic starter  

Noticed today that the condensate drain is not draining away.  See attached.   I believe there is a heater element in the copper pipe/hole.  What might be my options?

BTW, heating working really well in the cooler weather.

IMG 4769

 


2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5716
 

From the picture, in which I think I can see a pool of water, it looks to me like the problem is not the heater, it's that once the water exits the pipe it has nowhere to go.which may indicate inadequate drainage once the water leaves the pipe.


This post was modified 2 weeks ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

trebor12345
(@trebor12345)
Reputable Member Member
Joined: 3 years ago
Posts: 220
Topic starter  

Posted by: @jamespa
↑

From the picture, in which I think I can see a pool of water, it looks to me like the problem is not the heater, it's that once the water exits the pipe it has nowhere to go.which may indicate inadequate drainage once the water leaves the pipe.

you are correct, it's insufficient drainage in the hole. Do you think the copper pipe could be removed from the white connector? Is the white connector a push fit?

 


This post was modified 2 weeks ago by trebor12345

2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5716
 

@trebor12345 

I would say it may need to be excavated, or a path created to carry the water to a place where it can drain away, preferably safely but above all drain away. 

What you don't want is the end getting blocked which appears to be happening as the end of the pipe is below the surface level.


This post was modified 2 weeks ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
trebor12345
(@trebor12345)
Reputable Member Member
Joined: 3 years ago
Posts: 220
Topic starter  

Posted by: @jamespa
↑

@trebor12345 

I would say it may need to be excavated, or a path created to carry the water to a place where it can drain away, preferably safely but above all drain away. 

What you don't want is the end getting blocked which appears to be happening as the end of the pipe is below the surface level.

Could I pipe it to a acro drain which is within 500mm against the wall?  Can the copper pipe be removed from that white connector?  Is it push fit?

 


2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5716
 

Posted by: @trebor12345
↑

Posted by: @jamespa
↑

@trebor12345 

I would say it may need to be excavated, or a path created to carry the water to a place where it can drain away, preferably safely but above all drain away. 

What you don't want is the end getting blocked which appears to be happening as the end of the pipe is below the surface level.

Could I pipe it to a acro drain which is within 500mm against the wall?  Can the copper pipe be removed from that white connector?  Is it push fit?

 

If there is a drain nearby that's exactly what I would do and indeed how mine has been organised.

I don't know how the copper pipe connects, I think Vaillant just provide a hole with a connector, but no idea the spec.  I would imagine it's push fit but don't know for sure, I do know that it's not well attached to the casing in my 2024 model and needed to be propped up by my installer to stop it falling out!.  You can get at it if you take the front off (usual warnings apply), you need the right kind of security bit to do this but a kit of 12 assorted bits covering everything you are ever likely to need costs a few pounds.

 


This post was modified 2 weeks ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   