Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Heat Loss Calculations

5 Posts
4 Users
2 Reactions
20 Views
(@l8again)
Estimable Member Member
Joined: 10 months ago
Posts: 71
Topic starter   [#3235]

Looking at HeatPumpMonitor there is a new expanded page of information (well at least to me). Looking at various heat pump sites, the one thing that stands out is the difference between the survey calculated heat loss and that calculated by HeatPumpMonitor. Clearly, the former influences the size of the heat pump and the latter its actual performance.

This mismatch is not limited to one particular installer/company. This is a particularly stark example: a design of 10.5kW heat loss compared to a HeatPumpMonitor heat loss of 4.5kW. Thoughts/comments?

IMG 1713

 


This topic was modified 55 minutes ago by L8Again

   
Quote
(@singlespeed)
Trusted Member Member
Joined: 8 months ago
Posts: 63

   
ReplyQuote
(@spen74)
New Member Member
Joined: 2 days ago
Posts: 2
 

Hi, we currently don't have a HP but its something im very interested in and currently just looking at.

I would ask, does the survey take into consideration the location of the property, ie exposed to the prevailing wind/weather?

What about the altitude? I live not far from Newcastle, but up big hill, we can have ice and snow yet in less than 2miles its frost and rain. Another 10 mile up the road they would have good snow coverage. 

Orientation of the property? Ours is (almost) dead on north/south, the back gets full sun while the front none. Theres a noticeable temperature (and light levels) difference.....our living room is colder than the kitchen. 

Do different foundations affect the property?

Could it be they just over spec for fudge factor, easier than under spec and needing a new HP.



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5709
 

Posted by: @l8again
↑

Looking at various heat pump sites, the one thing that stands out is the difference between the survey calculated heat loss and that calculated by HeatPumpMonitor. Clearly, the former influences the size of the heat pump and the latter its actual performance.

This mismatch is not limited to one particular installer/company. This is a particularly stark example: a design of 10.5kW heat loss compared to a HeatPumpMonitor heat loss of 4.5kW. ....

Thoughts/comments

No surprise TBH.  For years heat losses have been frequently overestimated, mine by a factor of more than 2 (16kW Vs 7kW).  Ridiculous air change rates, ignoring fabric upgrades, double counting room to room losses and then adding 20% for good measure.  I do have the impression it's got better in recent years but the legacy is still out there.

In fairness there are some unknowns so heat loss calculations will always be estimates, but not to the extent that some installers have achieved.

It is for this reason that I would always recommend a sense check based on gas/oil consumption if you have any data at all.  Fortunately I did so got a 7kW pump not 16 which several wanted to sell me (one even suggested a cascade!).


This post was modified 11 minutes ago by JamesPa
This post was modified 6 minutes ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
2
ReplyQuote

JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5709
 

Posted by: @spen74
↑

Hi, we currently don't have a HP but its something im very interested in and currently just looking at.

I would ask, does the survey take into consideration the location of the property, ie exposed to the prevailing wind/weather?

What about the altitude? I live not far from Newcastle, but up big hill, we can have ice and snow yet in less than 2miles its frost and rain. Another 10 mile up the road they would have good snow coverage. 

Orientation of the property? Ours is (almost) dead on north/south, the back gets full sun while the front none. Theres a noticeable temperature (and light levels) difference.....our living room is colder than the kitchen. 

Do different foundations affect the property?

Could it be they just over spec for fudge factor, easier than under spec and needing a new HP.

The survey can take into account exposed postiion etc, whether they all do I cant say

Foundations dont make much difference, floor insulation (if any) does.

Adding a fudge factor is one of the things historically leading to overestimated heat losses.  This can matter, sometimes a lot.  That and the points you bring up are another good reason to do a sense check.

Heat loss estimates look very scientific, and in principle they are.  However there are inevitably unknowns.  Judging by what we see here the better installers appear to have gotten to grips much better with this compared to the position even 2 years ago.

Whats you property size (sq m), construction, and annual fuel consumption, that should ballpark it and make to possible to comment a boit more specifically,

 


This post was modified 1 minute ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   