Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
15kw pump for 225m2 1990's house - over kill?
I have read you latest response re buffer tanks and I must say that, based on that, I would not trust your installer. It's not that the answer is wrong, just that there are other ways to solve the problems he alludes to if indeed they exist.
For me this remains essentially simple. 15kW is almost certainly too big, and very definitely way too big after you have insulated which you plan to do. There is no identified reason for a buffer.
Thus, unless it's a desperate situation and based on the information you have shared I simply would not proceed until these issues are resolved. Thus I would either insulate, measure, and seek alternative quotes, or seek a bufferless quote with a heat pump not more than 12kW (which will likely be tolerably oversized after insulation) if it must be done now.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@seaviews your installer would be right to say that the extra volume of water in the tank will help with defrosting the heat pump. That would require a 2 port volumiser, not a 4 port buffer tank - the tank itself may perform either role depending on how it is plumbed in.
However, it is not entirely clear that is what he is saying. Some installers will tell you that the volume of hot water in the buffer tank will enable you to keep the radiators warm, while the heat pump turns itself off. That would be misguided, as you want the heat pump to be running low and slow continuously 24 hours per day.
While a 4 port buffer does help separate out sludge in the system, that is not its primary purpose. Its main purpose is hydronic separation of primary and secondary circuits, which is usually unnecessary. If the water needs cleaning up, then you need a power flush and refilling with inhibitor added to the water. You also need a filter such as MagSafe to prevent the particles gumming up the heat exchanger in the heat pump. It is worthwhile investigating whether your particular type of old radiator is likely to cause more particle problems than modern radiators. I have no experience or understanding of that.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
@seaviews Agree with the others on sequence: loft first, then resize. On the cast-iron you plan to keep for now, you can check room by room in about an hour.
For each radiator note height, columns and sections. Makers publish W per section at ΔT50; old ones are close enough if you match height and columns. At heat-pump temps output is roughly 0.4x that figure at ~45 C mean water, about 0.5x around 50 C. Put that next to each room's loss and any room that fails jumps out.
Made-up example: 12-section 4-column at ~110 W/section is ~1320 W at ΔT50, so ~500 W at 45 C mean water. An upstairs bedroom under a bare loft can need ~1000 W; with 300 mm loft insulation more like 400-500 W. Same radiator, from clearly short to fine.
So loft first may retire some radiator decisions on its own. There are also easy tools to help with the calculation like heatlosspro.cloud for example.