Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Problems with sizing a replacement for a Viessmann Vitocal 200-S

37 Posts
6 Users
12 Reactions
242 Views
 jon
(@jon)
Active Member Member
Joined: 3 years ago
Posts: 12
Topic starter  

@judith Thanks very much for this! My room by room calculation, done on my own spreadsheet, comes out at about 18 kW. I've also found the original Nu-Heat UFH design sheets, which also show around 18 kW (although it gets some rooms completely wrong, mostly as they get too hot). 

Then I worked out the flow rate from the secondary pump on the internal unit, which feeds the buffer cylinder. As I don't have a flow meter, I did this by charging the buffer with the flow and return to the UFH and rads closed. I used this to recalculate the measured delivered heat by source for the 2024 - 2025 season:

measured delivered heat by source

 This pretty much agrees with the previous calculations in the colder bands, but diverges as it gets milder. This is a much better fit and again agrees with the gas only regression which gave around the same figure at a design temperature of -3. So the house draws around 13 kW at -3 with gains present. The 12 hour sustained peak was 13.7 kW. Adding in a margin for the coldest bin, the boiler efficiency being 90% and the house actually being heated to 23.5 C (rather too hot, I know!), gives a heat pump sizing of 16 kW delivered at A-3/W35.

Posted by: @judith

Your house ought to be more thermally efficient from its build standard so you probably won’t need 2.5 times our usage to heat it (ratio of floor areas). 

Your 5 January figure, corrected by your own 5 per cent, is 169 kWh over 24 hours in 200 m2. That is 7.0 kW average, or 35.2 W/m2, at 21 C internal.

My nearest equivalent is 147 hours in the -2 to 0 band last season, at 11.2 kW. Over 571 m2 that is 19.6 W/m2, while holding the house at about 23.5 C rather than 21. That's around 1.53 W/m2K conductance for yours against 0.82 for mine.

Posted by: @judith

Your extrapolation to -3/-4 is indeed eye watering and perhaps you might consider plotting error bars on the data and slope?

I haven't done this yet, but will post again once I have!

 

 

 



   