Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Problems with sizing a replacement for a Viessmann Vitocal 200-S
@judith Thanks very much for this! My room by room calculation, done on my own spreadsheet, comes out at about 18 kW. I've also found the original Nu-Heat UFH design sheets, which also show around 18 kW (although it gets some rooms completely wrong, mostly as they get too hot).
Then I worked out the flow rate from the secondary pump on the internal unit, which feeds the buffer cylinder. As I don't have a flow meter, I did this by charging the buffer with the flow and return to the UFH and rads closed. I used this to recalculate the measured delivered heat by source for the 2024 - 2025 season:
This pretty much agrees with the previous calculations in the colder bands, but diverges as it gets milder. This is a much better fit and again agrees with the gas only regression which gave around the same figure at a design temperature of -3. So the house draws around 13 kW at -3 with gains present. The 12 hour sustained peak was 13.7 kW. Adding in a margin for the coldest bin, the boiler efficiency being 90% and the house actually being heated to 23.5 C (rather too hot, I know!), gives a heat pump sizing of 16 kW delivered at A-3/W35.
Posted by: @judithYour house ought to be more thermally efficient from its build standard so you probably won’t need 2.5 times our usage to heat it (ratio of floor areas).
Your 5 January figure, corrected by your own 5 per cent, is 169 kWh over 24 hours in 200 m2. That is 7.0 kW average, or 35.2 W/m2, at 21 C internal.
My nearest equivalent is 147 hours in the -2 to 0 band last season, at 11.2 kW. Over 571 m2 that is 19.6 W/m2, while holding the house at about 23.5 C rather than 21. That's around 1.53 W/m2K conductance for yours against 0.82 for mine.
Posted by: @judithYour extrapolation to -3/-4 is indeed eye watering and perhaps you might consider plotting error bars on the data and slope?
I haven't done this yet, but will post again once I have!
Posted by: @jonYour extrapolation to -3/-4 is indeed eye watering and perhaps you might consider plotting error bars on the data and slope?
I haven't done this yet, but will post again once I have!
R (The R Project for Statistical Computing, I use it with R Studio) can do and plot confidence intervals for regression lines but I suspect they will end up looking like a cartoon blunderbuss given the data you have. R is not for the fainthearted, but it is extremely capable, and produces very high quality plots.
It might also be worth doing a residuals plot.
I take it you are also following the Adventures in heat loss calculations thread, if not, you may want to take a look, asit has some useful stuff in it.
Midea 14kW (for now...) ASHP heating both building and DHW
- 27 Forums
- 2,809 Topics
- 66.4 K Posts
- 2,515 Online
- 7,215 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
There's a company called Xlinks who are proposing just ...
By Transparent , 5 minutes ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 hours ago
-
RE: Octopussy cosy 6 experience
@paultheheating Unless things have changed more recentl...
By Toodles , 17 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Sorry I thought and meant to put 'may' in, but the diff...
By JamesPa , 20 hours ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 22 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
Potentially the largest data centre hub in Europe and t...
By Jeff , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 2 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 2 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 2 days ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@etchedpixels Agreed, just a thought for others. I am...
By Watcher , 3 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 4 days ago
-
Coming back on subject... A shortened version of the ...
By Transparent , 4 days ago
-
RE: Say hello and introduce yourself
Perhaps it is time for an update on ‘our’ project. We h...
By Toodles , 4 days ago
-
RE: Free app: run the immersion / heat pump from Growatt battery & solar surplus – no Home Assistant
Please bear in mind, everyone, that in order to use thi...
By Majordennisbloodnok , 6 days ago