Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Problems with sizing a replacement for a Viessmann Vitocal 200-S
@judith Thanks very much for this! My room by room calculation, done on my own spreadsheet, comes out at about 18 kW. I've also found the original Nu-Heat UFH design sheets, which also show around 18 kW (although it gets some rooms completely wrong, mostly as they get too hot).
Then I worked out the flow rate from the secondary pump on the internal unit, which feeds the buffer cylinder. As I don't have a flow meter, I did this by charging the buffer with the flow and return to the UFH and rads closed. I used this to recalculate the measured delivered heat by source for the 2024 - 2025 season:
This pretty much agrees with the previous calculations in the colder bands, but diverges as it gets milder. This is a much better fit and again agrees with the gas only regression which gave around the same figure at a design temperature of -3. So the house draws around 13 kW at -3 with gains present. The 12 hour sustained peak was 13.7 kW. Adding in a margin for the coldest bin, the boiler efficiency being 90% and the house actually being heated to 23.5 C (rather too hot, I know!), gives a heat pump sizing of 16 kW delivered at A-3/W35.
Posted by: @judithYour house ought to be more thermally efficient from its build standard so you probably won’t need 2.5 times our usage to heat it (ratio of floor areas).
Your 5 January figure, corrected by your own 5 per cent, is 169 kWh over 24 hours in 200 m2. That is 7.0 kW average, or 35.2 W/m2, at 21 C internal.
My nearest equivalent is 147 hours in the -2 to 0 band last season, at 11.2 kW. Over 571 m2 that is 19.6 W/m2, while holding the house at about 23.5 C rather than 21. That's around 1.53 W/m2K conductance for yours against 0.82 for mine.
Posted by: @judithYour extrapolation to -3/-4 is indeed eye watering and perhaps you might consider plotting error bars on the data and slope?
I haven't done this yet, but will post again once I have!
Posted by: @jonYour extrapolation to -3/-4 is indeed eye watering and perhaps you might consider plotting error bars on the data and slope?
I haven't done this yet, but will post again once I have!
R (The R Project for Statistical Computing, I use it with R Studio) can do and plot confidence intervals for regression lines but I suspect they will end up looking like a cartoon blunderbuss given the data you have. R is not for the fainthearted, but it is extremely capable, and produces very high quality plots.
It might also be worth doing a residuals plot.
I take it you are also following the Adventures in heat loss calculations thread, if not, you may want to take a look, asit has some useful stuff in it.
Midea 14kW (for now...) ASHP heating both building and DHW
- 27 Forums
- 2,788 Topics
- 65.9 K Posts
- 3,367 Online
- 7,192 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@ashp-bobba I don’t think it would kill the heat pump i...
By Mars , 10 minutes ago
-
RE: Why are ASHP installs so expensive?
@rob-of-york I think the most revealing question here i...
By Mars , 37 minutes ago
-
RE: Does anyone have experience of a smart water meter?
@downfield You are opening a whole can of cans there!
By Toodles , 39 minutes ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
I found some interesting data about the price of heat p...
By Rob of York , 5 hours ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
Thanks for that, quite interesting. I liked the bit a...
By springswood , 6 hours ago
-
RE: PV and battery long payback - sense check query
Thanks for all the comments. I finally got to the bott...
By DavidB , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
People following this thread who are hoping that plug i...
By JamesPa , 17 hours ago
-
Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
Whilst searching for other information I came across th...
By JamesPa , 17 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
By Singlespeed , 19 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
just had Vaillant over to service the HP and asked abou...
By AdamK , 19 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
OK so ZEB is basically a variant on a storage heater, b...
By JamesPa , 2 days ago
-
RE: Heat Geek installations: share your experiences
@editor I suspect that the Heat Geek online quote is a ...
By AndrewJ , 2 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
Ah, yes. Thanks for clarifying.
By Transparent , 2 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
@trebor12345 I have been meaning to get home assista...
By Batpred , 3 days ago