Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Problems with sizing a replacement for a Viessmann Vitocal 200-S
@judith Thanks very much for this! My room by room calculation, done on my own spreadsheet, comes out at about 18 kW. I've also found the original Nu-Heat UFH design sheets, which also show around 18 kW (although it gets some rooms completely wrong, mostly as they get too hot).
Then I worked out the flow rate from the secondary pump on the internal unit, which feeds the buffer cylinder. As I don't have a flow meter, I did this by charging the buffer with the flow and return to the UFH and rads closed. I used this to recalculate the measured delivered heat by source for the 2024 - 2025 season:
This pretty much agrees with the previous calculations in the colder bands, but diverges as it gets milder. This is a much better fit and again agrees with the gas only regression which gave around the same figure at a design temperature of -3. So the house draws around 13 kW at -3 with gains present. The 12 hour sustained peak was 13.7 kW. Adding in a margin for the coldest bin, the boiler efficiency being 90% and the house actually being heated to 23.5 C (rather too hot, I know!), gives a heat pump sizing of 16 kW delivered at A-3/W35.
Posted by: @judithYour house ought to be more thermally efficient from its build standard so you probably won’t need 2.5 times our usage to heat it (ratio of floor areas).
Your 5 January figure, corrected by your own 5 per cent, is 169 kWh over 24 hours in 200 m2. That is 7.0 kW average, or 35.2 W/m2, at 21 C internal.
My nearest equivalent is 147 hours in the -2 to 0 band last season, at 11.2 kW. Over 571 m2 that is 19.6 W/m2, while holding the house at about 23.5 C rather than 21. That's around 1.53 W/m2K conductance for yours against 0.82 for mine.
Posted by: @judithYour extrapolation to -3/-4 is indeed eye watering and perhaps you might consider plotting error bars on the data and slope?
I haven't done this yet, but will post again once I have!
Posted by: @jonYour extrapolation to -3/-4 is indeed eye watering and perhaps you might consider plotting error bars on the data and slope?
I haven't done this yet, but will post again once I have!
R (The R Project for Statistical Computing, I use it with R Studio) can do and plot confidence intervals for regression lines but I suspect they will end up looking like a cartoon blunderbuss given the data you have. R is not for the fainthearted, but it is extremely capable, and produces very high quality plots.
It might also be worth doing a residuals plot.
I take it you are also following the Adventures in heat loss calculations thread, if not, you may want to take a look, asit has some useful stuff in it.
Midea 14kW (for now...) ASHP heating both building and DHW
- 27 Forums
- 2,787 Topics
- 65.8 K Posts
- 1,140 Online
- 7,192 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
@rob-of-york My reasoning for the move away from storag...
By Paul1098 , 14 minutes ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Yes to the final sentence. There are actually two cont...
By JamesPa , 45 minutes ago
-
RE: Missing flow temperature in Heat Geek proposal
@ashp-bobba It is very pleasing to me to hear that the ...
By Toodles , 45 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
The main issue is that the items you want to power are ...
By JamesPa , 7 hours ago
-
RE: battery storage without solar
Also don't forget that in you may not be able to use th...
By JamesPa , 9 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
One practical safeguard is to separate the calibration ...
By EnergyStorageTech , 10 hours ago
-
RE: Nook batteries from Octopus
Until Octopus publishes the electrical limits, the key ...
By EnergyStorageTech , 15 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
There is at least one large scale system in this catego...
By Toodles , 23 hours ago
-
RE: Getting closer to a finished Haier system
Apart from sealing the external Primary Pro joints and ...
By Singlespeed , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@jamespa Hope someone tries it! As a consumer, I woul...
By Batpred , 2 days ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
Our latest Homeowners’ Q&A episode has just dropped...
By Mars , 2 days ago
-
RE: Vaillant ecoTEC Plus with sensoCOMFORT and weather compensation
Yes, its described in the sensocomfort manual. Its als...
By JamesPa , 2 days ago
-
RE: Heat Geek installations: share your experiences
My summary, highlighting the oddities.
By Batpred , 2 days ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
What a day yesterday! Two podcasts recorded, brilliant ...
By Mars , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
I too use AI when researching online. It's able to co...
By Transparent , 3 days ago