Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Vaillant ecoTEC Plus - Flow Temp and Set Up

25 Posts
3 Users
4 Reactions
1,234 Views
trebor12345
(@trebor12345)
Reputable Member Member
Joined: 3 years ago
Posts: 223
Your energy: 8 kWh
Topic starter  

Posted by: @jamespa
↑

If you extrapolate the heat curve you posted linearly it hits 29 at 2.5C at which point it will flatline because you have (apparently) set 29 min.  I dont know that its exactly linear and nor do I know the precision with which it adjusts FT.  I would guess it might be 0.1C but its just as likely to be some odd fraction that works out well in binary, or even 0.5C.  I also dont know the precision with which it measures flow temperature.  Until temp falls below zero for a few hours I wouldn't be worried if I didn't see a change other than in  compressor modulation depth which will respond to demand.

I think I have better handle on this now.  Because my system is sitting on a 29°C minimum-flow-temperature floor at around 2°C outside, the compressor is increasing output instead. As the outside temperature stays colder and the curve's target rises above that floor, I should eventually see the flow temperature rise.  There will always be delays/misalignments as it adjusts so the relationship will not ever be perfect unless OAT stabilises for a long period of time.  

Now wait and see what happens.

 


2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3


   