Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Surge Protection Devices

63 Posts
7 Users
14 Reactions
2,666 Views
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5002
 

@batpred of course you could just leave out the RCD altogether which is what my electrician did.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Batpred
(@batpred)
Noble Member Member
Joined: 1 year ago
Posts: 993
 

@jamespa 

I suggested to have a Contactum RCBO and the installer´s anxiety was very clear! Obviously the Hager CU is worth it, to avoid the emergency electricians that he had in the past. And not knowing for sure if the DC leakage is solved, I definitely want to make sure it is in place - we are resigned to add yet another CU to our collection. We kept some old CUs, but clearly this large RCCB comes with a matching Hager CU. 

The other topic that we became aware of is that the Arotherm Pro heatpump is still not in the ENA list. I have no idea if the special RCBO that is needed for the current Plus is listed nor whether the Pro will also have it. It reminded me that the DNO step is an application, not a notification. 🤨  


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 3249
 

Posted by: @batpred

And not knowing for sure if the DC leakage is solved,

The issue isn't DC leakage.

Type-B RCDs and RCBOs will trip correctly despite the waveform having a DC component present.

You need the contacts to open when there is a genuine difference of 30mA or more between the AC current being supplied via the Live and returning in the Neutral. A Type-B will do so; ie the DC element is ignored.

 

The presence of a DC component is usually regarded as an undesirable effect imposed by EV Chargers.

The presence of harmonics is generally associated with heat-pumps.

It seems odd to me that Vaillant have introduced an AC to DC power supply into their ASHPs which is imposing both errors onto the mains incomer to sufficient extent that the company has teamed up with Hager to recommend a particular protection trip. The message it gives to me is "our power supply design isn't good, and we haven't fitted HF filters either!"

Consumers shouldn't be asked to spend £600 having an expensive RCD fitted just because the heat-pump power supply has design deficiencies.

 

HarmonicImbalance

I've created the above timeline from spreadsheet date sent to me by a DNO.

It shows the absolute deviation of voltage imbalances which are being passed through local substations and on to the higher voltages of the Distribution Grid (11kV and above).

Whilst losses due to phase imbalances are substantially occurring only at the local substation level, harmonics pass right through every transformer on the grid. This is what causes the audible hum when you're in the vicinity of larger transformers. That's energy being lost.


Save energy... recycle electrons!


   
ReplyQuote