Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Surge Protection Devices

56 Posts
7 Users
12 Reactions
2,636 Views
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 163
Topic starter  

Posted by: @jamespa

Posted by: @trebor12345

The requirement for me came from the following document.

Screenshot 2026 06 11 at 09.52.46

 

 

 

@trebor12345 

Noted.  As I say the Valiant installation manual I have does not require an RCD, but does specify the type if one is fitted.

I would say that the document above could be read either way however if you read it as RCD mandatory then a fuse is also mandatory and hardly anyone is going to fit one of those.  Thus I would personally refer to the installation manual for clarification.

This was a bit of a nightmare when I discussing my install with the provider.  However, the install manual also stated that I need this:

 

Screenshot 2026 06 11 at 14.21.32

 


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 163
Topic starter  

Posted by: @transparent

Although we can't see the part number on that photo above, I assume that the Hager RCD in the upper consumer unit is this one.

here's a close up of what is installed.

IMG 0569

 


2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 3247
 

I'm 90% certain that the device you have does not operate as over-current protection.

The number of Amps stated on it are the rating of the contacts. It doesn't trip out if you exceed that.

What is the part number printed above the blue button?


Save energy... recycle electrons!


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4998
 

Posted by: @trebor12345

Posted by: @jamespa

Posted by: @trebor12345

The requirement for me came from the following document.

Screenshot 2026 06 11 at 09.52.46

 

 

 

@trebor12345 

Noted.  As I say the Valiant installation manual I have does not require an RCD, but does specify the type if one is fitted.

I would say that the document above could be read either way however if you read it as RCD mandatory then a fuse is also mandatory and hardly anyone is going to fit one of those.  Thus I would personally refer to the installation manual for clarification.

This was a bit of a nightmare when I discussing my install with the provider.  However, the install manual also stated that I need this:

 

Screenshot 2026 06 11 at 14.21.32

 

Same as I quoted, no requirement for an RCD to be fitted but if one is fitted then it must be of a specific type.  I think that's very clear and also entirely logical.

Not sure why they use the word 'fuse'.  Most installations will use MCBs these days.  Maybe it's a translation from the German or Czech.

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 3247
 

Hager CDB540HP is a Residual Current Circuit Breaker.

Here's the English text in the Installation Manual.
It measures current which leaks to earth.

image

It needs an MCB in series to provide over-current protection.

The current rating of the MCB is determined by the cable-size which supplies the Heat Pump.
Do you know what that is?


Save energy... recycle electrons!


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4998
 

@transparent. It looks from the picture posted earlier as if this RCD is fed from the main cu.  That being the case perhaps there is an MCB in series there


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 3247
 

OP wrote:

Posted by: @trebor12345

There is NO MCB in the main consumer unit for the heat pump. 

So I'd be interested to know where the feed to the new CU is supplied from...
... and what size cable it has between the two units.


Save energy... recycle electrons!


   
👍
1
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4998
 

Posted by: @transparent

OP wrote:

Posted by: @trebor12345

There is NO MCB in the main consumer unit for the heat pump. 

So I'd be interested to know where the feed to the new CU is supplied from...
... and what size cable it has between the two units.

Sorry missed that.  It's pretty obvious from the photo that this RCD is fed from the main cu, but if there is no MCB then, as you say, what protects the cable?

?x79161

 


This post was modified 27 minutes ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote