Surge Protection De...
Surge Protection Devices
7 Users
18 Reactions
19.2 K Views
trebor12345
(@trebor12345)
Your energy: 13 kWh
Posted by: @trebor12345
The requirement for me came from the following document.
Screenshot 2026 06 11 at 09.52.46
@trebor12345
Noted.  As I say the Valiant installation manual I have does not require an RCD, but does specify the type if one is fitted.
I would say that the document above could be read either way however if you read it as RCD mandatory then a fuse is also mandatory and hardly anyone is going to fit one of those.  Thus I would personally refer to the installation manual for clarification.
This was a bit of a nightmare when I discussing my install with the provider.  However, the install manual also stated that I need this:
Screenshot 2026 06 11 at 14.21.32
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3
trebor12345
(@trebor12345)
Your energy: 13 kWh
Posted by: @transparent
Although we can't see the part number on that photo above, I assume that the Hager RCD in the upper consumer unit is this one.
here's a close up of what is installed.
IMG 0569
50 litre volumiser
3.6KW solar panels
Your energy: 110 kWh
I'm 90% certain that the device you have does not operate as over-current protection.
The number of Amps stated on it are the rating of the contacts. It doesn't trip out if you exceed that.
What is the part number printed above the blue button?
Your energy: 161 kWh
@trebor12345
Same as I quoted, no requirement for an RCD to be fitted but if one is fitted then it must be of a specific type.  I think that's very clear and also entirely logical.
Not sure why they use the word 'fuse'.  Most installations will use MCBs these days.  Maybe it's a translation from the German or Czech.
Hager CDB540HP is a Residual Current Circuit Breaker.
Here's the English text in the Installation Manual.
It measures current which leaks to earth.
It needs an MCB in series to provide over-current protection.
The current rating of the MCB is determined by the cable-size which supplies the Heat Pump.
Do you know what that is?
@transparent. It looks from the picture posted earlier as if this RCD is fed from the main cu.  That being the case perhaps there is an MCB in series there
There is NO MCB in the main consumer unit for the heat pump.
So I'd be interested to know where the feed to the new CU is supplied from...
... and what size cable it has between the two units.
Sorry missed that.  It's pretty obvious from the photo that this RCD is fed from the main cu, but if there is no MCB then, as you say, what protects the cable?
?x79161
This post was modified 6 months ago by JamesPa
trebor12345
(@trebor12345)
Your energy: 13 kWh
I stand corrected on this, there is a 20 Amp MCB feeding the heat pump.
50 litre volumiser
3.6KW solar panels
trebor12345
(@trebor12345)
Your energy: 13 kWh
I don't know specifically but based on physical size, it looks like standard twin and earth that would be used on a 13 Amp socket.  This is the feed from the CU to the Heat Pump.
This post was modified 6 months ago by trebor12345
50 litre volumiser
3.6KW solar panels
(@batpred)
Your energy: 31 kWh
I don't understand why the electrician working for @trebor12345 chose this particular Hager unit.
Based on what I was told and read, because Vaillant and Hager collaborated to design this heatpump RCCB model. So marketing appears to have used that as a springboard. Most of the electricians seem to know the Hager solution as a way to reduce nuisance tripping, etc.
We are planning to get a Vaillant so most of the installers that estimated for us seemed aware of this.
The situation of requiring such a specific RCCB is hopefully transitional. Vaillant would probably want to remove this complication by:
  • designing out the possibility of DC currents;
  • or incorporating a suitable circuit protection device in their unit.
The current Vaiilant manual says the same as mine, IE it specifies the type of RCD if an RCD is fitted, but does not specify that an RCD must be fitted.  That latter decision is, by implication, left to the installer/local regs.
I had a look at the German language documentation for the Arotherm Pro (no British version available).
It only includes a generic mention that implies an RCD/RCCB is not mandatory:
"If prescribed for the installation location, check whether an RCD has been installed"
I also did a deep search for any references to any special type of RCD but could not find anything for the Pro (e.g. VWL 75/7.1 for the 7kw model). Perhaps this new model is the first that no longer needs DC capable residual current circuit breakers.
This post was modified 6 months ago 2 times by Batpred
trebor12345
(@trebor12345)
Your energy: 13 kWh
Posted by: @batpred
The electrician was an employee of the company that performed the HP design and installation. As part of the design process I felt it was a mandatory requirement.
50 litre volumiser
3.6KW solar panels
Page 5 / 7