Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Recommended home battery inverters + regulatory matters - help requested
Posted by: @transparentPosted by: @transparentEqually, an electrician will understand that the Change-over switch must not be positioned within a CU alongside MCBs supplying other circuits.
We're discussing a situation where the change-over switch is in a separate enclosure, for reasons which I hope are now obvious.Not to me I must say. Whats the additional risk exactly that is not covered by a label.
I keep in mind the following two checks:
a: by modifying a design/schematic am I increasing safety (lowering risk) ?
b: is my strategy providing flexibility without compromising system resilience ?
On this forum we are already advocating the use of a separate double-pole isolator on the incomer wires to a CU.
It's not mandatory.
But it allows an electrician to work in a CU without the 240v input to the Main Switch being live.
In your case @jamespa the Changeover Switch in a separate enclosure would also provide that functionality via a Centre-Off position.
Placing a switch (that already requires a Warning Label) inside that CU increases the risk level,
and it does so beyond the level normally met by a double-pole Main Switch with a 240v incomer.
There is a reason that "Danger 440v" and "Danger 415v" signs exist.
They demonstrate a commitment to reduce risk under ISO 7010, and the Health and Safety at Work Act.
And they comply with the IET Wiring Regulations (BS7671), section 514.10.1
[...] a warning notice must be installed where a nominal voltage exceeding 230 V to earth (or 400 V between lines) exists
within an enclosure or on equipment, particularly where such a voltage would not normally be expected.
Posted by: @jamespaFurthermore if the ups and downs of the grid as it switched on are likely to damage electronics, which you suggest above, then everyone without an inverter faces this risk.
Not quite.
A hybrid inverter is itself a generator.
It can create harmonics and spikes locally (within the home).
Those don't have the benefit of being suppressed by the capacitance of the long length of cable between the home and a local substation.
You really want the grid mains to be stable before offering it as the supply to an inverter.
Save energy... recycle electrons!
Posted by: @transparentPosted by: @batpredOne thing to be aware is that this 440V/different phases in various sockets should not normally happen, not with this Solis S6 hybrid.
We're discussing 440v being present inside the enclosure which houses the change-over switch.
There needs to be a warning.
An electrician can then be sufficiently aware of the situation to ensure that the cover of that enclosure is in place before switching the house back on
following whatever work or tests might have been carried out.
The regulation mandates labels indicating that there are multiple generation sources in the site. My installation has this, but for better awareness (and for eventual future residents), we will add 4xxV labels to the switch and isolator.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @transparentIn your case @jamespa the Changeover Switch in a separate enclosure would also provide that functionality via a Centre-Off position.
That would make sense; the 2 off mcbs would need to go in the same enclosure so the challenge might be to find the right kit of parts! A quick search didn't turn up any din mounted 4 pole 100A changeover switches with centre off other than an unbranded Chinese one. Hopefully one exists!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @batpredThe regulation mandates labels indicating that there are multiple generation sources in the site.
Would you care to say which regulation you're referring to?
In my quest for safe practice I am often 'fed' relevant clips on YouTube.
This one from eFIXX about possible types of Neutral and Earthing faults is informative.
On this forum I don't think we can conjecture all the possible fault scenarios which inverter wiring should provide a level of protection against.
But videos like this give me sufficient 'feel' for the subject that I find myself erring on the side of reducing risk.
That seems the right way to be going.
Save energy... recycle electrons!
Posted by: @transparentPosted by: @batpredThe regulation mandates labels indicating that there are multiple generation sources in the site.
Would you care to say which regulation you're referring to?
When I was looking for the regs for labelling when introducing an inverter able to export, I started with some of the questions present in the G99 commissioning form like:
- Generator’s Installation satisfies the requirements of BS7671 (IET Wiring Regulations).
- Suitable lockable points of isolation have been provided between the PGMs and the rest of the Generator’s Installation.
- Labels have been installed at all points of isolation in accordance with EREC G99.
As I wanted to make sure the electrician would have the required labels, I purchased a set of labels of the type suitable for a PV installation. A subset of these were then applied in and around the consumer unit and inverter. Something like the below:
For guidelines including an overview of labelling, this IET article seems relevant. Ultimately, qualified electricians have access to the current regulations.
Posted by: @transparentOn this forum I don't think we can conjecture all the possible fault scenarios which inverter wiring should provide a level of protection against.
But videos like this give me sufficient 'feel' for the subject that I find myself erring on the side of reducing risk.That seems the right way to be going.
Yes and it can be very difficult to give advice without assessing all the site conditions. The video you shared seems to focus on risks related to earthing, but I appreciate it is not easy to find one describing specific islanding inverter topics.
My approach has been that, given how few domestic electricians have extensive experience with inverters, etc, it helps readers to become informed owners. They may be able to do some of the planning. Whilst using an electrician is essential, more knowledge helps. I do not even envision trying to understand all the extensive considerations that MCS would impose on this type of installation work, in terms of ideal calculations of ROI, etc (mainly because, at the end of the day, MCS does not provide a guarantee themselves..).
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
I’m quite intrigued by sodium ion batteries over lithium. Does anyone on the forums have one running at home?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editorI’m quite intrigued by sodium ion batteries over lithium. Does anyone on the forums have one running at home?
We discussed this recently in the Sodium battle thread, @editor . There are very few systems available to consumers and they do not look very mature. Inverters able to handle sodium are significantly different, so the initially available systems are not modular (like commonly available lithium based systems).
The current low starting price for lifepo4 batteries and the expectation (given the relative cost of lithium vs sodium) that sodium based would be lower cost does not indicate a fast uptake...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @editorI’m quite intrigued by sodium ion batteries over lithium.
See what I posted over on that other topic:
Posted by: @transparentPrices are very similar to FePO4 but the nominal cell-voltage is slightly lower (3.1v instead of 3.2v)
and the operational range is much wider (1.5v - 4.1v).
Suppose your Na-ion battery was to supply a heat-pump which required 3kW (at 240v)...
and that you had 16 cells in series.
A fully charged sodium battery with cells at 4.1v would be operating at 65½v and delivering 45A to the inverter.
As it reaches 10% capacity, the battery voltage would've fallen to about 48v (3.0v per cell – see green curve below)
At 48v the inverter would now be drawing 62A current from the sodium battery.
Although the sodium battery would happily allow you to use that last 10% of capacity, the increased current you'd need means that it's unviable.
The cabling would need to be thicker to carry currents in excess of 100A, and the BMS capable of handling that too.
For that reason a system based on sodium ion chemistry requires inbuilt cut-offs to limit the current,
as opposed to Li-ion technology which has limits imposed to prevent damage to the cell electrodes.
The concepts are similar, but the approach is slightly different due to the wider voltage range.
Save energy... recycle electrons!
Posted by: @dr_dongle...
and you have to charge the PW3 (albeit at cheap rate). I reckon this saves about £1/day over a standard tariff for a cost of the order of at least £8k installed. I understand that the top end battery storage systems come with guarantees of up to 15 years but in most cases capacity losses at 10 years will be 10-20% - all of which adds up to at least £500 per annum in depreciation. Unless I've messed up my figures then I can't make it cost effective.
That makes sense. I thought better to comment in this thread.
Modular systems like Fox seem to now be available including from big players like Octopus with installation included and at much lower price points. No endorsement intended.
And the DIY route that a site like RHH enables makes a system with 8kw hybrid inverter and 16kwh life04 battery (that even provides UPS capability), possible for less than £3k all included. Depending on your location, you may be on positive ground before year 3. In that type of scenario, unless the tariffs change very quickly and in unusual ways, the investment seemed fairly low risk. In my case, much faster payback and less headaches than PV.
In this thread we were looking at ways to combine several inverters in the same installation, so potentially applicable. Even if the prospect of upgrading a PW based systems by using it to feed a Solax, Sunsynk or Solis may cause severe anxiety to Tesla salespeople..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @jamespaI must say I don't much care for the Solis instruction manual which does concern me, the Sunsynk one is much better. On the other hand Solis have answered my questions, I have yet to ask any of Sunsynk.
Hi, just curious on whether you progressed your upgrade and what you chose?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredPosted by: @jamespaI must say I don't much care for the Solis instruction manual which does concern me, the Sunsynk one is much better. On the other hand Solis have answered my questions, I have yet to ask any of Sunsynk.
Hi, just curious on whether you progressed your upgrade and what you chose?
I haven't, I still cant make the business case work with less than 10 years payback relative to just sticking with Octopus Go and loading as much as I reasonably can into the overnight period.
Probably if I didn't already have solar panels (and a functioning solar inverter) it would make more sense, but I do! Ho hum.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @batpredHi, just curious on whether you progressed your upgrade and what you chose?
I haven't, I still cant make the business case work with less than 10 years payback relative to just sticking with Octopus Go and loading as much as I reasonably can into the overnight period.
I suppose if your pv inverter packs up, you have a plan?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,644 Topics
- 61.7 K Posts
- 517 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 10 hours ago
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
@jamespa that’s actually a really interesting observati...
By Mars , 11 hours ago
-
RE: How many people are happy with their ASHP and do you believe them?
Good luck, I spent a couple of hours and, whilst I foun...
By JamesPa , 11 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 19 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 20 hours ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 21 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 22 hours ago
-
Mentally you have to separate the ac side and the DC si...
By JamesPa , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 3 days ago
-
Hard to tell but I think I have placed the arrow on wha...
By ASHP-BOBBA , 4 days ago