Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Adding 5 More Panels to My Growatt Inverter – Second String Questions on Specs, Cabling & Configuration

45 Posts
6 Users
6 Reactions
853 Views
(@david999)
Reputable Member Member
Joined: 2 years ago
Posts: 338
Topic starter  

That’s the solar up and running, I don’t think it’s the most attractive addition to my property but very practical.  It’s all bolted down and the tubs also filled with broken up pavers so I hope they don’t go flying in a storm.  At the minute the 6 on my house at 2.4 max and the 5x510 panels are producing 4kwh. A bit overcast today but I’m pleased at that. 

a big thank you to you all, especially transparent who is a star

IMG 8268
IMG 8269
IMG 8267
IMG 8257

 



   
ReplyQuote
(@david999)
Reputable Member Member
Joined: 2 years ago
Posts: 338
Topic starter  

I have just installed another string and now doubled my solar to 4.9 from the registered original 2.6.  Currently output is around 4kwh, do I need to inform the DNO, will they know and will I be in trouble for not informing them. 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4928
 

If you have added or changed the inverter then definitely yes. Otherwise possibly not because they care only about the inverter which is what determines the max output to grid.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@david999)
Reputable Member Member
Joined: 2 years ago
Posts: 338
Topic starter  

@jamespa same inverter, just added another string to the spare input.  I read somewhere that a max of 3.6 output was the max allowed in a domestic and I am sending out 4 on a good day. It’s hardly likely to cause an overload though and it’s only producing that on a good day.  Oversized to provide a decent output, most of the time it never got near the 2.6 of the previous panels.



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4928
 

Your inverter should limit power to the grid to 16A/3.68 kW unless you received permission for greater.  If it's not doing that then it has potentially not been correctly configured.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@temperature_gradient)
Trusted Member Member
Joined: 9 months ago
Posts: 47
 

Posted by: @david999

I have just installed another string and now doubled my solar to 4.9 from the registered original 2.6.  Currently output is around 4kwh, do I need to inform the DNO, will they know and will I be in trouble for not informing them. 

There's a threshold at 3.6kW / 16A, below this follows one process G98 which is typically connect and then notify with this being permitted, above this is G99 and you typically need to apply and get permission for these larger capacity installations.

More details on the ENA website - these are the standard processes most of the industry follows to give you some guidance. You should also look at the website for your local distribution network operator to see exactly what their processes require.

https://www.energynetworks.org/industry/connecting-to-the-networks/connecting-generation-to-the-electricity-networks

 



   
ReplyQuote
(@david999)
Reputable Member Member
Joined: 2 years ago
Posts: 338
Topic starter  

@jamespa my total dc voltage is 490 and the inverter max is 550.  I’m getting confused regarding outputs but it looks like I’m within the working loads. As you say my inverter won’t go beyond that 3680 kw.  Bit confusing the dc max and kw max of panels, but I think I understand now.



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4928
 

Mentally you have to separate the ac side and the DC side.  The ac side will cap the output if it is set up to do so. 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@old_scientist)
Honorable Member Member
Joined: 2 years ago
Posts: 406
 

Posted by: @david999

I have just installed another string and now doubled my solar to 4.9 from the registered original 2.6.  Currently output is around 4kwh, do I need to inform the DNO, will they know and will I be in trouble for not informing them. 

Yes, you will need to notify them even if the inverter remains the same. You originally had 2.55kW of generating capacity installed so would not have reached your inverter's rated 3.6kW output limit, but with the extra panels you will now be able to achieve the full 3.6kW and the DNO will want to know about that change as it affects the amount of export you will be able to achieve, although still within G98 limits.

 


Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.


   