Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Sensotherm puzzle
Replacement Vaillant heat pump installed, with sensotherm controls. Two zones upstairs and downstairs.
Downstairs has underfloor heating, and three existing room thermostats. All heating fine.
Upstairs has radiators on one loop, and the sensotherm should control them, but nothing happens when the desired temperature is higher than the room temperature.
Installer has checked the installation with Vaillant technical support on the phone, but still nothing happening.
Anyone else had a similar problem?
Sorry to hear about the problems, its going to be something fixable for sure.
Posted by: @gutoffowcAnyone else had a similar problem?
No (I have only one zone) but the obvious questions are
- What is controlling the demand for heat to the heat pump?
- What is controlling the zone valves?
- What if any schedule have you got on the zones?
- What room influence mode is set, what are the weather compensation settings
- How are the thermostats connected?
- How does the behaviour differ according to whether downstairs is 'on' or not?
And of course
- Why do you need 2* zones in the first instance, with it's inevitable complexity. Why not run single zone?
There are a fair number of possible reasons but they almost all come down to the control strategy (including any zone valves), not the heat pump which may be why Vaillant can't immediately help. Did your installer think through the control strategy properly, or just assume that the more knobs there are to turn the better?
Do you have a controls diagram (and if not Im wondering how your installer knows that the controls design should work)?
*5 zones if the thermostats are still functional!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaSorry to hear about the problems, its going to be something fixable for sure.
Posted by: @gutoffowcAnyone else had a similar problem?
No (I have only one zone) but the obvious questions are
- What is controlling the demand for heat to the heat pump?
- What is controlling the zone valves?
- What if any schedule have you got on the zones?
- What room influence mode is set, what are the weather compensation settings
- How are the thermostats connected?
- How does the behaviour differ according to whether downstairs is 'on' or not?
And of course
- Why do you need 2* zones in the first instance, with it's inevitable complexity. Why not run single zone?
There are a fair number of possible reasons but they almost all come down to the control strategy (including any zone valves), not the heat pump which may be why Vaillant can't immediately help. Did your installer think through the control strategy properly, or just assume that the more knobs there are to turn the better?
Do you have a controls diagram (and if not Im wondering how your installer knows that the controls design should work)?
*5 zones if the thermostats are still functional!
I think the mystery is in the first question;
the sensocomfort is insisting that there is "no heat demand" and the heat pump is therefore not responding; there are in effect 4 zones; and 4 thermostats; the sensocomfort has replaced the upstairs thermostat.
We haven't set time schedules, as it's fairly mild at the moment, I'm assuming weather compensation has been set, as that's what I was told by the installer.
Posted by: @gutoffowcI'm assuming weather compensation has been set, as that's what I was told by the installer.
Never assume, it makes an ass of u and me!
Posted by: @gutoffowcthe sensocomfort is insisting that there is "no heat demand" and the heat pump is therefore not responding; there are in effect 4 zones; and 4 thermostats; the sensocomfort has replaced the upstairs thermostat.
OK, thats progress. The sensocomfort is detecting the local temperature as 21C and, because of whatever it has been told (through the configuration that the installer dialed in) has decided that this means that there is no requirement to heat. Potentially not an unreasonable conclusion, most people want to stop heating at 21. Don't forget that it only knows what it knows and can only react as it has been told to react. It doesn't, and cant, know what you intend to happen, only what the installer told it (and the other control elements) to do.
Which brings us back to the central question. How did the installer intend all the separate control elements to work together? This then triggers a secondary question - has he put in the right parameters/connected them up so that they do in fact work the way he intended.
This really is your installers' responsibility to draw a diagram and explain how the control elements are supposed to co-exist. Prima facie you have too many bosses, and thus its predictable that the wrong thing will happen if not carefully configured. Vaillant cant be expected to support this because its not their (control) system, its the installers control system comprising two sensocomforts and several thermostats connected together in unknown ways.
Its difficult to comment further without more detail of both the house and the control system. Its also difficult without that information to judge whether your installer knew what he was doing but didn't explain it adequately, or just hadn't got a scooby which unfortunately is not impossible. He may have installed a control salad not a control system, it happens, can generally be easily sorted out, but is frustrating.
I think you have two options
- put the responsibility firmly in the lap of your installer and rely on him to sort it out
- do some simple experiments, a bit of diagnostics and share some information about your system and your house then, with the help of those here, understand your system and fix it up by reprogramming some key components.
Of course someone here may pop up with THE solution, but its unlikely because nobody else has the same control system as you (they may well have the same components, but how do they know that they are connected/configured in the same way)
If this were my house (and because I generally default to prefer option 2) I would start by taking some control elements out of the equation thus simplifying it. That's (almost certainly) easily done by whacking all the thermostats up to max, so that they are continually calling for heat. Then its the sensocomforts alone that are 'in charge' and you can take a deeper look at how they are interacting, without being bothered by the extraneous thermostats (which I am presuming are not Vaillant devices but please confirm). I would then look a bit at how they have been configured in an effort to reverse engineer what the installer has done. Along the way I would try to understand why I need five zones in the first instance. My 200sqm house runs just fine on a single zone controlled by the one sensocomfort alone, which is delightfully simple. Of course yours may be much bigger or you may have more complex needs which, if you care to share them, we might be able to help with.
Please let us know how you wish to proceed, I (and others I am sure) are willing to help but you need to be committed to that route if its to be successful. It will probably turn out to be very simple once we have understood the control system!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa We've not had a Vaillant engineer in, who may have sorted out one problem but created another; (he wasn't inspiring confidence in knowing how to sort out the problem, and left us with a timed setting for downstairs, so nothing responded till I spotted this and reset it to manual.
He was here on saturday, last night we noticed the pump serving the upstairs rads loop was working, even though there was no demand for heating. The ASHP wasn't producing heat, but why should a pump still be running?. Stating the bleedin' obvious; it's wasting electricity and adding wear and tear to a pump. if we asked for underfloor heating to come on, it was then circulating the same heated water to upstairs! All we could do was turn off the electric to the heating.
So back to the installer to sort out, we agree on that.
Another sleepless night!
Posted by: @gutoffowcHe was here on saturday, last night we noticed the pump serving the upstairs rads loop was working, even though there was no demand for heating. The ASHP wasn't producing heat, but why should a pump still be running?.
Depends on what controls the pump! Thats the whole point, a control system needs to be thought through, not just cobbled together from a set of components more or less randomly connected. Unfortunately, based on what you have told us, there is a fair probability that your installer hasn't got a scooby and will come in, change a few things but wont ultimately sort it (or he will sort this problem but create another)
You may ultimately be best off going back to basics, tracing what connects to what and cutting most of it out. Assuming you have one heat pump and your house area is less than say 250 sqm what you need is one sensotherm, no thermostats, and the system properly balanced to achieve your desired temperatures (presumably a bit cooler in the bedrooms than the living rooms).
As a matter of interest
a) do you have a buffer tank (a tank of water connected to both flow and return between the heat pump and the emitters)
b) how many water pumps do you have in addition to the one in the Outdoor unit
If the answer to a) is yes or the answer to b is more than zero, then your installer also almost certainly has some plumbing problems to sort out and I wouldn't let him get away until he has. Have you paid him, if not dont!
The Vaillant heat pump and its controls are excellent pieces of kit. Unfortunately like any boiler/heat pump poorly thought through controls can make the system as a whole behave weirdly and vastly increase the running cost.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,781 Topics
- 65.6 K Posts
- 1,838 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Tesla Powerwall (2) Calibration Cycles
Yes, I agree. I give Tesla my thoughts on the topic eve...
By Old_Scientist , 8 minutes ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 18 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 3 hours ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
The source legislation is here and is definitive The ...
By JamesPa , 5 hours ago
-
RE: Getting closer to a finished Haier system
Very nice! Congratulations. Big MLC looks neat whe...
By bobflux , 8 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 23 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 1 day ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 1 day ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
One thing a spreadsheet based heat loss calculator can ...
By cathodeRay , 1 day ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 2 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 2 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 3 days ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 3 days ago
-
RE: Estimating true heat loss from twelve months of consumption data
I did, indeed, go with the 12 KW Vaillant unit.  ...
By ian33a , 3 days ago