Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Next steps on my ASHP journey: Radiators and Pipework
Posted by: @rob-of-yorkDoes this set up mean that I should reject having a volumiser or a buffer in the heat pump system design, since the water volumes already in the radiators make them unnecessary, or is there some other valid purpose for having these present?
You should (amost) always reject having a buffer, by which I mean any kind of tank between the heat pump and emitters that is connected both to feed and return.
A volumiser (by which I mean a tank in either the feed (preferable) or the return (OK) and plumbed in such a position that it is not engaged when DHW is being heated), will do no harm, so if an installer wants to fit one and there is space, I wouldn't make a great song and dance about it. It might just make defrost a bit quicker and/or smooth cooling during defrost, but possibly not a lot.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,766 Topics
- 65.1 K Posts
- 710 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Siting of the external sensor on a heatpump
Because not everyone needs it and to be effective it wo...
By JamesPa , 7 minutes ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
You should (amost) always reject having a buffer, by wh...
By JamesPa , 1 hour ago
-
RE: Navigating the World of Refrigerants In Heat Pumps: A Guide for Homeowners
Indeed we are invvestigating AC at present and are havi...
By Toodles , 5 hours ago
-
RE: Is it the house or the equipment?
@majordennisbloodnok I do sympathise. On the original...
By springswood , 7 hours ago
-
No, but the heat pump must be capable of delivering a S...
By JamesPa , 11 hours ago
-
Sorry to hear about the problems, its going to be somet...
By JamesPa , 12 hours ago
-
RE: Daikin ESPAltherma and Home Assistant installation
It's laziness lol The PV system is very chatty, meter...
By bobflux , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 1 day ago
-
RE: Vaillant Arotherm Plus 7KW need a service on it
booked it with Vaillant. will use them until i can find...
By AdamK , 1 day ago
-
RE: Adventures in heat loss calculations
I have seen it stated that the declared calorific value...
By JamesPa , 1 day ago
-
RE: Two heating zones to one zone
@transparent Many thanks. The garage is fairly well ...
By Profzarkov , 2 days ago
-
RE: Vaillant Aurotherm - Heater Wire Position
Ah, good point. I need to check if this was installed i...
By Batpred , 2 days ago
-
@batpred thanks for getting a copy. Appreciate the supp...
By Mars , 3 days ago
-
RE: Tell us about your Solar (PV) setup
We have a 6.56kW solar PV system (16x 410W panels) inst...
By Rob of York , 3 days ago