Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@mike-camelot Your house is an area which has been extensively flooded overnight.
Can you give us any news on both the way your SIP house has been affected, and the situation in the surrounding villages?
Here's a snapshot of NGED's power-cut map for 11:30 today (27th Jan) showing East Devon where Mike lives.
For the benefit of readers in other parts of the UK, the main A30 has been closed due to flooding east of Exeter.
That's true in so many ways: roads, railways, internet connectivity, electricity supplies, housing, ecological imbalance and food production.
There's probably a lot of 'knowledge' on this Forum which could be tapped into, with a view to developing a more resilient society and infrastructure.
The 'solutions' are not going to magically appear from Westminster.
Save energy... recycle electrons!
@transparent No problems today. We had a power cut Sunday night Monday. I don't what time the power went off.It came back at 01.32. I think that it was about 1 hour duration but I can't be certain. I have lived here for 2 ½ years. In that time there have been 3 other cuts. One lasted for 18 hours when a sub station had a problem.
Thanks Mike. Glad to know that you and the house are both intact.
I have access to many of the NGED in-house data and network maps, within a 'partnership agreement'.
That means I can 'see' the connections in your area, and statistics on the physical cables.
Whilst I don't know which is your house, I can already see that you are connected to a pole-mounted local substation, which will be one of:
- Awliscombe 31/1248
- Losses Farm 31/4426
The substation reference number is on the pole at 2m above ground level.
The '31' refers to the Bulk Supply Point (transformers) from which the 33kV cabling originates that you are connected to.
I have a particular interest in increasing network resilience.
That means I keep a lookout for areas which suffer power-cuts more than once for the same reason.
Save energy... recycle electrons!
@transparent, not wanting to derail this thread, I really feel that there are way too many power cuts in the UK. This is a relatively small country and homeowners are paying a stupid amount of money for grid maintenance, upkeep, etc. We're OK where we are, but family in East Sussex/Kent have power outages lasting upwards of 6 hours on a fortnightly basis. It's nuts.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
We used to one or two powercuts a year but I believe they may have put us on a different type of circuit, so it became a lot better.
Not long ago, when going on a hike in Herts we heard about some case where roadworks changed water drainage and some local substation was being flooded on a regular basis. What amazed me is this seemed to be going on for over a year!
I remember thinking about it, all talk and no action..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @editorI really feel that there are way too many power cuts in the UK.
True... but I'll be the one derailing this topic if I respond here.
Firstly I know how to reduce the number of power cuts, in which we can make a difference.
Secondly, this is another instance of customers in SE England being treated differently by their DNO to those of us living elsewhere.
That DNO is UK Power Networks, which appears to be operating outside the norms which other DNOs implement.
The DNO 'UKPN' is more than 75% owned by UK Power Networks Holdings Ltd. which has 10 of its 14 listed Directors based in China.
UK Power Networks Holdings Ltd. is between 25% to 50% owned by Cki Number 1 Limited.
Cki Number 1 Limited is more than 75% owned by Cki Number 2 Limited
Cki Number 2 Limited is more than 75% owned by Cki Number 3 Ltd.
Cki Number 3 Ltd is owned by Ck Infrastructure Holdings Limited, which is based in Bermuda.
All companies in that chain substantially share the same directors.
In effect it's an international financial company which holds an Ofgem Licence to act as DNO for three regions in England.
Whatever gets discussed at Board level is unlikely to have much to do with power outages in East Sussex or Kent!
Further discussion needs to be in a new topic...
... so that @mike-camelot can revert to being worried solely about his hostile installer!
Save energy... recycle electrons!
Update
I just thought that I would post an update. I have still not been able to get any information from my installer so I have contacted the manufacturer in Sweden and asked them to try and take some action.
I contacted OFGEM and found that no application has been made for the BUS Grant. No paperwork has been submitted to the local building control.
As recommended I bought several of the “fridge” digital thermometers and have been taking readings at various points on the system. They have been really useful. I have made several adjustments and the thermometers can very quickly indicate a result.
When I ordered the UFH there was a miscommunication as to what would be the heat source. To cover all possibilities they assumed that it would be a “Boiler System”. As a result they included a mixer valve for each manifold(2). My plumber assumed that it should be fitted and I didn’t know any different. I have now discovered that even with the mixer vale in the fully closed position it still allows for some mixing. This has resulted in the supply temperature drop from pre-mixer valve to post mixer valve of 5C. Wunda have sent replacement valves. My plumber will remove the mixers. At the same time he remove some of the 90 degree bends to improve the flow.
I now believe that my installer over sized my heat pump so it is still cycling at about 1 to 1½ hours. This means that the UFH pumps are running 24/7 and for much of the time are circulating increasingly cooler water while the heat pump is off. I am looking at installing a single pump in the heat pump to UFH supply line. The problem I have is that I need a way of sensing when the heat pump switches on so that it will switch on the “supply pump”. This will result in the pump running only while the heat pump is on. Anyone got any ideas?
I have also discussed replumbing the volumizer.
I have been in contact with NIBE customer care and told them about the problems with my installer. I am waiting for their response. It may be necessary for me to contract an MCS installer to come and commission my installation and generate all the necessary paperwork. Probably an expensive exercise but I may be able to get the Grant.
I used Heat Punk to calculate the “heat loss” for my house. (something else that my installer didn’t do) Thank you for suggesting the program. If you can use standard parameters it is very straightforward. Any “custom” inputs require a little more thought. Their Customer Care, both telephone and email are great.
Since I started to write this update I have had an email from NIBE UK. They said that the installer (they use his first name, James) will call me next week. They also said that all future communications on this matter must only be conducted with the installer. In other words they “wash their hands of the matter”. Since in the last 5 months he didn’t commission or complete any of the required paperwork, including the BUS Grant application, I do not have any expectations of a resolution.
Thanks again to the Forum. You have been a huge help.
Posted by: @mike-camelotI now believe that my installer over sized my heat pump so it is still cycling at about 1 to 1½ hours. This means that the UFH pumps are running 24/7 and for much of the time are circulating increasingly cooler water while the heat pump is off. I am looking at installing a single pump in the heat pump to UFH supply line. The problem I have is that I need a way of sensing when the heat pump switches on so that it will switch on the “supply pump”. This will result in the pump running only while the heat pump is on. Anyone got any ideas?
er, if you do this how will the heat pump ever know to switch on? The obvious thing is to tie it to the heat pump's water pump so it switches on whenever the heat pumps pump switches on. Then if, for example, it runs a sniffing cycle it will sniff from the UFH which is what you need. basically you need to be careful to think this mod through.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @mike-camelotI now believe that my installer over sized my heat pump so it is still cycling at about 1 to 1½ hours
That's not bad.
We've had visitors to this forum with cycling 20x per hour!
If 'James' can't or won't resolve the issues, then you could take this issue to CAB with the prospect of them ruling that he should refund some of your money for 'services' that weren't carried out. Those include
- commissioning the system to use as a little energy (input) as possible as per Building Regs Part-L
- producing full system drawings and operating instructions
- application for BUS
- registering the installation with MCS
Save energy... recycle electrons!
As already covered in this thread, I have an F2040-12 and an SMO 20. It is supplying a Wunda Fast response UFH. I run "open Loop" with all of the zones except the bedroom open. I have an open plan single story house which is very airtight, an MVHR, and very insulated. The temperature throughout the house only varies from 21C to 23C. I have installed thermostats on the recirculation pumps for the UFH so they only run when the heat pump supply exceeds 27C and switch off when the heat pump switches off and the temperature falls below 26.5C. This setup seems to be working reasonably well, but I am thinking of adding a BT 50 internal temperature sensor in the lounge area. Because of the construction of the house, the temperature varies very little unless there is a significant change in the outside temperature. However the heat pump is still cycling between 1.5 to 2 hours (except when the OAT is above 15C approx) with a run time of approx 40 minutes. Is there anyone on the forum has the BT50 fitted, and if so what is your experience?
Posted by: @mike-camelotHowever the heat pump is still cycling between 1.5 to 2 hours (except when the OAT is above 15C approx) with a run time of approx 40 minutes.
As @transparent has observed above, this is not bad, and is nothing to worry about. When the heat loss is below the heat pump's minimum output, and it is on, it has to cycle, otherwise the IAT will continue to rise above the desired IAT. It is normal behaviour.
Above 15 (or 15.5)°C OAT, the need for heating is greatly diminished, or non-existent, and the heat pump can be turned off (set the main room stat very low say 12°C), and a heat pump that is off won't cycle!
Midea 14kW (for now...) ASHP heating both building and DHW
I don't have a room (central) thermostat. That was actually my question. My system has been working quite well while the OAT has been cool. Now we are seeing higher temperatures I was considering fitting a central thermostat (NIBE BT 50) so that I could set it to a temperature that would more efficiently reflect the demands of the house. I was asking for feedback from anyone who may have this unit fitted?
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 1,030 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
Hi @ian33a you could do your own heat loss calculation ...
By Judith , 5 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@djh ah, I have never seen this before, interesting ide...
By ASHP-BOBBA , 5 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 6 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa — this version may be marginally better: &nb...
By cathodeRay , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 8 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 13 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 16 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 17 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 20 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 20 hours ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
That would be abnormal but I cant see from your charts ...
By JamesPa , 21 hours ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago