Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Surface mount or bury primaries for heat pump installation?
Hi,
I'm in the early stages of planning my heat pump installation and whilst I know where the pump itself will be sited, I need to work out how to get the water into the garage. The path will see the pipes run up the side access and turn into the garage before getting connected to my heating. The route includes data and power cable.
I have two options.
1. I surface mount the primaries and run them along my neighbour's wall. I then have to either go under the paving or run the pipes up an over. I'll need a bracket of some sort between my neighbour's wall and the heat pump itself as I can't fix them to their failing timber fence.
2. I bury an instulated pipe that holds everything. The problem is that my side access is pretty busy underground with storm, waster and water main pipes. I'm told I should bury the pipe at 600mm, but I don't believe that's possible. At least not all the way. I have photos of this before it was backfilled.
What I want to know is why we can surface mount pipes in insulation, but we're required to put insulated pipes quite deep in the ground.
Has anyone got their primaries buried at a depth less than 600?
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Heat pump installation has started!
I think I would be wary of attaching my services to a neighbours property without some form of legal agreement to allow this and the required access to them in perpetuity. It also leaves the pipework at the risk of the neighbouring owner, or any future owner, making perfectly legal changes to their property which impacts on your pipe run.
@abernyte That is an excellent point. I hadn't considered that at all! I think I'll be burying a pipe 🙂
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Heat pump installation has started!
Posted by: @tomasmcguinnessHas anyone got their primaries buried at a depth less than 600?
Yes, ours are buried. 20m run from the heat pump to the utility room. Buried at roughly 50-60cm. I dug the trench myself with pickaxe and spade, because I knew there pipes (waste and gutter run off) underground.
The insulated heat loss pipe is quite pricey from what I can remember.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@editor My side access already contains services, so it's not easy. I think I'm going to have to shallow bury the pipe as it will need to go over some of the existing services. There is clay pipe down there and I don't want to disturb that.
Is there any solid guidance on buying pipes? I'm less concerned about the water and more about the electrical cable.
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Heat pump installation has started!
Broadly, the electrical cable will need to be either earthed armoured or in a duct to prevent mechanical damage. Both need to be marked with the required tape.
@tomasmcguinness, because ours runs under our driveway, and I was keen to avoid going too shallow in case it ever got damaged from heavy vehicle deliveries or future resurfacing.
As for guidance on insulation depth, the general 600mm recommendation is more about frost protection and physical damage prevention than some hard and fast requirement (as far as I know anyway). If you’re using decent insulated pipework and you’re not in an area prone to severe frost, going a bit shallower (like 300–400mm) in tight spots should be fine.
In your case, I’d agree that shallow burial with good-quality pre-insulated pipework is a practical way forward. You could always add some additional foam lagging and a protective duct over the section that runs shallower, just to give it a bit of extra mechanical protection.
On the electrical side, the key thing is to use appropriately rated armoured cable, preferably in its own duct separate from the primary pipe, especially if it’s running alongside heat-carrying pipework. It’s also worth checking the manufacturer’s guidance… some kits include pre-bundled solutions, while others require cables to be run independently.
Out of interest, which heat pump are you going with? And who’s installing it? Always helpful context for others following your project too.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@abernyte I was thinking of an SWA *in* the ducting. I'm looking at a combined water and electrical pipe (uponor or isoflow for example).
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Heat pump installation has started!
Current thinking is a Kronoterm Adapt. Doing the ground works myself (trench digging, base casting, that sort of thing). Then the professionals will finish the job.
Presently, I'm just exploring my options to get the water from the heat pump into the garage.
I'm constrained by the existing services, so I'm not sure how deep I'll actually manage.
Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Heat pump installation has started!
@tomasmcguinness bold choice on the Kronoterm. Nice! Will be very curious to see how it performs. Have heard very good things about them.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@tomasmcguinness HI, The rules is a best practise, the heating pipes do not come under the same rules as services such as gas and mains drinking water.
Mostly its for frost protection but when the pipes are only just below the surface it is advisable to well insulate above 100mm thickness to slow losses and mechanically protect if possible.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @tomasmcguinnessI was thinking of an SWA *in* the ducting.
What you run the cable through will affect its current rating (and hence voltage drop).
SWA is intended for direct burial in the ground... the wetter the better.
You want any heat-loss from the cable to be conducted away into the surrounding soil.
Placing a cable inside an air-filled duct has the opposite effect.
The air acts as an insulating jacket. You've just made yourself an underground oven in a long tube. 😥
When you select the required cable size, you would usually enter the figures into an online calculator.
Here's one on the website for TLC-Direct.
That will tell you the cross-sectional area of the copper conductors you will require.
Secondly, if you have any services at shallow depth, where they might get hit by a garden fork for example,
place some basic paving slabs above them.
Although buried electrical cables must also have warning tape above them,
there's nothing like having the fork hit a 40mm piece of concrete slab to warn you there's something down there!
Save energy... recycle electrons!
-
How Accurate Is My DIY Heat Loss Calculation?
23 hours ago
-
Issue with Samsung Cascade System
1 month ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
2 months ago
-
Design Of Cascade System Replacing Undersized ASHP
2 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
5 months ago
Currently viewing this topic 3 guests.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,297 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
It's an enticing idea, but the problem is knowing the o...
By cathodeRay , 7 minutes ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 3 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 8 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 23 hours ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 23 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago