Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Design Of Cascade System Replacing Undersized ASHP
Hi folks
I have posted before about my ASHP problems which eventually led to my installer admitting that the original ASHP was undersized. We are now getting close to the time where they will replace the system and I am waiting for them to confirm the system design.
To summarise - original heat loss calculation was 8kW and 12kW Midea was installed. System could not get house to desired temps when OAT was below -1C. I ran my own calculations, collected data and had a new, independent heat loss calculation done. My calcs came out at 13kW and the independent one came out at 14kW. Lots of discussion and help on here and we don't need to revisit that element of the discussion.
The options for replacement were a 16kW single unit or cascade of 2 x 10kW Clivet Evo Edge units, which is what my installer is going with. After 2 years of wrangling with them, I'm not going to fight this.
House has UFH downstairs and rads upstairs. Upstairs not used much and no problem running single flow temp as all upstairs rooms are bedrooms and they can hit desired IAT with same flow temp as the UFH.
They are doing the refit at their cost and the units will be new with new guarantees. My current ASHP is nearly 5 years old so there is upside in this.
My questions are therefore related to how the system should be configured. In other forum posts, there are suggestions that with a cascade, a buffer can actually be a good idea although my previous conclusion from extensive reading here on single ASHP systems, was that a system volumiser would be a better idea. What do I need to know about cascade systems to make sure the installation is correct?
Specifically
Do I need a buffer or would system volumiser be better?
How should the cascade be set up?
Should 1 unit generally run until more power is needed when unit 2 kicks in or should they both run equally?
Should 1 unit do heating while the other does HW and additional power for heating when needed?
Will I have any control over what each unit does after installation?
What else do I need to consider?
All help welcome
Many thanks
I don't know the full details of your house or installation so this is just thinking out aloud, but going through this current heat-wave, I'd be thinking about whether there's a solution which could provide the additional top-up heating and some cooling.
For example, would it be feasible to have an air-to-air / aircon type unit in a room, or a multi-split to provide additional heating to a few rooms with the summer cooling thrown in?
Or, if it has to be an additional heat-pump, can it be installed in a way that allows some fan-coils to be added to provide additional heating/cooling.
How does the installer propose to control it? Do Clivet offer a controller capable of modulating 2 outdoor units? Will both outdoors have their own pumps, how will these be controlled? Would one unit be master, start on demand, ramp to 80% and if PI&D is increasing then ramp down and bring on second unit and modulate both until demand is hit? In theory easily done, in practice especially with pumps involved it could take some tuning, I've no great experience with domestic controlling but have worked on numerous commercial installs with multiple outdoors. Hat tip to Graham Hendra, this isn't a cascade:) https://www.linkedin.com/pulse/is2-heat-pumps-cascade-graham-hendra?trk=public_post_feed-article-content
Thanks for your reply. Answers to the questions you raised is exactly the kind of info I am looking for. I have asked the installer for a full PI&D and will revert when I have this
Pash
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
2 hours ago
-
Surface mount or bury primaries for heat pump installation?
1 week ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
3 months ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
4 months ago
-
Rodents! A word of warning for heat pump owners
6 months ago
- 26 Forums
- 2,717 Topics
- 63.6 K Posts
- 2,382 Online
- 7,119 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Hi everyone, I’m looking for real-world advice and co...
By asoksevil , 2 hours ago
-
I knew that Reactive Power support was required by the ...
By Transparent , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Those are very good questions and indeed ones I was ask...
By JamesPa , 7 hours ago
-
For cooling a whole building, or even a big room with l...
By EtchedPixels , 8 hours ago
-
RE: Comms and power cabling to outside unit
@old_scientist 100%, the cover is for warrantied unit...
By Papahuhu , 8 hours ago
-
I don't remember the manufacturer name, but I saw simil...
By bobflux , 10 hours ago
-
RE: Weather compensated secondary circuits with Biomass
UFH is ideal to get max efficiency with a heat pump, bu...
By bobflux , 10 hours ago
-
RE: Vaillant Arotherm Pro vs new Plus
when our system was installed in September 2 years ago ...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
I had a Heat Geek lead install by Green Heat Norfolk. T...
By Orlando , 1 day ago
-
RE: Mitsubishi Ecodan FTC6 settings
While @F1p's dongles are great, the FTC can do this its...
By RobS , 2 days ago
-
RE: Samsung heat pump - data cable issue
If it's a data cable, current will be minuscule, voltag...
By bobflux , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
I got hit with an RHI audit in 2022. It was far from c...
By Abernyte , 2 days ago
-
Hi,is there any Haier super aqua gt users on here,that ...
By Glenn Crawford , 2 days ago
-
RE: Electricity price predictions
@papahuhu Groucho Marx had something to say about no...
By Toodles , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa haha very true, although the engineer yesterda...
By swwils , 3 days ago