Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Spent £1,000 Trying to Fix My Oversized LG ASHP, Now Considering Vaillant or Ideal. Advice Needed.
Hi all,
I recently purchased a house in a small development (8 houses) which has an oversized LG 9kw split block fitted, we have had issues all winter and it seems that all of the houses on the development have had similar issues with 2 of them already having had new systems fitted. After spending almost £1000 so far trying to get it sorted we have decided to cut our loses and get a new system installed and I am after some help with figuring out some of the specifics.
The house;
Built 2017
126sqm
Heat loss 3-3.5kW
UFH downstairs which is currently set up on 3 zones (kitchen, living room, hall), and 7 radiators upstairs - currently configured so if any of the UFH zones call for heat the radiators will also get heat.
When we have had the system working we have had it in WC using the thermostats as a limiter but have had difficulty balancing the upstairs radiators to be comfortable.
I have requested the new system to be on 2 zones, downstairs and upstairs (I know that zoning isn't the most efficient but I am willing to sacrifice some efficiency for comfort, ideally I can balance the system and have all zones open on WC mode but having the option to zone upstairs separately would be nice).So the new system we have been recommended is either a Vaillant Arotherm plus 5kw or Ideal logic air 5kw. 210l pre-plumbed cylinder - the installer has recommended a buffer as one of the issues we currently get is a low flow rate, this has occurred less since removing the TRV's but still happens and I assume this is partly down to the unit being oversized. Having read around a lot including this forum I would rather not have a buffer but I am willing to sacrifice some efficiency in order to have a working system - I am going to ask the installer to fit it as a 2-port buffer/volumizer. I should also add that there will be an 18m run of piping that will run 600mm below the garden from the ASHP to the house due to the layout of our house.
My question's;
- From my understanding the benefit of a buffer is that for much larger buildings you have a separate circulation pump after the buffer - With the run from the ASHP to the house being fairly long, will I need a secondary circulation pump?
- If I do need a secondary circulation pump does this mean I have to have a buffer or can you have a secondary pump with a volumizer?
- Any recommendations between the Ideal logic vs Vaillant? I know there is a new version of the Vaillant which I would like to wait for but there is a substantial cost difference with the ideal system being almost £2000 cheaper!
Thanks in advance
Posted by: @bones
I am in a similar situation as you. Have an oversized heat pump 7KW in a 2KW at -2C property with UFH. I have selected a Vaillant 3.5KW as my replacement. Why, right size, appears to me to be the most purchased machine, lots of service engineer options.
I also have a buffer tank on my current system. I plan to convert this to a volumiser on my new system.
I also looked at the new black version due to be released in the UK next month. I managed to get hold of a spec from Germany. I could not see much of a difference in terms of the spec to the current UK heat pump.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
You would need to engage someone that is able to calculate and design your system and select the correct pump capacity to open loop a system with an 18m run from the garden (this is possible to do as we have installed them as far as 20m and they work fine) balancing rads against UFH is tricky but possible, Fire Power sell an FRV lock shields for the rads this would help as you could set the rads based on a set flow rate and calculate the required flow - capacity making sure they are the correct Kw (link below)
Use of a buffer:- Ok so this is where you get a bit of kick back, buffers are often a no no, if you can avoid a buffer its ideal but in your case what a buffer will do for you if you are willing to loose a bit of efficiency is allow to move the heat twice, once from the ASHP internal pump to the buffer and then again from the buffer to the home, the other thing having a buffer and 2nd pump will allow is for you to select another pump at the correct capacity to handle the UFH and rads rather than rely on the internal pump of the ASHP. (so options are bigger pump open loop, 2 smaller pumps with hydraulic break buffer) having a buffer can also often disguise an over sized ASHP somewhat but as you are changing the heat pump so there is no need.
There is one more option, you can choose an ASHP such as a Mitsi Ecodan that has no pump, calculate a light commercial pump (if needed) to do the duty and revert back to no buffer, of see if the pump in the Vaillant will do the duty which it just might.
Best advice, see if you can engage a company that is use to doing these kinds of upgrades and changes that minimises your costs and keeps as much of the existing equipment you have but can re-design or reverse design your whole system. We have changed 6 of these in the last year alone and it takes quite an investigation to be sure, example, if the original company installed the wrong size ASHP and could not balance the system, what else did they get wrong, the hardest thing you will find is someone willing to take on another's bad installation and offer guarantees.
https://www.firepowerheating.co.uk/frv
Editor's Note: use code RHHFRV10 at checkout to get 10% off.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba in reading your post, I did wonder where your stated 3 to 3.5kW heat loss came from? Was this a calculated figure or derived from operation of your existing unit? I ask because I have a 3.5kW Vaillant and it will give over 4KW at -5. My 110sq m house was subject to a deep refurb and that included an mvhr system. Most of the time over this winter the pump has been consuming about 500W and giving a heat and DHW cop of 3.9 so 2 to 3 kW of heat. Maybe your 3.5 kW demand is calculated but does it include an allowance for the ventilation losses? If the figure is derived from the demand on your existing system maybe the smaller 3.5 Vaillant would be suitable?
A related issue is of course the sizing of the emitters. You only say UF and radiator numbers. Do you know what they will emit at what DT. My system was set on WC of 0.6 most of the winter. I have both radiators and UF all on one zone. In February I discovered the UF had a stuck valve. Once I cleared that I could drop the WC curve to 0.4 - which is probably marginally low.
i am definitely not a heating engineer but reflecting on how our system seems to operate in practice.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @davidb@ashp-bobba in reading your post, I did wonder where your stated 3 to 3.5kW heat loss came from? Was this a calculated figure or derived from operation of your existing unit? I ask because I have a 3.5kW Vaillant and it will give over 4KW at -5. My 110sq m house was subject to a deep refurb and that included an mvhr system. Most of the time over this winter the pump has been consuming about 500W and giving a heat and DHW cop of 3.9 so 2 to 3 kW of heat. Maybe your 3.5 kW demand is calculated but does it include an allowance for the ventilation losses? If the figure is derived from the demand on your existing system maybe the smaller 3.5 Vaillant would be suitable?
A related issue is of course the sizing of the emitters. You only say UF and radiator numbers. Do you know what they will emit at what DT. My system was set on WC of 0.6 most of the winter. I have both radiators and UF all on one zone. In February I discovered the UF had a stuck valve. Once I cleared that I could drop the WC curve to 0.4 - which is probably marginally low.
i am definitely not a heating engineer but reflecting on how our system seems to operate in practice.
I have calculated the heat loss using heatpunk as 3kw, our neighbour who has the same house had a few calculations which came in around 3-3.5kw. We do have MHVR in our house but this also doesn't work so hasn't been calculated into heat loss, something I will have to look into. From my understanding the 3.5kw and 5kw vaillant are the same, just the smaller unit is software locked to a max output but the minimum modulation is the same so I don't think it is worth going for the smaller unit other than upfront savings which is minimal.
For the emitters I have no idea what the UFH emits, we have had flows of 35-40 this winter and it has kept the house warm. For the rads I have calculated them as sufficient using heatpunk for a flow temp of 40.
The FRV's you mention look good, I may have to invest in some of these to help balance the system.
So if I go for set the buffer up in 2 port I would need to use either the ASHP internal pump or a single larger pump rather than 2 pumps?
We have had a few companies come out and look at the system who just won't go near it, the company we are using have suggested improvements to our system but have admitted that they cannot guarantee any fixes as they are not 100% sure what the issue is, if they rip it out and start again they will give us a guarantee that the system will work correctly.
Posted by: @trebor12345Posted by: @bonesI am in a similar situation as you. Have an oversized heat pump 7KW in a 2KW at -2C property with UFH. I have selected a Vaillant 3.5KW as my replacement. Why, right size, appears to me to be the most purchased machine, lots of service engineer options.
I also have a buffer tank on my current system. I plan to convert this to a volumiser on my new system.
I also looked at the new black version due to be released in the UK next month. I managed to get hold of a spec from Germany. I could not see much of a difference in terms of the spec to the current UK heat pump.
I am thinking the same, I would prefer Vaillant as there is a lot more info out there regarding the arotherm, there controller and app seem much better than the Ideal as well. I have looked at the spec sheet for the new arotherm and I agree it doesn't look like any major improvements, slightly better COP figures on the spec sheet - The installer has said it should be the same price as the current unit so I figure I may as well wait for the new unit as I won't need the heating over summer anyway.
Posted by: @bonesThe FRV's you mention look good, I may have to invest in some of these to help balance the system.
So if I go for set the buffer up in 2 port I would need to use either the ASHP internal pump or a single larger pump rather than 2 pumps?
We have had a few companies come out and look at the system who just won't go near it, the company we are using have suggested improvements to our system but have admitted that they cannot guarantee any fixes as they are not 100% sure what the issue is, if they rip it out and start again they will give us a guarantee that the system will work correctly.
Hi, If you mean 2 port (only using 2 ports of the buffer) this would be a volumiser and yes only 1 pump, if you use it as a buffer (ASHP F+R on one side and Home F+R on the other) you would need a second pump for the house side.
I hear this often about companies hesitation, if not nearly all the time, if you are in Kent I would be happy to help, unfortunately we only cover Kent due to the volume of work here is overwhelming. It takes a very confident company in their abilities to offer improvements and take the risk.
We installed a new system for a client that had been turned down by multiple bigger companies Inc one of the best companies in the country* for design as they said the existing underground pipework from their oil boiler looked 20mm and cannot carry the 8kW required to heat the home and as the home was 100 years old and the fact that the customer did not want to dig up 20m of garden or change their cast iron rads it would not work, it was also unknown what level of insulation was under the ground. We attended, to investigate, calculated the Rads, calculated the runs and explained to the customer about the risks but said we can prove if it will work or not for £100 before installation, the client engaged.
We 1st inspected with an IR camera on the main pipe work under the ground just to make sure there was no extreme leakage, then we disconnected both ends and measure the maximum flow rate we could achieve through the pipe in the ground, it turns out we could get 11.1kW through the pipe and it was in fact 25mm with 100mm insulation, we then heated the water in the test loop to 50 Deg C and measured the flow to see if there was any drop in tempersature, the drop was 0.7 Deg C so not bad. We then calculated like in your case what index PA was needed which led to a light commercial pump at 8M head.
As a result the customer engaged us to install, the cast rads were around 5-9% under sized in 2 rooms either side of the hall way, the hall way had an old stelrad so we upgraded this to 140% for that area that then supported the 2 short areas as it was between them.
This home has now been running from November 2025-today and the SCOP is 3.9 on an 8Kw Ecodan several meters down the garden, the customer reported that even on the -6 days in January the system held a perfect 21 Deg C, the system was 40% open loop and TRV's every where else.
* No Names and not the best at everything
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba on the FRVs, I’m finding them a bit annoying and not sure if you’ve experienced this. On rads where we have to reduce flow to under 0.5 l/min/m², I find that the valve is not very accurate, and, more often than not, it just shuts the valve off completely and the rads are stone cold. I’ve now had to put all those valves up to 1 l/min/m² just to make sure they remain open.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editor@ashp-bobba on the FRVs, I’m finding them a bit annoying and not sure if you’ve experienced this. On rads where we have to reduce flow to under 0.5 l/min/m², I find that the valve is not very accurate, and, more often than not, it just shuts the valve off completely and the rads are stone cold. I’ve now had to put all those valves up to 1 l/min/m² just to make sure they remain open.
I have only used a couple so far and that was at 2-l/pm as i needed around 750 watts out of the rad, that said i did DT clamp and IR test as well, it just helped me set them much quicker.
Are your rads with these on very small heat requirement? 1ltr is only 350W, also they do a low flow insert that goes with the valve but I don't know at what point (what is low flow) you would use this, I assume from below 1-ltr/pm
Perhaps it may be better if @bones waits for IMI neo flow and change all of the UFH and TRVS to match thats another way that might be good for a mixed rads and UFH balance, as soon as these come out I am going to offer them to a client at cost just to get some data back.
I am myself looking for all market solutions for room control and mix rad / UFH solutions that offer a 90% close or programmable part close so I can replicate our preferred style of commissioning which is having 30% open loop system while being able to control most rooms as I find this is what most clients would like. If I was to programme all of or the main rooms to close 90% I no longer need to have an open loop as all of the 90% closed rads will equate to a prat open loop, I am sure this is one future design that will be common practise. I think this would reduce nearly all offthe miss control flow failures and some good news for many on here that have that issue.
Self balancing is coming too, lets have some of that please.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
When we have had the system working we have had it in WC using the thermostats as a limiter but have had difficulty balancing the upstairs radiators to be comfortable.
I presume this means that upstairs was too hot? If so and given the FT art which you were operating, no need to worry too much about radiator sizing and you may wish to try turning FT down even further and operating the UFH open loop. Take note of the min FT setting, this is frequently set to 35 or even 37, which is far too high in many cases bus avoids call outs on account of the radiators not 'feeling hot'.
Posted by: @bonesPosted by: @trebor12345Posted by: @bonesI am in a similar situation as you. Have an oversized heat pump 7KW in a 2KW at -2C property with UFH. I have selected a Vaillant 3.5KW as my replacement. Why, right size, appears to me to be the most purchased machine, lots of service engineer options.
I also have a buffer tank on my current system. I plan to convert this to a volumiser on my new system.
I also looked at the new black version due to be released in the UK next month. I managed to get hold of a spec from Germany. I could not see much of a difference in terms of the spec to the current UK heat pump.
I am thinking the same, I would prefer Vaillant as there is a lot more info out there regarding the arotherm, there controller and app seem much better than the Ideal as well. I have looked at the spec sheet for the new arotherm and I agree it doesn't look like any major improvements, slightly better COP figures on the spec sheet - The installer has said it should be the same price as the current unit so I figure I may as well wait for the new unit as I won't need the heating over summer anyway.
I have the Vaillant 7kW and confirm that I am very pleased with it. Both App and control interface provide everything you need. For the Arotherm Plyus the 3.5kW is just the 5kW downrated in firmware, which cuts the max output without affecting the min. I dont know if thats also true of the Arotherm pro. If so might be worth getting the 5kW because DHW reheat will be quicker
@bones based on what you have said I cant think of a reason why you would need a buffer or a secondary circulation pump. No harm in fitting a 2 port volumiser though and, given your low loss, it would likely be a good addition. It needs to be either in the flow (arguably marginally preferable) or the return, but not between the two. It should be plumbed so it is NOT engaged during a DHW run.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 462 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
So the red bars are 'DHW' and the yellow bars 'heating'...
By JamesPa , 43 minutes ago
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
Every manufacture has a guide and service list...
By ASHP-BOBBA , 2 hours ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 4 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 4 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 4 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 16 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 17 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 18 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 20 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 23 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 3 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 3 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 5 days ago