Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Grant Aeona 3 R32 cycling with weather compensation.

2 Posts
2 Users
0 Reactions
35 Views
(@ga3_usr)
Active Member Member
Joined: 6 months ago
Posts: 6
Topic starter   [#2992]

Our Heat pump has a low deltaT of 1 to 2degC. 

 

The way it appears to operate from being idle (no compressor, circulating pump runs 24hrs, room stat set at 24deg, WC enabled.)

 

The flow temperature drops to a certain value below the target flow temperature. The compressor starts at full pelt and flow temperature starts to rise.

When the flow temperature reaches the target the compressors throttles right back and micro adjusts itself so the flow temperature matches the target temperature during this time the flow temp may be a bit above or below the target.

 

Then one of the following seems to happen;

 

  1. The slug of initial hot water from the start of the cycle returns, and if this is hotter than the measured flow temperature the compressor stops until the flow and return are cool enough for the cycle to restart.

 

  1. The heat pump manages the compressor so flow temperature  matches target temperature, it doesn't get caught in the above loop and just runs steady for hours.

 

  1. The same as point 2, but at some point the outside temperature increases by 1degC, the target flow temp decreases by 1degC then the heat pump throttles back to lower the flow temperature and either the loop in point 1 begins, or it manages to continue as per point 2.

 

Given the resolution and precision of the data from the grant smart controller it's difficult to know if the above is the logic or just coincidence and I'm just seeing something which isn't there.

 

My thinking is if I could get the system to loose a little more heat through the radiators and have a larger delta T at the heat pump the system would ride out the small changes in outside temperature much better.

 

Any thoughts?

 

The images show what I would consider normal operation, and the cycling I'm trying to describe.

Compressor Hz,

Temperatures, Green:DHW, Blue:target flow temp, Yellow: flow temperature (at HP), Red: Return temperature (at HP) 

 

Screenshot 20260509 193606~2
Screenshot 20260509 142640~2

 

 

sd


   
Quote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4858
 

Posted by: @ga3_usr

My thinking is if I could get the system to loose a little more heat through the radiators and have a larger delta T at the heat pump the system would ride out the small changes in outside temperature much better.

 

Any thoughts?

If the system loses more through the radiators the house will get warmer.  Is that what you want?  If you do want this then you will need to increase the flow temperature.

All heat pumps and boilers cycle if the house demand is less than the minimum output of which the device is capable.  This is bound to happen at moderate OATs and may happen even at low OAT if the heat pump/boiler is oversized.

What is it that you think is abnormal in your case?


This post was modified 7 hours ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote