Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Grant Aeona 3 R32 cycling with weather compensation.
Our Heat pump has a low deltaT of 1 to 2degC.
The way it appears to operate from being idle (no compressor, circulating pump runs 24hrs, room stat set at 24deg, WC enabled.)
The flow temperature drops to a certain value below the target flow temperature. The compressor starts at full pelt and flow temperature starts to rise.
When the flow temperature reaches the target the compressors throttles right back and micro adjusts itself so the flow temperature matches the target temperature during this time the flow temp may be a bit above or below the target.
Then one of the following seems to happen;
- The slug of initial hot water from the start of the cycle returns, and if this is hotter than the measured flow temperature the compressor stops until the flow and return are cool enough for the cycle to restart.
- The heat pump manages the compressor so flow temperature matches target temperature, it doesn't get caught in the above loop and just runs steady for hours.
- The same as point 2, but at some point the outside temperature increases by 1degC, the target flow temp decreases by 1degC then the heat pump throttles back to lower the flow temperature and either the loop in point 1 begins, or it manages to continue as per point 2.
Given the resolution and precision of the data from the grant smart controller it's difficult to know if the above is the logic or just coincidence and I'm just seeing something which isn't there.
My thinking is if I could get the system to loose a little more heat through the radiators and have a larger delta T at the heat pump the system would ride out the small changes in outside temperature much better.
Any thoughts?
The images show what I would consider normal operation, and the cycling I'm trying to describe.
Compressor Hz,
Temperatures, Green:DHW, Blue:target flow temp, Yellow: flow temperature (at HP), Red: Return temperature (at HP)
Posted by: @ga3_usrMy thinking is if I could get the system to loose a little more heat through the radiators and have a larger delta T at the heat pump the system would ride out the small changes in outside temperature much better.
Any thoughts?
If the system loses more through the radiators the house will get warmer. Is that what you want? If you do want this then you will need to increase the flow temperature.
All heat pumps and boilers cycle if the house demand is less than the minimum output of which the device is capable. This is bound to happen at moderate OATs and may happen even at low OAT if the heat pump/boiler is oversized.
What is it that you think is abnormal in your case?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
What I would think of as abnormal would be the heat pump cycling on every small blip in another otherwise fairly consistent OAT, as opposed to cycling because the house is up to a temperature that it can't take any more heat from the radiators.
Of course without access to a detailed log I can only ever guess at what triggers what in the logic.
What I might do as an experiment is, if I catch a time when it looks like small OAT changes are causing cycling is turn off the WC, fix the flow temperature to that temperature and see how it behaves. It might be Autumn for that though.
Posted by: @ga3_usrWhat I would think of as abnormal would be the heat pump cycling on every small blip in another otherwise fairly consistent OAT, as opposed to cycling because the house is up to a temperature that it can't take any more heat from the radiators.
That would be abnormal but I cant see from your charts that its doing that. The first chart looks like roughly hourly cycles, the second a single cycle and the third cycles every 2-3 hours. The ups and downs of the compressor modulation seem to indicate a bit of hunting in the compressor modulation control loop, but I wouldn't worry about that personally, unless someone tells me otherwise. Im concentrating mostly on the yellow (to understand what the FT control loop is doing) and ignoring the short term noise on this signal which could be due to almost anything including the effects you have mentioned (or it could literally be noise)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The hot water heating looks normal. The heat transfer into the tank is so fast that the heat pump takes a long time to reach the target flow temperature. When it does, or when the timer expires, it switches back to space heating.
The cycling is happening over a long period of time. The heat pump is stopping for an hour and not just for a few minutes. It is behaving as though the room thermostat has reached its target temperature and is no longer asking for heat, but that seems unlikely with a 24C target room temperature.
It would be interesting to plot the target and actual room temperature and outdoor temperature as well, if that is possible.
What are your weather compensation settings?
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 3,338 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How much of your renewable and home setup would still work if the internet went down?
Agree but remember to retain your isp router as they wi...
By JamesPa , 15 minutes ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@susannasaunders Reluctantly I think i agree with @r...
By JamesPa , 21 minutes ago
-
RE: Why don't people choose heat pumps?
It's swings and roundabouts - during off-peak periods t...
By Temperature_Gradient , 2 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 9 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 9 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 9 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 13 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 16 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 4 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago