Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your post before. I hope this feedback is still helpful.
Leaving pump blockade off enables the heat pump to know the temperature of the water in the system, so it can decide to turn on the compressor again. Your system seemed happy to run continuously overnight. During the day when the outside temperature got to 10C it turned off a few times. This is probably because it can't reduce the flow temperature any lower than about 27C.
According to the Smart Controller Installer and Operating Instructions table in Section 7.14.1
''DECREASING FIXED WATER TEMPERATURE' applies only to non-weather compensated circuits. Therefore it does not apply to us.
Section 7.14.2 for Weather Compensated Circuits is confusing. I think it is meant to apply a setback to the flow temperature during Night Mode.
It says:
During a scheduled night/unoccupied time period, the water flow temperature will be reduced by the configured value
‘DECREASE WATER TEMPERATURE’ set during system setup or in the circuit settings.
However, confusingly then it goes on to say something that seems to contradict Room Temperature Correction below.
...With a Thermostat...
If ‘THERMOSTATIC PUMP BLOCKADE’ is not enabled, once the target air temperature is achieved the smart controller will use decrease the flow temperature target by the ‘DECREASE WATER TEMPERATURE’ value, which is set correctly will maintain the target air temperature. Refer to 7.3.1.3 for recommended setback values based on heat emitters for the circuit.
Room Temperature Correction
Target temperature with correction = Target air temperature of the thermostat assigned to the circuit minus Current temperature of the thermostat assigned to the circuit x Room temperature correction.
By default, the Room temperature correction value is 4.0, and the value range is 0 - 10.
It is necessary to find appropriate value of the Room temperature correction. The higher the coefficient, the greater the correction of target circuit temperature. If the setting is “0”, the target circuit temperature is not corrected. Note: setting a value of the room temperature coefficient too high may cause cyclical fluctuations of the room temperature.
Bottom line, I think you should use Decrease Water Temperature for Night Time set back and Room Temperature Correction to add some room influence to the flow temperature. But I could be wrong!
Graham
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
I am following this thread with great interest and thank you all for the hints and education!
I agree with GrahamF about the Smart Controller manual. Some of it has confused the hell out of me especially around temperature correction and even hysteresis. With our old GSHP the hysteresis behaved as I expected: if there is a 47c target then raise the temp above it and when the temp falls some degrees below it then kick in the heating. However, our DHW does not hit the target of 47 at all but cycles somewhat below it (with 6c hysteresis):
I have manually had to reduce the target the last few days for the central heating to get a look in.
I will reduce the DHW schedule to a few hours in the morning and afternoon but I cannot understand the mechanism which switches off the compressor when the DHW hits around 45.5c.
Our controller certainly has no input for temperature sensor on Circuit 1. Econet24 just shows it the same as Heat Pump Actual Temp. Currently the three circuits are set to fixed temp but I am going to try weather compensation as that certainly worked well on the GSHP. (It was an IVT with some REGO controller. Much, much simpler than the Grant Smart Controller.)
Thanks again,
Gerald.
- 27 Forums
- 2,783 Topics
- 65.6 K Posts
- 1,826 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How should the Boiler Upgrade Scheme be reformed?
Yes, their gas typically costs twice ours and electrici...
By Batpred , 21 minutes ago
-
Over the years, due to the non barrier PEX underfloor h...
By bobflux , 1 hour ago
-
RE: Getting closer to a finished Haier system
All the 45° elbows required for getting the primaries i...
By Singlespeed , 2 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
@papahuhu Likewise, the main ‘extra’ relates to TOU tar...
By Toodles , 8 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
That sounds like a better approach (being able to see a...
By cathodeRay , 1 day ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
Thanks for the reference @jamespa I can't see any te...
By Transparent , 1 day ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 2 days ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 2 days ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 4 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 4 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 4 days ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 4 days ago