Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your post before. I hope this feedback is still helpful.
Leaving pump blockade off enables the heat pump to know the temperature of the water in the system, so it can decide to turn on the compressor again. Your system seemed happy to run continuously overnight. During the day when the outside temperature got to 10C it turned off a few times. This is probably because it can't reduce the flow temperature any lower than about 27C.
According to the Smart Controller Installer and Operating Instructions table in Section 7.14.1
''DECREASING FIXED WATER TEMPERATURE' applies only to non-weather compensated circuits. Therefore it does not apply to us.
Section 7.14.2 for Weather Compensated Circuits is confusing. I think it is meant to apply a setback to the flow temperature during Night Mode.
It says:
During a scheduled night/unoccupied time period, the water flow temperature will be reduced by the configured value
‘DECREASE WATER TEMPERATURE’ set during system setup or in the circuit settings.
However, confusingly then it goes on to say something that seems to contradict Room Temperature Correction below.
...With a Thermostat...
If ‘THERMOSTATIC PUMP BLOCKADE’ is not enabled, once the target air temperature is achieved the smart controller will use decrease the flow temperature target by the ‘DECREASE WATER TEMPERATURE’ value, which is set correctly will maintain the target air temperature. Refer to 7.3.1.3 for recommended setback values based on heat emitters for the circuit.
Room Temperature Correction
Target temperature with correction = Target air temperature of the thermostat assigned to the circuit minus Current temperature of the thermostat assigned to the circuit x Room temperature correction.
By default, the Room temperature correction value is 4.0, and the value range is 0 - 10.
It is necessary to find appropriate value of the Room temperature correction. The higher the coefficient, the greater the correction of target circuit temperature. If the setting is “0”, the target circuit temperature is not corrected. Note: setting a value of the room temperature coefficient too high may cause cyclical fluctuations of the room temperature.
Bottom line, I think you should use Decrease Water Temperature for Night Time set back and Room Temperature Correction to add some room influence to the flow temperature. But I could be wrong!
Graham
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
I am following this thread with great interest and thank you all for the hints and education!
I agree with GrahamF about the Smart Controller manual. Some of it has confused the hell out of me especially around temperature correction and even hysteresis. With our old GSHP the hysteresis behaved as I expected: if there is a 47c target then raise the temp above it and when the temp falls some degrees below it then kick in the heating. However, our DHW does not hit the target of 47 at all but cycles somewhat below it (with 6c hysteresis):
I have manually had to reduce the target the last few days for the central heating to get a look in.
I will reduce the DHW schedule to a few hours in the morning and afternoon but I cannot understand the mechanism which switches off the compressor when the DHW hits around 45.5c.
Our controller certainly has no input for temperature sensor on Circuit 1. Econet24 just shows it the same as Heat Pump Actual Temp. Currently the three circuits are set to fixed temp but I am going to try weather compensation as that certainly worked well on the GSHP. (It was an IVT with some REGO controller. Much, much simpler than the Grant Smart Controller.)
Thanks again,
Gerald.
- 26 Forums
- 2,677 Topics
- 62.6 K Posts
- 208 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Floor standing brackets for K3 rads
My neighbour is a plumber and said I would need to fit ...
By Singlespeed , 26 minutes ago
-
After an intense recode, I’m pleased to announce that w...
By Mars , 34 minutes ago
-
RE: Heat pump installation quotations
@batpred, @sttpd1917 I agree with what @batpred says...
By JamesPa , 34 minutes ago
-
RE: Harvest Thermal - ASHP with a smart thermal battery
As its using ToU tarrifs then its totally believable so...
By JamesPa , 2 hours ago
-
Why do you want to maintain a specific deltaT? The out...
By JamesPa , 2 hours ago
-
Hopefully this will answer your question. To...
By ASHP-BOBBA , 3 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I would be interested to find out if others do this and...
By ASHP-BOBBA , 3 hours ago
-
Don't you dare. You just carry on as you are; as @batpr...
By Majordennisbloodnok , 5 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@ragtime27 some rooms in our house only have one place ...
By Judith , 5 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 9 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 9 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 9 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 13 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago