Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Spent £1,000 Trying to Fix My Oversized LG ASHP, Now Considering Vaillant or Ideal. Advice Needed.
@ashp-bobba thanks, we are too far away from Kent unfortunately. Self balancing would be ideal, as much a trv's aren't ideal for heat pumps they are useful in bedrooms where guests/other family members may want a different temperature and you need to change it quickly.
@jamespa - The upstairs would sometimes be too hot, sometimes too cold - with the heat pump beings so inconsistent it's been difficult to have it working long enough to properly have a go at making adjustments and seeing how they affect the house. In an ideal world we would like upstairs 1 or 2 degrees cooler than downstairs majority of the time. Thanks for the tip about min FT settings, I'll make sure to adjust them when we get a new system.
Glad to hear you are happy with the vaillant - I am going to go back to the installer and see about having the buffer set up as a Volumiser, this will hopefully save on costs as we won't need a secondary pump
Posted by: @bonesSelf balancing would be ideal, as much a trv's aren't ideal for heat pumps they are useful in bedrooms where guests/other family members may want a different temperature and you need to change it quickly.
In addition to Adia, there's an exciting new product that will hopefully drop in the UK later this summer.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @bones@jamespa - The upstairs would sometimes be too hot, sometimes too cold - with the heat pump beings so inconsistent it's been difficult to have it working long enough to properly have a go at making adjustments and seeing how they affect the house. In an ideal world we would like upstairs 1 or 2 degrees cooler than downstairs majority of the time. Thanks for the tip about min FT settings, I'll make sure to adjust them when we get a new system.
I recommend very strongly that you insist on no buffer (volumiser OK) unless your installer has a very coherent reason why, and even if they do (have a coherent reason why) I strongly recommend writing it down carefully and testing the argument here. If the argument isnt valid and installer wont budge, find another installer.
Once you get the new kit I suggest you try operating open loop 24x7, if you can get it balanced right it will be very likely both the most comfortable and the cheapest way to operate. It will totally avoid the 'inconsistency' which arises because you have unlinked control systems fighting each other which is unlikely ever to be satisfactory. Many people here operate in this manner and there is good reason!
I have rads upstairs and down, and have balanced so that upstairs is a couple of degrees cooler than downstairs. All but one rad is open loop, the one that has a TRV is in a guest bedroom, as a courtesy you guests who may want a different sleeping temp than we do. The level of comfort is well beyond anything I ever achieved with a boiler and TRVs all over the place.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
K@jamespa thanks for the advice. The plan is to get it all set up open loop 24/7 - will be nice to have the thermostats upstairs to fall back on though.
Our current Thermostats and ufh is manager for a heatmiser uh8 - the installer has said that this will remain for the UFH and the vaillant /ideal thermostat will control upstairs. I assume this is OK as the heatmiser downstairs is just opening/closing zones based on the thermostats but I will be using these as a limiter and allowing the heat pump to manage the system?
Posted by: @bonesK@jamespa thanks for the advice. The plan is to get it all set up open loop 24/7 - will be nice to have the thermostats upstairs to fall back on though.
Our current Thermostats and ufh is manager for a heatmiser uh8 - the installer has said that this will remain for the UFH and the vaillant /ideal thermostat will control upstairs. I assume this is OK as the heatmiser downstairs is just opening/closing zones based on the thermostats but I will be using these as a limiter and allowing the heat pump to manage the system?
Its not really OK, neither is it true that the Vaillant (or ideal) controller is 'just controlling the upstairs' unless the Vaillant is set to pure WC mode without room influence (which may be the installers intention, but quite possibly isn't). However if there is any room influence at all on the Vaillant controller then it will shut down when upstairs is warm enough, and then there is nothing the downstairs can do if the downstairs isnt warm enough. Thus the downstairs is in reality controlled by the Vaillant also and you have effectively two control systems fighting each other. Two bosses are never a good thing! The problem is worse still if a buffer is fitted, because then there is the control of the secondary pump to consider. Hopefully you have resolved this and there will be no secondary pump.
One approach to all of this (once the buffer/secondary pump have been eliminated) is just to ignore the installer and do your own thing with the controls. You can disable them all by setting them significantly higher than target. You can then balance radiators to UFH so that they both run 24x7 and are both controlled by the Vaillant. If you then need to apply a limiting function you can, but on top of a system that is properly balanced to start with. However this may fail if you have a secondary pump depending on how that is controlled, which is another reason to ensure that is resolved.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - Thanks, I hadn't considered the room influence.
Seems like this is becoming more expensive and complicated by the day!
My UFH manifold and UH8 is in a different room to the cylinder, looking into it I think if I want to get the full vaillant setup and controls I would need to replace the heatmiser with something like the VR71 - this would require me to wire an ebus between the manifold room and cylinder room?
Posted by: @bonesMy UFH manifold and UH8 is in a different room to the cylinder, looking into it I think if I want to get the full vaillant setup and controls I would need to replace the heatmiser with something like the VR71 - this would require me to wire an ebus between the manifold room and cylinder room?
You dont need to do any of this and by far the best thing is to make it more simple not more complicated, particularly in a new build house of the size yours is. Assuming you haven't got a buffer, just disable any room influence due to the heatmiser and any other external controllers and TRVs by turning all the thermostats/TRVs up to full. Then turn down the weather compensation (heat) curve on the Vaillant until the house settles at the right temperature overall, and balance the system so the rooms settle at the right relative temperature.
Having set it up this way you can either leave it as is or decide to reintroduce room influence in rooms where its eg to control excess solar gain. If you do you the latter can experiment with where to where to put the wireless controller (Sensocomfort) that comes with the Vaillant, otherwise it doesn't matter where you put it because its not taking any notice of the room temperature.
Please forget everything you thought you know about controlling central heating and get over the idea that you need lots of controls, you dont and they arent particularly effective in anything other than a mansion, because houses have memory, rooms share heat and too many bosses simply doesnt work.
Its almost certainly the case that your most comfortable and cheapest way to run the house is to set it up to run it without room influence, on pure weather compensation and balance the rads/UFH to get the desired relative temperatures between rooms. My house is bigger than yours and thats how I run it, many here do the same. Its never been more comfortable
The thermostat(s) and/or Vaillant controller can be used as a limiting device, set a couple of degrees above the desired temperature, to switch off in the case of excess solar gain. I did this at the very end only of the first season with a heat pump, when solar gain becomes significant in comparison to house loss. This season it hasn't been necessary, I have operated on pure weather compensation throughout.
It might be a good idea to read this introductory article which explains some of what I am saying above with a bit more context.
As an aside and without knowing how you are operating your LG, I would hazard a guess its because you are are using too many controls that you currently have a problem, not because its oversized. You probably will find a smaller Vaillant easier to get on with and it probably will be more efficient, but Im far from convinced that this is the root cause of the problem you describe. If you wish to explore that thought further rather than spending several £K on a new heat pump I am happy to do so, but only if you are serious because I dont want to waste time if you have already made a decision! Bear in mind that its interests of the controls industry to sell you more controls, and in the interests of the plumbing industry to sell you new systems. Just saying!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - Ideally we would leave it in WC mode 24/7 but it would be nice to have the room influence for solar gain etc, I'm not chasing 100% efficiency just a balance between efficiency and comfort. If I can get it to work with the heatmiser that would be ideal - in this scenario let's say the sensocomfort is the thermostat in our main bedroom which controls the upstairs zone, if we have WC on and the thermostat set a few degrees above our desired temp, if we get solar gain and the thermostat turns off the upstairs zone, will the ufh downstairs still get flow from the heat pump?
Our current system runs either at a set flow of 35 or WC with the thermostats set to 23, WC mode 24/7 no setbacks and we adjust the WC to aim for room temps of 20. The issue is when have errors on the LG controller 90% of plumbers / engineers insist the strainer is blocked (it isn't), the few that have come and looked at the system just seem in shock at how poor it's been plumbed in and don't want to get involved with it. I appreciate the offer but we have already made the decision to cut our loses and go for a new install.
Posted by: @bonesOur current system runs either at a set flow of 35 or WC with the thermostats set to 23, WC mode 24/7 no setbacks and we adjust the WC to aim for room temps of 20. The issue is when have errors on the LG controller 90% of plumbers / engineers insist the strainer is blocked (it isn't), the few that have come and looked at the system just seem in shock at how poor it's been plumbed in and don't want to get involved with it. I appreciate the offer but we have already made the decision to cut our loses and go for a new install.
Fair enough, once a decision is made its best to stick with it. Just be certain that your new installer doesn't make different mistakes
If the errors are flow rate errors and the strainer isnt blocked it may be a control problem. With lots of zones (or active TRVs) you can get zones shutting down reducing throughput which causes flow rate errors. The solution is to operate in a way that means the zones dont shut down, or if they do its only a minority of the total. Of course because its oversized its expecting a much higher flow rate which is also a problem, so getting a lower capacity unit should deal with this.
Posted by: @bones@jamespa - Ideally we would leave it in WC mode 24/7 but it would be nice to have the room influence for solar gain etc, I'm not chasing 100% efficiency just a balance between efficiency and comfort. If I can get it to work with the heatmiser that would be ideal - in this scenario let's say the sensocomfort is the thermostat in our main bedroom which controls the upstairs zone, if we have WC on and the thermostat set a few degrees above our desired temp, if we get solar gain and the thermostat turns off the upstairs zone, will the ufh downstairs still get flow from the heat pump?
No, thats the point I have been trying to make. If you turn the heat pump off you turn it off, just like if you turn a boiler off, you turn it off.
Assuming you have TRVs upstairs then I would deal with excess solar gain using these so that you don't conflict with the downstairs, but dont overdo the number of rads you have active TRVs on otherwise you will be getting flow rate errors still - presumably only a minority of rooms suffer/benefit from excess solar gain? That said, unless you work at night, does it matter if a bedroom overheats slightly during the day?
Posted by: @bonesI'm not chasing 100% efficiency just a balance between efficiency and comfort
No need to worry much about 'balance' as, in an unusual quirk of physics, maximum comfort and maximum efficiency can pretty much be achieved simultaneously in most cases by operating as suggested. Forget needing lots of controls to achieve comfort, you don't. All you need is to balance heat loss from the house with energy supplied by the heating system, which results in a stable temperature. Properly adjusted pure weather compensation comes very, very close indeed to achieving that, as well as being most efficient. The only 'losers' in this game are the manufacturers of third party controls which are in most cases unnecessary and often counterproductive.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaI recommend very strongly that you insist on no buffer (volumiser OK) unless your installer has a very coherent reason why, and even if they do (have a coherent reason why) I strongly recommend writing it down carefully and testing the argument here. If the argument isnt valid and installer wont budge, find another installer.
Hi James, we are now evaluating installing a heatpump. We had a look at a neighbours install that have a Vaillant which they was installed above their disused garage, with the tanks in the garage. We do not that type of spare space. Also as we would be replacing a combi, we need to find space for the hot water tank. But as I counted 4 tanks in total in our neighbours', it seems we will need more space than for the hot water tank. And if we need so much, it could be a showstopper..
We will not have UFH, but will probably have some rads replaced. Pipework should not need changes. Also since we insulated the house to modern standards, I am not expecting a very powerful ASHP.
We had a few initial estimates a few months back, but with little detail. I am wondering the minimum number of tanks that we need to consider and does MCS mandate a minimum hot water tank size for a a 4 bed..
I believe we always need hot water (200L?), volumiser (50L?, hopefully horizontal is available) and expansion vessel (12L)? Hopefully we do we need to find space for more...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredBut as I counted 4 tanks in total in our neighbours', it seems we will need more space than for the hot water tank. And if we need so much, it could be a showstopper..
You need one hot water tank. Its typically about 500mm diameter and perhaps 1.3m high, although it depends on what capacity you want (see comment below). It can go either upstairs or downstairs, in a garage, in a loft, or even in a purpose built insulated shed or (as in older homes) in a purpose built cupboard which is then used for 'airing' clothes/towels etc. You ned to be able to rout a pipe to the outside world with a continuous downward slop, so if its near an outisde wall it helps (there are workarounds though).
There are two expansion vessels about 30cm dia and 30cm high, normally one red and one white. These can go more or anywhere connected to (a) the central heating (the red one) and (b) the DHW (normally white). I have one in the loft and one in a garage. They are often tucked away at high level, or at low level in some available space.
You may need a volumiser, it depends on your house loss in relation to the size of heat pump you can conveniently have. 50L is usually plenty, it needs to go before the pipework divides to feed the rads/UFH. They can be wall mounted and in more or less any orientation.
Anything else is superfluous, probably a buffer tank, which you do not want under any circumstances.
Posted by: @batpredWe had a few initial estimates a few months back, but with little detail. I am wondering the minimum number of tanks that we need to consider and does MCS mandate a minimum hot water tank size for a a 4 bed..
Yes, but there is leeway if the mandated size is not practical so its not absolute. I think its about 200l for 4 bed (thats what my water tank is and I have 4 bedrooms). Obviously you need sufficient capacity for your DHW needs but there are games you can play with this also if (say) 200l wont fit.
Hope that helps you find space. In a 4 bedroom house, even if the bedrooms are quite small, it should be possible if you think a bit out of the box..
If you say a bit more about house size and construction we its possible to ballpark the capacity of heat pump you need, better still if you have records of gas usage. This is anyway a good sanity check on the sometimes excessive figures that some surveys produce!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @batpredBut as I counted 4 tanks in total in our neighbours', it seems we will need more space than for the hot water tank. And if we need so much, it could be a showstopper..
You need one hot water tank. Its typically about 500mm diameter and perhaps 1.3m high, although it depends on what capacity you want (see comment below). It can go either upstairs or downstairs, in a garage, in a loft, or even in a purpose built insulated shed or (as in older homes) in a purpose built cupboard which is then used for 'airing' clothes/towels etc. You ned to be able to rout a pipe to the outside world with a continuous downward slop, so if its near an outisde wall it helps (there are workarounds though).
There are two expansion vessels about 30cm dia and 30cm high, normally one red and one white. These can go more or anywhere connected to (a) the central heating (the red one) and (b) the DHW (normally white). I have one in the loft and one in a garage. They are often tucked away at high level, or at low level in some available space.
You may need a volumiser, it depends on your house loss in relation to the size of heat pump you can conveniently have. 50L is usually plenty, it needs to go before the pipework divides to feed the rads/UFH. They can be wall mounted and in more or less any orientation.
Anything else is superfluous, probably a buffer tank, which you do not want under any circumstances.
Thanks, it is amazing how this info is hard to get even talking to a manufacturer! Daikin in my case, which also has an indoor unit. I think we could cope with it, but it will take some convincing..
Octopus is now giving night electricity for 3.5p per kwh. If this stays, the maths will be very appealing. With another battery..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,610 Topics
- 60.8 K Posts
- 1,112 Online
- 6,966 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Anyone concerned about GivEnergy?
An incredibly enlightening piece on the subject by @maj...
By Mars , 28 minutes ago
-
Home automation and the cloud; is there a better way?
You’ve just had a brand new system installed (heat pump...
By Majordennisbloodnok , 33 minutes ago
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
We've started to document everything, and part 2 of the...
By Mars , 48 minutes ago
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
So the red bars are 'DHW' and the yellow bars 'heating'...
By JamesPa , 2 hours ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 5 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 5 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 5 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 5 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 16 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 17 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 19 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 19 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 21 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 1 day ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 3 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago