Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
DIY or Don’t Touch? Solarman Smart Meter Install
Posted by: @jamespaPosted by: @batpredProbably since, as you stated, a leak to earth would impact the reading on the neutral.
If you have a leak to earth you have a problem which would trip an RCD if the circuit has one. It's a fault condition.
Yes, but many circuits do not have RCD/RCBO. As they are not mandatory in all circuits (and as usual the regulations do not mandate them retrospectively...)
Anyway, agree that the clamp should also work around the neutral.
Another thing I realised is that, when having multiple clamps along the same wire, it is a good idea to have a few cm in between them.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
Posted by: @batpredYes, but many circuits do not have RCD/RCBO. As they are not mandatory in all circuits (and as usual the regulations do not mandate them retrospectively...)
True. But a minor earth leakage will make no significant difference to the measurement and a major one is probably a near short so major enough to blow a fuse/MCB. There may be a mechanism for an earth leakage that is material but not sufficient to blow a fuse, but it's difficult to think what it is (other than a miswire of course!)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Makes sense to me. The simpler it is to install it, the more people will do like Mars and not be held back by an electrician visit…
On a related point, one of my ashp quotes listed the need for an “mcs electrical meter” (assume it is just a ct clamp). I told them i do not need it, but they stated it is mandatory. I remember some folk posting here and wanting to know how much their heatpump was consuming? Unless they had an mcs meter they would not trust, is it the case of some old rule that no longer applies?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
Posted by: @batpredOn a related point, one of my ashp quotes listed the need for an “mcs electrical meter” (assume it is just a ct clamp). I told them i do not need it, but they stated it is mandatory. I remember some folk posting here and wanting to know how much their heatpump was consuming? Unless they had an mcs meter they would not trust, is it the case of some old rule that no longer applies?
Bow Locks. Ask them to tell you the reference number of the regulation specifies this, the rules are all in the public domain. Or look elsewhere! If you are claiming RHI then it may be mandatory, but not otherwise.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @batpredOn a related point, one of my ashp quotes listed the need for an “mcs electrical meter” (assume it is just a ct clamp). I told them i do not need it, but they stated it is mandatory. I remember some folk posting here and wanting to know how much their heatpump was consuming? Unless they had an mcs meter they would not trust, is it the case of some old rule that no longer applies?
Bow Locks. Ask them to tell you the reference number of the regulation specifies this, the rules are all in the public domain. Or look elsewhere! If you are claiming RHI then it may be mandatory, but not otherwise.
Very much agree. Even with RHI (and we were one of the last to get in under this scheme), it's only necessary in some cases. We, for instance, do not need any kind of metering to get our repayments.
Bear in mind, of course, that you (either out of your own pocket or via the subsidy scheme you are unlocking) have to pay for every piece of kit that's installed. If it doesn't provide you with a benefit of some kind, why should you pay for it and why should you allow it in your home? If the installer is wanting to put something in that's only for their own benefit, they should be the ones paying for it and even then only installing it with your permission.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokVery much agree. Even with RHI (and we were one of the last to get in under this scheme), it's only necessary in some cases. We, for instance, do not need any kind of metering to get our repayments.
Bear in mind, of course, that you (either out of your own pocket or via the subsidy scheme you are unlocking) have to pay for every piece of kit that's installed. If it doesn't provide you with a benefit of some kind, why should you pay for it and why should you allow it in your home? If the installer is wanting to put something in that's only for their own benefit, they should be the ones paying for it and even then only installing it with your permission.
Yes, and these guys would probably be my preferred installers, a nice family business. They are however sticking to old habits.
The other thing is he included the buffer tank even when I explicitly excluded it. Now he removed it but claim that the use of a third party tank instead of Vaillant adds to their costs! Having a single line item for 16k was suspicious but they still managed to undermine themselves further.
A shame, as I will be posting locally when more local folk really start to switch. I will only be able to comment on the old tech and pricing habits.. Like paying for something I do not need and still paying for it when I am not having it.
At this stage, not even worth the £250 survey.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
Posted by: @jamespaPosted by: @batpredYes, but many circuits do not have RCD/RCBO. As they are not mandatory in all circuits (and as usual the regulations do not mandate them retrospectively...)
True. But a minor earth leakage will make no significant difference to the measurement and a major one is probably a near short so major enough to blow a fuse/MCB. There may be a mechanism for an earth leakage that is material but not sufficient to blow a fuse, but it's difficult to think what it is (other than a miswire of course!)
An earth fault on a TT derived supply (typically but not exclusively overhead lines) will often not trip an MCB/Fuse (or at least not disconnect the fault within the required time) due to the high EFLI.
In these cases you'd typically use an upfront RCCB for fault protection with the fuses / MCBs providing the overload and short circuit protection. Or more recently every circuit on an RCBO with tail clamps on the main switch.
Posted by: @ga3_usrPosted by: @jamespaPosted by: @batpredYes, but many circuits do not have RCD/RCBO. As they are not mandatory in all circuits (and as usual the regulations do not mandate them retrospectively...)
True. But a minor earth leakage will make no significant difference to the measurement and a major one is probably a near short so major enough to blow a fuse/MCB. There may be a mechanism for an earth leakage that is material but not sufficient to blow a fuse, but it's difficult to think what it is (other than a miswire of course!)
An earth fault on a TT derived supply (typically but not exclusively overhead lines) will often not trip an MCB/Fuse (or at least not disconnect the fault within the required time) due to the high EFLI.
In these cases you'd typically use an upfront RCCB for fault protection with the fuses / MCBs providing the overload and short circuit protection. Or more recently every circuit on an RCBO with tail clamps on the main switch.
That was my understanding also.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,811 Topics
- 66.6 K Posts
- 3,448 Online
- 7,223 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Why don't people choose heat pumps?
I love that concept of net0! My concern with the nesta ...
By Batpred , 4 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
I think you're right! 🤨
By Transparent , 5 hours ago
-
RE: Renewables & Heat Pumps in the News
ECO4 muddies the water somewhat, and then some. I thi...
By cathodeRay , 6 hours ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
@jamespa Yes indeed, I meant ‘add-on’ in the sense that...
By Toodles , 6 hours ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
If there is a drain nearby that's exactly what I would ...
By JamesPa , 6 hours ago
-
RE: DIY powerflushing tutorial
This is what bacterial growth in UFH loops looks like. ...
By Pirate Rich , 13 hours ago
-
I think that CCGT plant in Lingen is more likely to suc...
By Transparent , 2 days ago
-
RE: Heat Geek installations: share your experiences
@l8again fwiw my experience (Valiant but not with heat ...
By JamesPa , 2 days ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
@etchedpixels thank you for the advice paid cash all...
By Chilli304 , 3 days ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@susannasaunders An interesting conversation to have ...
By Rob of York , 3 days ago
-
RE: Electricity price predictions
@rob-of-york sounds like a term that Heidegger would...
By Papahuhu , 4 days ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 4 days ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 4 days ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 4 days ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 6 days ago
Members Online
No online members at the moment