Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Is the Grant controller a thermostat?
The Aerona 290 is from a different (Chinese) OEM, compared with the Japanese (Chofu) R32 Aerona3. I don't have experience with the R290, or the smart controller.
From what I can tell, on the R32 the smart controller is effectively a prettier settings and status UI than the Chofu LCD programmer. For example, instead of going to the Chofu programmer and holding buttons to go into installer mode to change setting 3141 to 0, you would go into a touchscreen menu and choose 'Legionella day' to be 'Monday'. But what happens during the legionella cycle is still controlled by the HP, not by the smart controller - the smart controller just talks to the HP via Modbus to change the settings. That means if the smart controller goes away for some reason, the HP carries on as normal - you just can't change the settings.
I don't know if the R290 works any differently. From a brief look at the smart controller installation instructions it seems that it forms the traditional wiring centre, with only Modbus going back to the ASHP. That implies that the decisions whether to turn on/off valves, pumps, etc are being made in the smart controller, or made in the HP and being sent to the smart controller via Modbus and the smart controller drives the relay. That means a failure of the smart controller would cause the heating to fail, but doesn't mean that internet access is required (it looks like it's an addon so I suspect it isn't).
(On the R32, I have reverse engineered some of the Modbus status but not enough to control valves, immersion from Modbus values. I'm not sure if they are being reported that way - but I haven't put a lot of effort into it)
I would question whether you actually need multiple temperatures at different times in different rooms. Heat pump heat is much more even, and it's more efficient to keep everything at a constant temperature than have it swinging about all the time (Heat Geek has a video on how zoning is actually counterproductive). We just manually adjust the temp at night; that's something possible to adjust via Modbus so I expect the smart controller could do that automatically.
Again, for hot water I just leave it on 'comfort' at 44C which means there is hot water all the time, and the HP comes on if the hot water falls below that. For this it needs a temperature sensor in the cylinder - I think Grant include that as part of the Smart Controller setup?
If you are trying to make it run at particular times to suit a variable tariff then that's another thing, but I think it's better just to leave it to get on with it. It makes for a more comfortable house because you're never cold or have cold water.
Thanks for the clarification. Slightly concerning OEM approach, would need to look into the Grant warranty cover carefully..
Posted by: @prunusI would question whether you actually need multiple temperatures at different times in different rooms. Heat pump heat is much more even, and it's more efficient to keep everything at a constant temperature than have it swinging about all the time (Heat Geek has a video on how zoning is actually counterproductive). We just manually adjust the temp at night; that's something possible to adjust via Modbus so I expect the smart controller could do that automatically.
We plan to have a single home temperature driving the pump, but it would be nice to vary that temperature in terms of day and night. Nowhere near perfect and we may not vary it much anyway but will help peace of mind..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
Hi @batpred, the smart controller came as part of the Grant Quick Recovery Smart DHW cylinder as it is mounted on the front.
The smart controller acts as a thermostat, but you can also connect in a wireless thermostat if needed.
Grant do only allow you to have one thermostat assigned to each heating circuit. The controller supports up to 3 separate heating circuits.
You can set a ‘day’ temperature and a ‘night’ temperature on the controller and program a schedule to change between. You can do this for each day of the week individually.
Weather compensation works with the external sensor included with the external unit, or you can connect a separate external temperature sensor to the controller I believe.
DHW schedule is fully programmable in half hour slots for 7 days of the week.
Legionella cycle is supported with the included immersion heater in the DHW tank, with a programmable day and time to run once a week.
The smart controller is completely standalone and doesn’t require Internet access to function. Internet access is only required if you wish to use the econet app to monitor or adjust settings remotely.
The smart controller shows electricity usage for the DHW and space heating separately along with the heat output generated. It lists an instant COP and average COP figure to show efficiency of the ASHP.
Grant 12kW r290 ASHP - Sunsynk 3.6kW Solar Inverter with 3.5kW panels and GSL 10kWh home battery
Posted by: @batpredWe plan to have a single home temperature driving the pump, but it would be nice to vary that temperature in terms of day and night. Nowhere near perfect and we may not vary it much anyway but will help peace of mind..
So the 'nice' may well limit you to a small subset of heat pumps unless you want everything other than the highest to be on/off control on (built in) thermostat.
You will need to read the manuals pretty carefully to determine whether changing the set temperature changes flow temperature or just invokes the inbuilt temperature sensor/thermostat function, ie acts as on/off. I can say for certain that Vaillant does the first, cant be certain/remember others. I suspect Homley, Passiv, Havenwise, Adia as addons do the first also. Not sure how much it matters in practice if setback is small, but it might matter quite a bit if you want to do a set forward because it means that most of the time (when not set forward) you are operating on thermostat.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@batpred I have the Aerona 290 15.5kW. It has run happily through our first winter down to -5C with no problems.
I suggest you read the Grant Aerona Smart Heat Pump System Controller Installation & Operating Instructions. Below, I will refer to section numbers in that manual.
In answer to your points:
- You have to use the Aerona Smart Controller with the Aerona 290. Yes, the associated display does include a thermostat. It is one of the more user friendly displays.
- The system comes with an external temperature sensor. You set the weather compensation curve as described in 7.13.
- Thermostat control (7.14.2): when the room reaches its target temperature, the system behaves differently depending on the setting of Thermostatic Pump Blockade":
- When Blockade is set to "On" and the temperature is reached, it turns the heat pump off.
- When Blockade is set to "Off" and the temperature is reached, it continues running with the water flow temperature by the amount set in "Decrease Water Temperature". See 7.8.1.1.
- You can set day and night temperatures - see 7.3.1.3.
- Domestic hot water:
- You can set the hot water temperature (7.2.3) to just one value.
- You can schedule the DHW in half hour slots (7.5).
- There is also a Boost function to make it run at any time. It will continue running until it reaches the target temperature, or until you turn it off (7.3.2.2). I would prefer a half hour timer on it as well.
- You can schedule the weekly Legionella cycle (7.4).
- You can configure a hot water loop, which I have. It pumps water from the tank around a loop to near the kitchen and back into the tank. Whenever you turn on the hot tap, you have nearly instant hot water for washing up. This is great in theory, but the circulation mixes hot and cold water in the tank, which makes it all tepid. You can mitigate this by scheduling the loop for meal times and setting the duration and frequency of each pumping cycle - e.g. pump for 1 minute, stop to 2 minutes, pump for 1 minute. See 7.5.4.
- There is no Holiday Mode button, at least in my version of the firmware - a shocking omission! You can turn the heat pump off when you go away and restart it remotely using the phone app.
- The Smart Controller is hardwired into the heat pump, the display and the Smart Hub (see 10) which connects to the Internet. It runs fine when the Internet goes down, but of course then you lose remote access.
- The User Settings/Energy Monitor displays the instantaneous electricity consumption, heat output and COP. It also displays the SCOP, which presumably has been measured since installation or maybe since the last power up or firmware upgrade (not sure). I should warn you that the COP is probably overstated, as is common with heat pump manufacturers.
- The phone/tablet app and the ECONET24 web site can display graphs of compressor frequency, flow and return temperature, outdoor temperature, room temperature, hot water temperature, 3-way valve setting... Frustratingly, you cannot produce a graph of electricity consumption, heat output or COP. However, if you are happy to interface it to Home Assistant, then you can produce graphs of all of those.
- I use a Shelly Pro EM-50 to track electricity consumption. It agrees closely with the heat pump's own measurements.
- The manual refers to a choice of "Installation Pack" (4.2). Ask your installer what is in the heat pump pack, which seems to be an outdated Grant term. You don't need flow/return temperature sensors or external pump, because the Aerona 290 includes them.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
That's very helpful.
Clearly the control has various unique features. The ability to have immediate hot water seems premium.
Useful how the Thermostatic Pump Blockade allows fine tuning of the flow temperature.
The thing is the way Grant changed from R32 to R290 highlights a different approach to product management. I wonder if that creates some interesting management of replacement parts...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
The Smart Controller does indeed have a thermostat but ours only covers one floor of three (Grant Aerona 290 15.5kW). We still have zone thermostats for our old system which used to have Uponor timers. These just now act as limiters - as I understand it! I wasn't around when the electrical connections to the UFH circuits were set up but I suspect the pumps and zone valves use the zero-volt terminals in the controller.
(I noticed the comment from GrahamF on the temperature correction and pleased he inserted the parenthesis to emphasise the mathematical priorites. They are not in the manual.)
Early days for us as the ASHP has only been running a couple of weeks. I have it connected to Home Assistant with a standard Econet300 integration but I am attempting to enhance the REST integration to obtain other metrics including the energy usage.
I should mention that we had a GSHP in our previous property in the Brecon Beacons. This had a Raspberry Pi interface. In 16 years the technology has advanced tremendously!
There are a few aspects of this particular system which confuse me:
- How hysteresis works - certainly not like I understood it as our DHW temp never reaches the target;
- Why circuit 1 assumes radiators as emitters;
- Why Econet24 reports Circuit1's actual temp as that of the ASHP - Circuit1 cannot have a temperature sensor;
- Why Circuit2 has gone missing from Econet24(!);
- How the heat pump's target outlet temp (Service params - read only values) is calculated;
- Why are there temp corrections set on DHW, Circuits, "Setpoint temp. correction - heating" in the Service parameters.
If anyone can point this old IT techie at a decent heat pump glossary, I would be very grateful!
I know that the system is configured to give DHW priority, but I think this one is configured such that the target is not reached but the compressor stops. (The hot water cylinder is not a Grant model as we needed a solar coil. It is a UK Cylinders 200l model.)
The house was only built in 2010 so has decent insulation and the like. I shall do some investigating and post my "discoveries" in this forum.
Thank you to all who contribute!
- 27 Forums
- 2,816 Topics
- 66.7 K Posts
- 2,782 Online
- 7,230 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Should I change my cylinder when changing from a gas boiler to a heat pump.
I have 178 L Gledhill unvented cylinder which was fitte...
By David , 5 hours ago
-
RE: Plug and play solar. Thoughts?
Impressions so far from the one I've installed are that...
By EtchedPixels , 6 hours ago
-
-
@batpred The Daikin temperature probe protrudes from th...
By Toodles , 10 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor And as an occasional contributor, may I say wel...
By Toodles , 12 hours ago
-
RE: Should Households Who Can Afford It Pay More for Energy to Help Those Who Can't?
They don't have to try. Our entire system is d...
By EtchedPixels , 12 hours ago
-
RE: Why don't people choose heat pumps?
Fair enough. I guess I was thinking of pipes that run ...
By JamesPa , 12 hours ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
Got excepted for the grant now so thanks for the replie...
By Chilli304 , 16 hours ago
-
Daikin Altherma 3 R F+W, room thermostat control, weath...
By JanHarley , 17 hours ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
Pretty much as I had guessed in my crude scaling from m...
By JamesPa , 20 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Well you have a vibration generator running at some fre...
By bobflux , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@downfield Thats a decent rate, I’m shocked they hadn...
By Papahuhu , 2 days ago
-
RE: Adventures in heat loss calculations
@toodles thanks! So as suspected, around a doubling of ...
By SusannaSaunders , 2 days ago
-
Six books in three years and I think I’ve now covered j...
By Mars , 3 days ago