Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Antifreeze protection
I have anti freeze valves. Due to complications of my install this past week in the cold snap, my anti freeze valves kicked into action and drained my system. The system was filled early afternoon, but they couldn't get the electrics to work so were unable to turn on that day. The temperature outside was below 0C all day and bottomed out at about -5C, so well below the design operation temp of the valves at 3C. The system started draining at about 11pm and was still going the next day. I'm unsure why it took so long, but I suspect a mixture of the valves being slow releasing and no air getting in from anywhere else to release the water.
I would suggest if this is going to happen to anyone else to isolate the exterior pipe run from the interior pipe run so you don't have to refill the whole thing when power returns after a long power cut. I was going to do this, but had assumed that the installers didn't do so for a reason (since we discussed the possibility of this happening) so didn't want to mess with it, but they said the next day that I should have. Do NOT isolate the heat pump from the valves.
As you can see from my timeline, you have a lot of warning that this is going to happen, and then it takes a long time to fully happen. Only if you were away from your house could this fully drain your system in my opinion, otherwise you will catch it, and if you are away from your house for so long in such conditions then you should be glad that the system did empty your interior pipework because that could burst too along with anything else that holds water in your house. Moreover inhibitor is cheap and easy to add through a rad, so if your whole system does dump then it's an easier fix than anti-freeze.
I suspect I'm one of a very small group of people this has ever happened to, but at least we now have proof the valves work.
@oswiu - very interested to hear your account of what actually happens. Am I right in thinking that once the anti freeze valves have decided to do their thing, you have no heating until you refill the system? I assumed this is the case, and your account seems to confirm it is the case, but isn't that the Achilles heel of using such valves, they do protect the system, but in a way that makes it incapable of operating, possibly when you need it the most? And furthermore, how many residents are standing by, possibly in the middle of a freezing winter's night, with all the supplies and kit needed to refill the system, which in turn may be easier said than done?
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay yes I suppose you are right that you have to refill. I think if the outside is isolated from the inside this shouldn't be too difficult, but I think one should be mindful of the filling instructions in the manual eg mine says to run an air purge on the controller if I remember rightly.
I doubt anyone is standing by in the middle of the night. My point was once there's a power cut then you should isolate outside, and you probably have in excess of 12 hours before anything happens which is long enough for power to come back in most circumstances, but if it isn't then I personally wouldn't worry about adding anything but water when it does come back because my exterior piperun is less than 10% of my system volume, so I'd think about inhibitor another day. That's not advice of course.
My old gas boiler was in my unheated garage with only thin lagging on the pipework, so under such a power cut that too could have frozen along with the heat exchanger in the boiler but with no protection.
@oswiu - I hadn't joined up the dots, and read your post to mean - I think I have now got it - it is as if you had a power cut. Bottom line was, for whatever reason, you didn't have a functioning heat pump that could protect itself from frost damage. On anti freeze additives vs anti freeze valves, I suppose both have pros and cons, and so it is horses for courses. Anti-freeze additives offer 'fill and forget' protection, at a cost, and until they need topping up, anti freeze valves also work, and I gather are cheaper (though whether that should be a consideration when the cost differential is £ while the cost of repairing a frost damaged heat pump will be ££££), but that add in the hassle of refilling the system, albeit a simpler process because only water is used.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay yes that's right it was as if I had a power cut. This was the installation of my heat pump, so when the plumbing guys finished the pipework they filled the system up and went home, but the controller was showing an error and the ASHP wouldn't turn on. In the end they had to replace a cable the next day after it had emptied itself.
I discussed glycol vs the valves with my installer who gave me the option. I was keen to get the valves because they're cheaper to buy and you don't have to contaminate the water with less efficient glycol.
Posted by: @oswiudon't have to contaminate the water with less efficient glycol
True, I meant to mention that in the pros and cons but forgot. As I understand it, the dilution of heat carrying ability isn't huge, but neither is it trivial. I forget the exact figures, but even if is it only 10%, that means 10% less heat power delivered to the house, 9kW when an all water setup would deliver 10kW. That might well be enough to take marginal installations below the building's heat loss.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @oswiudon't have to contaminate the water with less efficient glycol
True, I meant to mention that in the pros and cons but forgot. As I understand it, the dilution of heat carrying ability isn't huge, but neither is it trivial. I forget the exact figures, but even if is it only 10%, that means 10% less heat power delivered to the house, 9kW when an all water setup would deliver 10kW. That might well be enough to take marginal installations below the building's heat loss.
The antifreeze in my ASHP has a Specific Heat Capacity of 3655 J/kg/K measured at 30% dilution at 25 deg C. Compared with water at 4184 J/kg/K that’s a 12.64% reduction, which seems pretty significant. Do antifreeze valves only operate if there is a prolonged power cut and low temperatures, assuming the ASHP has its own frost protection system?
@mike-h - I don't have anti-freeze valves, so don't know the answer. Maybe someone who does have them can answer.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @mike-hPosted by: @cathoderayPosted by: @oswiudon't have to contaminate the water with less efficient glycol
True, I meant to mention that in the pros and cons but forgot. As I understand it, the dilution of heat carrying ability isn't huge, but neither is it trivial. I forget the exact figures, but even if is it only 10%, that means 10% less heat power delivered to the house, 9kW when an all water setup would deliver 10kW. That might well be enough to take marginal installations below the building's heat loss.
The antifreeze in my ASHP has a Specific Heat Capacity of 3655 J/kg/K measured at 30% dilution at 25 deg C. Compared with water at 4184 J/kg/K that’s a 12.64% reduction, which seems pretty significant. Do antifreeze valves only operate if there is a prolonged power cut and low temperatures, assuming the ASHP has its own frost protection system?
Yes. Read my post above for a fuller explanation, but mine operate when the valves themselves are below 3C. This requires rare cold temperatures and a power cut several to many hours long.
A heat pump's frost protection should kick in a few degrees above the design temp of the valves. Mine is set to do frost protection from 6C, and it runs the water at 25C.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 634 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 36 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 9 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 9 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 13 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 13 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 15 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 17 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 17 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 23 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago