Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
The Daikin DHW Manual was vague in that it just said "Glycol", the Monoblock manual has these handy hints...
The installer has left this, none been added yet, its says its non-toxic and biodegradable
its here:
https://solarandheatstore.com/product/e600-heat-pump-thermal-fluid-25l/
contains Mono Ethylene Glycol ? not propylene
if it contains ethylene glycol, it's not non-toxic.
https://en.wikipedia.org/wiki/Ethylene_glycol_poisoning
The reason Daikin says to use propylene glycol in a system that includes DHW is that there is a small chance that the flow water could leak into the DHW and someone could drink it. Propylene glycol is much less toxic.
Anyway, that E600 says it's pre-mixed and doesn't need diluted. That suggests it should be used to fill the whole system. 25% or so of that in your system isn't going to do a lot. On the label it says "add HTF50 for lower temps". HTF50 is the full strength concentrated stuff, which is what the Daikin table refers to.
An alternative approach to using glycol is to use anti-freeze valves. Basically you put these at the lowest point of the ASHP outdoor circuit, and they open when the temperature in the pipe gets close to freezing. This allows the water to drain out and air to get in, preventing a burst pipe.
One question I have about glycol: if you want to make modifications to the plumbing, perhaps moving a radiator, if there aren't suitable isolation valves what do you do? With a normal system you might drain and refill, or use a pipe freezer, but you can't freeze the glycol and you'd rather not throw it away. Do you have to pump it all out, store it and and pump it back again afterwards?
I saw them mentioned somewhere else but had never heard of them. When I had 3 rads taken off to decorate I wasn't sure whether to bother topping up the glycol. In the end I did; the plumber closed the valves, removed the rads then put the glycol into one of them when he replaced them.
The installer is coming back next week to fix my MMSP, which will need the system drained. I think they said they would drain it into a container and re-use but we'll see.
My system has the expansion valves on both external pipes meaning only water is flowing. If the system is off and the pipes freeze, then the valves allow water to flow out before freezing. You then refill via the hydro box, in my case in the garage.
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Volvo EX30 Ultra Twin Performance electric vehicles with Myenergi Zappi mk1 & Ohme chargers
I asked for the glycol level to be checked for my ASHP as it's so frequently topped up due to endless pressure drops. Using a refractometer the guy said it should be safe down to -5°C. I told him that I am starting to see outdoor temps of -7°C but he wasn't concerned even though he said HP's are normally topped up to provide protection down to between -10°C and -12°C. I also live in an area with frequent power cuts, although these generally last only max 3-4 hours. Should I be concerned?
@saz The issue I had was with getting the ASHP manufacturer to provide breakdown cover. They said they wouldn't if the glycol level was too low. But they relented and would cover the system if we switched on the anti-freeze function on the controller. I have done that, and now, at the present very low temperatures (-6C at the moment), the recirculating pump is constantly running.
A chinese copy of the Celeffi anti-freeze valve, £19, screwed into a 28mm press T. All the anti-freeze protection you need, without a drop of glycol.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@scratchyman Yeah, the defrost cycle is enabled. I wouldn't want my circ pump running 24/7 to be honest with you. Getting crazy low night time temps here at the moment!. We get alot of power cuts. I'm trying to work out a balance between risk and reduced efficiency due to the glycol.
Posted by: @saz@hughf I've heard about these but unfortunately I wouldn't be allowed to make any mods to my system.
are you a tenant? If not, it’s your system, you can do with it what you please.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,697 Topics
- 63.3 K Posts
- 807 Online
- 7,106 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Electricity price predictions
Chinese manufacturing has the ability to be very good q...
By Majordennisbloodnok , 1 hour ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: GotGordon Manufacturer: Samsun...
By Gotgordon , 13 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
@ian33a I am not easy with sleep either unfortunately…....
By MK4 , 14 hours ago
-
RE: Renewables uptake near you
In a village of under 40 houses...Conservation Area. I'...
By Tim441 , 1 day ago
-
RE: Home Alone with Home Assistant (previously A Beginner's Guide to ASHP Monitoring)
Great news, @bontwoody.
By Majordennisbloodnok , 1 day ago
-
Haier R290 Super Aqua Monobloc. Output capacity tables.
As I mentioned in my introduction post, I've been consi...
By Singlespeed , 1 day ago
-
RE: Air to air bus grant installer anywhere
I am consistently told by aircon folks (ie air/air) tha...
By EtchedPixels , 2 days ago
-
RE: What is possible with FIT, SEG, Hate Pumps and Batteries?
Thank you, everyone, for your replies. Our FIT provid...
By ian33a , 2 days ago
-
@mk4 And of course, the panels are less productive due ...
By Toodles , 2 days ago
-
RE: GivEnergy inverter tripping due to over-voltage?
I'm trying to get clarity on exactly when the inverter ...
By Tim441 , 2 days ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Autocorrupt seems to be working overtime.
By Majordennisbloodnok , 2 days ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
I looked into that wallbox a bit more off the back of t...
By Majordennisbloodnok , 3 days ago
-
RE: Say hello and introduce yourself
@jandp awesome system I hope it works out well.
By Judith , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@bobflux That's the stuff. The installer recommended tw...
By tomasmcguinness , 5 days ago