Posted by: @trebor12345@jamespa Can I check something that I done some weeks ago.
My underfloor manifold is set via the 12 flow gauges to a total of 20 l/m. In the UI of the indoor unit I have reduced the primary pump from 28.5 l/m to 24.3 l/m.
Why did I do this. I was seeing a lot of mixing in the buffer tank. Reducing the primary pump flow rate to 24.3 l/m reduced the amount of mixing. Therefore the return temperature to the heat exchanger is reduced slightly (approx 0.5C). Hope this makes sence.
Yes this makes sense. Ideally you match flow either side of the buffer, at which point it is pointless (but that is anyway the case). Since a perfect match isn't possible its better to have slightly more flow in the primary than in the secondary. This should force the cold water to the bottom of the tank thus (hopefully) reducing the flow temperature loss across the buffer to near zero.
Posted by: @trebor12345Nothing really new, except that these Thermo Off periods are way tooooo long at 1hr 20 mins and 2hrs 20 mins.
Way too long based on what criterion. From what I recall from your earlier post the house wouldn't cool much in this time. So why does it matter?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaWay too long based on what criterion. From what I recall from your earlier post the house wouldn't cool much in this time. So why does it matter?
You always challenge my thinking! I don't specifically know why I think it's too long. My only thought is do other systems/users have that long time.
Yesterday it did take some time to get heat into building, the off's didn't help.
It was 0C over night, so when I turned the heating off at 11pm it was 22C, this morning it had dropped to 20.5C in the main living area (20sqm of glass), so a little cool for us.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
Posted by: @trebor12345You always challenge my thinking! I don't specifically know why I think it's too long. My only thought is do other systems/users have that long time.
Its not so much challenging as seeking to understand. Your house cools very slowly so provided that the right amount of energy is put in over several hours (which, if the WC curve is correctly adjusted it should), you wont notice it. It is quite a long off time but that said my heat pump will do that in one of its modes. My house cools quicker than yours so I do notice it, and therefore dont operate in that mode preferring pure weather compensation instead.
I am reasonably sure that the key to getting this to work is 24x7 operation on WC, with no human intervention other than, not more than once a day and always in the same direction, adjusting the WC settings. Once thats set up then the various behavioural features of the heat pump and your house can be observed and optimised or adapted if necessary. Until it is set up you are operating with a (largely human based) control system which is inherently unstable because of the delayed response of your house and the fact that the control system stops working overnight, and is therefore impossible to diagnose.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I find having my thinking challenged is always a good thing 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyI find having my thinking challenged is always a good thing 🙂
I’m always pleasantly surprised when I find out I’ve been thinking in the first place. 😎
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok ‘Sometimes, I sits and thinks, other times, I just sits’. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodles@majordennisbloodnok ‘Sometimes, I sits and thinks, other times, I just sits’. Toodles.
"I think therefore I am" - René Descartes
"To be is to do" - Socrates
"To do is to be" - Jean-Paul Sartre
"Do be do be do" - Frank Sinatra
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok Tibby or not Tibby - anyone seen my cat?
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @jamespaYes this makes sense. Ideally you match flow either side of the buffer, at which point it is pointless (but that is anyway the case). Since a perfect match isn't possible its better to have slightly more flow in the primary than in the secondary. This should force the cold water to the bottom of the tank thus (hopefully) reducing the flow temperature loss across the buffer to near zero.
JamesPa. Thats one thing that I do have right. Cross that one off the list.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
JamesPa Below is the plot of yesterdays run (30 Nov). Surprise NO THERMO OFFS. Ran for 10.5 hours. Im afraid it's a fluke!!!
I have always expressed the view that the HP is oversized, as you have found the Night/ECO setting, I turned it down to 50%. This is the result.
It's not a sustainable way to run the heating.
Does it tell us anything else?
I am looking at setting up the WC.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
- 26 Forums
- 2,418 Topics
- 54.8 K Posts
- 401 Online
- 6,098 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@editor I have now been allocated a complaint handler b...
By MairiA , 7 minutes ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
There is a third party app called iLetComf...
By Davesoa , 30 minutes ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
@ashp-bobba hey Bobba+Mars, thanks for jumping on the t...
By Patch321 , 60 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Here's that section of the Installation Manual: &nb...
By Transparent , 2 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@toodles Thank you for your input. As the days have got...
By Synthbuilder , 3 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Frost Protect/Freeze Stat is an operation mode, where D...
By F1p , 3 hours ago
-
RE: Fan unit Making terrible noise HELP!!
@gutoffowc Oh no, sorry to hear that, are you in the Ke...
By ASHP-BOBBA , 5 hours ago
-
RE: Sunsynk Whole House Backup Issue
@sheriff-fatman - could you please re-post that in the ...
By Transparent , 5 hours ago
-
RE: Running my new Nibe ASHP efficiently
I didn't. I spent a while manually messing around with ...
By jamieheatpumpnew , 7 hours ago
-
RE: I’m glad the cold spell is over!
I comparison with the 65kWh used above yesterday was on...
By Judith , 7 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
I should think so, I thought that pretty much universal...
By JamesPa , 8 hours ago
-
RE: Setback savings - fact or fiction?
I'm also inclined to look into how a defrost is actuall...
By cathodeRay , 8 hours ago
-
MLCP (Multi-Layer Composite Pipe) for ASHP
@editor nope. The info you reported was sufficient for ...
By iotum , 18 hours ago
-
RE: Experience - New Build / Complete New Heating System
@vincro I would be surprised if it is much above 5 to 6...
By ASHP-BOBBA , 20 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Yes bang on and maybe I can illustrate that by way of e...
By iotum , 22 hours ago
-
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
A big thank you to @jamespa for all his efforts online ...
By trebor12345 , 1 day ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor It is indeed for servicing. My current service ...
By Morgan , 1 day ago