Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
6 meter run of pipe from the outside to the UniSTOR Pure 200lt cylinder: do I go plastic or copper?
Regarding the install of a Vaillant 3.5Kw arotherm plus. I have a 6 meter run of pipe from the outside to the UniSTOR Pure 200lt cylinder: 1 meter in pipe insulation outside, 2 meters outside in plastic trunking up the wall, 4 meters in loft space.
Should I go with plastic or copper? What have others used?
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Go with PEX/PE-RT/Multilayer Pipe (plastic in other words). You have a lower thermal conductivity than copper, so you get better performance. It's typically also easier to install and you won't have potential corrosion issues. It's also cheaper.
My blog where I write about all the systems in place and decisions made for my off-grid house at 63 degrees north in Finland.
I would agree 22mm plastic can move close to 5kW so would be ample for your 3.5kW output
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
What matters for flow and pressure drop is internal diameter. Thus 32mm MLC (26mm internal diameter) is equivalent to 28mm copper (also 26mm internal diameter).
Ultraviolet from sunlight destroys PEX, so not recommended for outdoors use. It also has quite high thermal expansion and gets soft when hot. Thus it must be installed in conduit to be able to dilate and wiggle around freely. PEX's main advantage is being very cheap. Non O2 barrier PEX will let oxygen into your pipes, this will corrode your steel radiators and eventually destroy your installation. When using PEX for heating, always use O2 barrier PEX, which has very low but not zero oxygen permeability.
Copper and MLC have zero oxygen permeability so no worries.
Copper tube is expensive but brazed fittings are inexpensive and cause very low pressure drop, so copper is great for short but complex pipe layouts with lots of fittings, like plant room, manifolds, etc. Press fittings are quite expensive and require a specialized press tool, also very low pressure drop.
MLC has an internal aluminium layer which solves PEX's main issues. It is inexpensive, but fittings are expensive, take a lot of space and have high pressure drop due to the reduction in internal diameter.
So MLC is the opposite of copper. MLC is great for long pipe runs with few fittings (ideally just one at each end). Unlike large diameter copper bars, MLC is delivered in a roll and can be bent and curved quite easily, by hand or with a pipe bending tool for larger diameters, which helps running a single uninterrupted pipe from point A to point B with no elbows, no joints, no risk of leaks. No fittings makes it much easier to insulate, and you can even buy it pre-insulated. For this use it is ideal, costs much less than copper and requires much less work.
MLC is plastic so it shouldn't be allowed to rub on abrasive stuff like masonry.
You will need a press tool for MLC fittings.
Freezing bursts copper. PEX just dilates (but the brass fittings will burst). MLC pipe also tends to somewhat survive freezing, but not the fittings.
If antifreeze valves are fitted on the heat pump then all exterior piping should be sloped towards the heat pump to make sure in case of emergency it can all drain via the antifreeze valves. Otherwise the antifreeze valves will save the heat pump, but water remaining in a low point in the pipe can burst it.
Posted by: @bobfluxUltraviolet from sunlight destroys PEX, so not recommended for outdoors use. It also has quite high thermal expansion and gets soft when hot. Thus it must be installed in conduit to be able to dilate and wiggle around freely. PEX's main advantage is being very cheap. Non O2 barrier PEX will let oxygen into your pipes, this will corrode your steel radiators and eventually destroy your installation. When using PEX for heating, always use O2 barrier PEX, which has very low but not zero oxygen permeability.
Copper and MLC have zero oxygen permeability so no worries.
MLC has an internal aluminium layer which solves PEX's main issues. It is inexpensive, but fittings are expensive, take a lot of space and have high pressure drop due to the reduction in internal diameter.
I didn't appreciate that there was so much to a piece of plastic pipe. Done some additional research to find out more, concluding that:
PEX-AL-PEX
PE-RT-AL-PE-RT
Both types should be OK as it has the Aluminium layer to avoid 02 ingress issues. The RT variant may be slightly better for higher temperatures.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
I didn't appreciate that there was so much to a piece of plastic pipe. Done some additional research to find out more, concluding that:Posted by: @trebor12345
Had to learn the hard way 🤣 now I'm sharing
The house has underfloor heating with non barrier PEX installed by the previous owner, this ended up with all the steel radiators being corroded, rust sludge everywhere, and a perforated heat pump exchanger. Underfloor heating means lots of pipes, thus lots of O2... so I've been looking into pipes for a while now lol
MLC is great but it's a good idea to pick the fittings from the same manufacturer.
"PE-RT" means non crosslinked PE rated for "high temperature"... but the gotcha is than "non crosslinked PE" isn't so good at high temperatures to begin with, so the "RT" version is a bit of a "less worse" version. Crosslinked PE (ie, PEX) withstands high temps much better to begin with, the basic PEX-Al-PEX goes to 95°C, much higher than PE-RT! Took me a while to figure this one out........
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 1,246 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
Hi @ian33a you could do your own heat loss calculation ...
By Judith , 6 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@djh ah, I have never seen this before, interesting ide...
By ASHP-BOBBA , 6 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 6 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa — this version may be marginally better: &nb...
By cathodeRay , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 9 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 14 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 16 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 18 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 21 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 21 hours ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
That would be abnormal but I cant see from your charts ...
By JamesPa , 21 hours ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago