Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Buying large amp bidirectional RCD and RCBO

23 Posts
4 Users
8 Reactions
6,362 Views
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 5 years ago
Posts: 3522
Your energy: 109 kWh
 

@jamespa – fuses and trips must be rated according to the current-carrying capacity of the cable, not calculated on the load(s) you intend to supply.

So if you want to deliver 80A max to the larger CU, then that dictates the cable size and how it can be carried/supported.
Fixing a cable to a solid surface (like a wall) by using clips, will give it a different rating than running the same size cable through conduit.
It affects how much heat can be radiated away into the air.

A professional electrician would look at the building and decide a route and fixing-strategy which has least adverse affect on the current that the cable can carry.

Sometimes he/she will use the 'standard' Twin & Earth cable (6424Y) which is most commonly used in domestic properties,
but there are other circumstances when more current could be passed by running 'singles' (6491X) through a 20mm diameter plastic conduit.

There isn't a 'standard' mains cable size between 16mm² and 25mm².

 

Let's assume you'd prefer to pay less for the 16mm² cable size:

To achieve 80A capacity using twin&earth it would need to be in free air for its entire length. That would give a rating of 83A.

If 16mm² single-cored wire was pulled through a conduit, then it would be rated 74A – 85A, depending on length and how much free space there was left in the conduit.

So you're asking for something which is close to the limits for that size of copper conductor.

 

Having an 80A Service Fuse might not be regarded as sufficiently fast protection for that 16mm² cable.
It could still get hot enough to be dangerous without the fuse blowing.

It's likely that an electrician will require a faster-acting MCB to which the cable is connected.

 

I can't immediately find an 80A MCB on the wholesaler sites I've just looked at.
They may not exist.

But there are 80A RCBOs with 30mA 'earth leakage' protection, with prices around £30.

 

The transfer switch must be rated at 80A minimum.
In practice you'd probably select one with 100A capability.

The MTS is not going to act as an MCB.
It doesn't 'trip out' if you try to draw more current through it.


This post was modified 10 months ago 2 times by Transparent

Save energy... recycle electrons!


   
Like
2
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5771
Your energy: 157 kWh
 

Posted by: @transparent
↑

@jamespa – fuses and trips must be rated according to the current-carrying capacity of the cable, not calculated on the load(s) you intend to supply.

So if you want to deliver 80A max to the larger CU, then that dictates the cable size and how it can be carried/supported.
Fixing a cable to a solid surface (like a wall) by using clips, will give it a different rating than running the same size cable through conduit.
It affects how much heat can be radiated away into the air.

A professional electrician would look at the building and decide a route and fixing-strategy which has least adverse affect on the current that the cable can carry.

Sometimes he/she will use the 'standard' Twin & Earth cable (6424Y) which is most commonly used in domestic properties,
but there are other circumstances when more current could be passed by running 'singles' (6491X) through a 20mm diameter plastic conduit.

There isn't a 'standard' mains cable size between 16mm² and 25mm².

 

Let's assume you'd prefer to pay less for the 16mm² cable size:

To achieve 80A capacity using twin&earth it would need to be in free air for its entire length. That would give a rating of 83A.

If 16mm² single-cored wire was pulled through a conduit, then it would be rated 74A – 85A, depending on length and how much free space there was left in the conduit.

So you're asking for something which is close to the limits for that size of copper conductor.

 

Having an 80A Service Fuse might not be regarded as sufficiently fast protection for that 16mm² cable.
It could still get hot enough to be dangerous without the fuse blowing.

It's likely that an electrician will require a faster-acting MCB to which the cable is connected.

 

I can't immediately find an 80A MCB on the wholesaler sites I've just looked at.
They may not exist.

But there are 80A RCBOs with 30mA 'earth leakage' protection, with prices around £30.

 

The transfer switch must be rated at 80A minimum.
In practice you'd probably select one with 100A capability.

The MTS is not going to act as an MCB.
It doesn't 'trip out' if you try to draw more current through it.

Thanks, I understand and indeed understood all of that, which is why my original diagram  showed thick cable (illustrated by a thick line) from service fuse to MTS and again from MTS to CU, and (at least in my mind) a 100A changeover switch, thus preserving the integrity of the cable and interrupter capacity relative to the (80A service) fuse right up to the point where it enters the CU (diagram reproduced in part below - ignore the question in the call out - that has now been resolved - it is necessary).  Your suggestion of a lower rated MTS complicates that relatively simple model, and requires yet another component between the service fuse and what would otherwise be the first point of interruption, in order to preserve the integrity with the lower rated components you suggest using.  Its possible of course, but putting another component in the box which must, in practice, be worked on 'live' (I have yet to see an electrician call out the DNO to interrupt the service and reconnect it!) seems like a retrograde step if it can be avoided.

I think the safety parameters are now sufficiently clear (for which many thanks) and the limiting factor is the  components that can be purchased from a company that I and the electrician trust, which in the case of a component required to stand 100A, is unlikely to include a one from an unknown Chinese manufacturer advertised on Alibaba or eBay!  Given the relatively small choice that I have found so far, that will probably determine the detailed design.  There do appear to be 100A transfer switches available from CES or the like, but unfortunately sold in an enclosure that is full already.  As the same enclosure ideally needs also to accommodate the two 32A MCBs protecting the inverter, that wont do.  I suppose that, in the limit, I could buy the enclosure plus switch and throw away the enclosure, but that feels a bit silly.

Hopefully a more in depth search will turn up a suitable part!

Once I have a final design with available components I will post it again.

 

image

This post was modified 10 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote
Batpred
(@batpred)
Vaillant
Noble Member Member
Joined: 2 years ago
Posts: 1253
Your energy: 31 kWh
Topic starter  

Posted by: @jamespa
↑

The main fuse is 80A, I was told to upgrade from 60A before getting an ashp.  In retrospect I don't know why.  However, given that this is rhe case it seems to me the transfer switch has to be rated at at least 80A as does everything else downstream until MCBs are reached.  Of course I could put in  63A MCB immediately prior, but its getting a bit silly tge number of components.

With our 8kw inverter we did not need any MCB over 63A (and that was just because Solis required 36.4*1.25 and we had to round up)... 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5771
Your energy: 157 kWh
 

Posted by: @batpred
↑

Posted by: @jamespa
↑

The main fuse is 80A, I was told to upgrade from 60A before getting an ashp.  In retrospect I don't know why.  However, given that this is rhe case it seems to me the transfer switch has to be rated at at least 80A as does everything else downstream until MCBs are reached.  Of course I could put in  63A MCB immediately prior, but its getting a bit silly tge number of components.

With our 8kw inverter we did not need any MCB over 63A (and that was just because Solis required 36.4*1.25 and we had to round up)... 

I am sure I wont need anything bigger for the inverter, but the grid supply is fused at  80A so any components and cable upstream of the first MCB have got to be rated for 80A or above.  The thick lines in the diagram I drew were intended to depict that.  

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

Batpred
(@batpred)
Vaillant
Noble Member Member
Joined: 2 years ago
Posts: 1253
Your energy: 31 kWh
Topic starter  

Posted by: @jamespa
↑

Posted by: @batpred
↑

Posted by: @jamespa
↑

The main fuse is 80A, I was told to upgrade from 60A before getting an ashp.  In retrospect I don't know why.  However, given that this is rhe case it seems to me the transfer switch has to be rated at at least 80A as does everything else downstream until MCBs are reached.  Of course I could put in  63A MCB immediately prior, but its getting a bit silly tge number of components.

With our 8kw inverter we did not need any MCB over 63A (and that was just because Solis required 36.4*1.25 and we had to round up)... 

I am sure I wont need anything bigger for the inverter, but the grid supply is fused at  80A so any components and cable upstream of the first MCB have got to be rated for 80A or above.  The thick lines in the diagram I drew were intended to depict that.  

The approach in my case was as follows:

- supply is 100amp

- tails (I think 25mm) connect to Henley box 

- tails connect from Henley box to CU 

- CU has a 63Amp MCB for grid port (as 36.4*1.25 is 45.5 and the cable could take more) . But a 50Amp MCB could have been used instead

- 16mm cable to grid port 

- the same CU also has a RCBO of 16amp for sockets, connecting to 2.5mm cable. 

The goal is, as I am sure you are aware, just to make sure that each section of cable is protected by an MCB of lower rating than the maximum rating of that cable. 

It was decided that the maximum required for the house (excluding EV and a small CU) was 36.4A. This was based on the inverter capacity (but it would be 50 with the same inverter if used with an AC coupled inverter on the smart port). So we no longer consider we could have a 100A supply to the house. Does this approach help?  

 


This post was modified 10 months ago by Batpred

8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC


   
ReplyQuote
Batpred
(@batpred)
Vaillant
Noble Member Member
Joined: 2 years ago
Posts: 1253
Your energy: 31 kWh
Topic starter  

We mentioned a need for bidirectional rcbos.

It needs to be made clear that, in a system with multiple generating units, all that can be named bidirectional are some of the cables where the power flows in different directions.

An alternating current changes direction 100 times a second. So no issue can be caused to an RCBO or RCD by the direction of the current. 

As @transparent mentioned, 

But if there is power still being applied in the reverse direction by an inverter or storage battery, when the contacts open, the solenoid remains energised.

But if there could be an issue caused by extraneous DC currents, is there a reason to not describe it as such? 

And while it does seem that the Beama manufacturers association could have caused confusion, it actually commented on a British electrical labelling standard indicating switches have input and output. 

The iec international standards do not seem to be particularly concerned about 'bidirectional' rcbos. 

 


This post was modified 10 months ago by Batpred

8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC


   
ReplyQuote
bobflux
(@bobflux)
Reputable Member Member
Joined: 9 months ago
Posts: 229
Your energy: 27 kWh
 

Noark makes 100mA/63A and higher RCDs.

FYI the reason for going above 30mA are:

- Higher power inverters have larger EMI filter caps causing higher leakage to ground

- PV panels form a plate capacitor between themselves and the nearest grounded conductor, which is either the roof (when dry) or the rainwater film on the panel (when wet). The more panels the higher the capacitance. In inverters without insulation between PV and Mains this capacitance creates AC common mode leakage current. On rainy days, my 12kWp has capacitive leakage of about 40-50mA, so the system would be unusable with a 30mA RCD.

 

 

 



   
ReplyQuote
Batpred
(@batpred)
Vaillant
Noble Member Member
Joined: 2 years ago
Posts: 1253
Your energy: 31 kWh
Topic starter  

Posted by: @bobflux
↑

Noark makes 100mA/63A and higher RCDs.

FYI the reason for going above 30mA are:

- Higher power inverters have larger EMI filter caps causing higher leakage to ground

- PV panels form a plate capacitor between themselves and the nearest grounded conductor, which is either the roof (when dry) or the rainwater film on the panel (when wet). The more panels the higher the capacitance. In inverters without insulation between PV and Mains this capacitance creates AC common mode leakage current. On rainy days, my 12kWp has capacitive leakage of about 40-50mA, so the system would be unusable with a 30mA RCD.

Thanks for sharing. 

We initially used Wylex 100mA RCD. But the uk electrical regulations mandate use of bidirectional devices when protecting circuits connecting multiple sources of generation. 

A bidirectional RCD device ensures that, when it opens the circuit, the device itself will not be damaged in case the output ports are still energised (which can happen due to malfunction of an inverter). 

To our knowledge, this requirement for bidirectional RCDs does not exist in other European countries. 


This post was modified 9 months ago by Batpred

8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC


   
ReplyQuote

bobflux
(@bobflux)
Reputable Member Member
Joined: 9 months ago
Posts: 229
Your energy: 27 kWh
 

Most if not all type A/AC RCDs are bidirectional... Ironically, manufacturers seem to consider this too obvious to explicitly mention it in the datasheet 🤣 or even on the fine print on the device itself.

It's common to wire the input on the top or bottom, whatever allows most convenient wiring for the rest of the panel... unless the device has an arrow indicating direction.

Noark shows both direction arrows:

image

The breaker/switch component is designed for AC so it has neither direction nor polarity.

If the datasheet mentions "Voltage independent" then the tripping mechanism is powered by the fault current itself through the current sense transformer, so the sensing circuit isn't actually connected to the terminals, hence bidirectional.

However if it contains electronics which must be powered (Type B...) then there's probably an IN and an OUT direction.

DC breakers though, tend to have a direction for current (not voltage) and will probably explode or start a fire if connected wrong.

 



   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 5 years ago
Posts: 3522
Your energy: 109 kWh
 

Posted by: @bobflux
↑

DC breakers though, tend to have a direction for current (not voltage) and will probably explode or start a fire if connected wrong.

I can answer that point! 🙂 

DC breakers have a pair of magnets either side of the arms which have the contacts at the end.

When the contacts open, the magnets pull the resulting DC arc into a series of metal plates called the arc-ladder where it gets quenched.

MCB1

 

If the DC wires are connected the 'wrong way around' then the outcome depends on the current which is flowing.

At low currents of 10A or so, the contacts open but the arc causes pitting on them. It's not that serious, but can increase the time taken for the trip to operate in future.

At high currents (100A) the magnets force the arc onto the contacts which welds them together. Current continues to flow to downstream devices because the circuit remains 'live'.

 

DC Breakers rated at 125A are commonly used as manual isolators between inverters and storage batteries. That means the direction of current changes depending on whether the battery is charging or discharging. Inevitably that means the breaker will sometimes be 'the wrong way round'.

For that reason it's good practice to also have a high-capacity fuse in series with the breaker. Should the contacts get welded together, it's the fuse which provides the required level of safety.


Save energy... recycle electrons!


   
Like
2
ReplyQuote
bobflux
(@bobflux)
Reputable Member Member
Joined: 9 months ago
Posts: 229
Your energy: 27 kWh
 

Yes... I went through this particular headache and ended up with NH00 fuse holders / disconnectors. Very robust and reliable, since they're just fuses and contacts. Yanking the handle pulls the fuses out. 125A DC fuses are available in NH00 format. 

 