Battery with existing PV - regulations
Im now looking again at batteries because recent changes in tarifs (which are no surprise and I suspect are the direction of travel) have altered the equation. I have grid tied solar and I am looking at grid tied AC coupled batteries. Ideally I would want islanding to be possible to cover power cuts and 3.6kW output maybe a bit more
At this stage I am trying to get my mind around the regs. As I understand it
a) even if the battery inverter is set so that it does not discharge when this would lead to export, I still need G99, which will need to specify both inverters, because the DNO assumes it might export. This might limit the max output of the battery inverter even though its not intended to export
b) If the inverter does support islanding, there must be a suitable cut out device |(presbetween the supply and any part of the internal wiring that will be energised during a power cut, to ensure that nothing is fed back to the grid in this circumstance
Have I got this correct? Im not trying to 'design' the system, just understand so I am an informed customer!
Also, has anyone looked seriously at sodium ion batteries. They seem to be obtainable and are, at least prima facie (but who knows what happens under the hood), more ethical in production and lower fire risk.
Sorry to ask simple questions, Im starting on a new learning curve here!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaa) even if the battery inverter is set so that it does not discharge when this would lead to export, I still need G99, which will need to specify both inverters, because the DNO assumes it might export. This might limit the max output of the battery inverter even though its not intended to export
I have just been through this. I had an electrician connect a battery to an inverter to my consumer unit (and I had previously had the CU replaced to improve safety).
I am not familiar with combined battery+inverter, my preference was to have a set that works, I chose low voltage lifepo4 as I understood it was the best value. I made the mistake to get a battery kit, there are now ready made 16kwh batteries starting at £1000.
I chose a solis hybrid inverter that provides 4ms switch from power failure, essentially it is fast enough that no device notices it. I did some tests. I switched the consumer unit off, all ok, the inverter made a few clicks and all continued as normal. I then switched it back to grid, again no issues, no flicking, as the inverter kept handling the load with the battery. It took some time to defer to use grid power. I think these timings are mandatory for approval.
I was not planning to export, but when I contacted my DNO (UK Power Networks) to let them know I had an inverter, they said they did not need to know unless I would be exporting. They "offered" 5kw export and said "just fill in the details in the initial G99 form as if G98". In short, right now I have an export MPAN.. for 8kw.. All without any MCS overhead.
As I underspent, we are now considering investing the spare funds and getting PV a bit earlier than we thought.
The regs may be a bit more restrictive than what UKPN allows.. So it may depend on what your DNO says and it may depend on your local grid as well.
Posted by: @jamespab) If the inverter does support islanding, there must be a suitable cut out device |(presbetween the supply and any part of the internal wiring that will be energised during a power cut, to ensure that nothing is fed back to the grid in this circumstance
Have I got this correct? Im not trying to 'design' the system, just understand so I am an informed customer!
Officially you may, and there is apparently only one brand of inverter in the list that does not require a separate device.
@transparent kindly provided an explanation of the oscillators the inverters have to support islanding, etc.
Still, my experience was that UKPN was happy to accept the Solis G100 capability. I contacted them after the system was up and running (I always made sure it was set to not export). When filling in the G99 commissioning form, provided the inverter is type approved, much of it does not need to be tested on your installation. it is "out of the box". Very little work involved, it seemed. They were very helpful.
Posted by: @jamespaAlso, has anyone looked seriously at sodium ion batteries. They seem to be obtainable and are, at least prima facie (but who knows what happens under the hood), more ethical in production and lower fire risk.
That may be a longer route.. If you search for sodium, some suggestions were made, but I think nobody ordered it, or if they did, I do not recall a report of the experience.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
G99 needed for ac coupled battery. DNO will assume it can export unless it is type tested G100 and installed how the DNO likes to be export proof. Limiting export via software settings is not considered inherently safe or reliable.
PV inverter + battery inverter together count as combined generation capacity.
If you want it to power the house during a grid outage, it must have a certified anti-islanding mechanism. Must comply with Engineering Recommendation G98/G99 and ENA anti-islanding requirements.
Sodium ion batteries are heavy, LFP cells are now so cheap the shipping is the majority of the price. So sodium has to "compete" against that. Sodium is dirt cheap, but you'll never avoid the weight. The temp tolerance is moot in domestic storage application where its being constantly cycled. They have lower power density and a wider, annoying, voltage range, which means inverters will need to change for them.
To make clear, my Solis inverter has anti islanding. But because it has a couple of separate ports that it can serve independently from the grid, those can continue to work based on PV or battery. So only the grid port looses power to prevent islanding.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Hi It well worth getting the G99 as it opens up "options"
I have the give energy AIO and "gateway" and yes i to had to get a G99 giving me 9.64kw export.
the AIO can discharge at 6kw which works for us.
the Gateway will go into "island Mode" if the grid is down all Automatically.
also when the AIO is support the home any solar will continue to charge or run the house, without the need for the grid.
A 2 box solution, just works ! and is tidy !
I see the Powerwall 3 can do a higher discharge and they do an equivalent to a "gateway"
Regarding Sodium I think in a year that be more options but your need more space for the same capacity.
I to will expand my storage with sodium when it more of a option..
Posted by: @swwils@batpred The EPS output can be tricky to do to current regs. The old "rcd socket for type 2 only!" doesn't really cut it anymore.
I have the export MPAN, what are you talking about?
This is how it is working, before exporting..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @rob-heatpump-bobRegarding Sodium I think in a year that be more options but your need more space for the same capacity.
I to will expand my storage with sodium when it more of a option..
I am curious... which inverter would you go with for sodium batteries?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @rob-heatpump-bobI have the give energy AIO and "gateway" and yes i to had to get a G99 giving me 9.64kw export.
We submitted our papers for SEG, so hopefully we will soon unleash our inverter with export. Keen to see what Solis AI can do with that.
@rob-heatpump-bob I am curious if your DNO accept 9.64kW on a single phase circuit?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,426 Topics
- 55.1 K Posts
- 149 Online
- 6,104 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Is it normal to use power from the grid when running off the battery?
@batpred I may be asking you for more info in how you h...
By JohnnyB , 6 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
@johnnyb The noise of the Solis is nothing very sign...
By Batpred , 6 hours ago
-
RE: Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
@papahuhu Yes, good information is often hard to find, ...
By Old_Scientist , 6 hours ago
-
RE: R290 and Foundation Air Bricks
Professional risk assessment (inc some common sense) ...
By ASHP-BOBBA , 7 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@toodles ahhh no trouble yeah probably won't mess with ...
By Burtis , 7 hours ago
-
RE: Daikin Wireless Thermostat
@bash we have mostly south facing rooms which would ove...
By Judith , 8 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Some more examples of those that really should be benef...
By Jeff , 10 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
I've now had an interesting email from a Complaints Res...
By MairiA , 11 hours ago
-
RE: Reliable, easy to use home battery options
Correct. LiFePO₄ cells mustn't be charged if their te...
By Transparent , 11 hours ago
-
RE: Water outage in the the south-east
Indeed!Any contamination in the well water would be tra...
By Transparent , 13 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I hear some cases of apparent misconfiguration of inver...
By Batpred , 14 hours ago
-
Are split ASHPs with R290 refrigerant coming soon?
Question. Are there any (or likely to be in the near t...
By iotum , 16 hours ago
-
RE: Setback savings - fact or fiction?
Indeed. In many ways, a defrost is a setback, with the ...
By cathodeRay , 16 hours ago
-
RE: Heat pump not reaching flow temperature
The good news is that it leaves no excuse if it doesn't...
By JamesPa , 16 hours ago
-
RE: How to use my Hanchu battery storage for home without it feeding back into the grid?
@countryman-helmsley In that case is there a button ...
By IRMartini , 16 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Great. It’s not bad is it, though I agree it may repres...
By Davesoa , 18 hours ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
@f1p apologies, you are absolutely correct
By Patch321 , 18 hours ago
-
RE: Samsung E101 Error Message and my ASHP Efficiency
@johnnyb amazing that the our forum is serving its purp...
By Mars , 1 day ago
-
Best option for controller upgrade? - Grant Aerona
Fairly new heat pump owner - Grant Aerona 3 10kw - and ...
By Topher , 1 day ago
-
Just a brief update to keep things transparent. Secti...
By DREI , 2 days ago