Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @transparentPosted by: @batpredIn my case, my voltage reads are now 240V. They should be 230V, so should I consume less?
...
The 'Declared Voltage' for LV is currently stated as 230v RMS
..
Since inverters have been pre-certified to G98/G99, they are more likely to decouple themselves from the grid due to low-volts detection.
Ok, my Solis can work to a huge variety of global grid standards. At the moment, it is working on G99, it is something that the engineers asked me early on to confirm before it connected to anything beyond the battery. Is the name for this new standard cenelec something or has bsi come up with a different prefix? I believe this type of info on grid standards is deployed to inverters via firmware updates.
A small setup like mine (where I do not think I will ever have more than 4kw solar with current panels) will just be expected to have an inverter that backs off if the local grid has a problem, or am I missing anything? To enable normal recovery of the grid, after which my Inverter would connect back to the grid?
It would be nice to be able to confirm that the standard that will replace g99 is in a future Solis update..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Given the underspent for the budget of the Solis inverter and battery 😀 😉, we are considering the next step: adding PV panels.
Just wanted to share our schedule of works and get views:
"We are taking care of the G99 approval with UK Power Networks. We expect to get SEG 8kw export via smart meter in a few weeks..
We assume you would use flat-roof ballasted frames (without penetrations) and a one-storey rear scaffold mounted in the back extension only. The roof has no shading except a small chimney.
A. Panels & mounting (flat-roof ballasted trays/frames, rails, clamps, ballast). Mounting on felt/bitumen. Would you install it as 2 strings into the existing hybrid inverter?
C. Scaffolding (one-storey rear access, small run, 1 week hire?)
D. Bird spikes along top edge (say 6–12 m)
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
So I submitted the SEG application to Octopus. Fingers crossed, perhaps it will not be tripped by any silly building regs "checking the checkers" process.
I did not manage to confirm if the G99 standard for low voltage is 230V. And is it replacing G59?
My DNO (UK PN) seems to supplying 240V in my area... Should my inverter be set to work at G59 in the meantime?
Or would there be another name for UK's 230V?
From what I see, the G99 Type A from ENA is a relevant document..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
G59 has already been replaced by G98 five years ago.
It's the type certification against which manufacturers of inverters are required to have their products tested.
G99 applies to installations which have more than one G98-certified device,
or where the electricity to be exported exceeds 16A per phase.
The voltage level of the mains supply isn't defined within the EREC G-standards.
The 'Declared Voltage' is already referenced to 230v, and not 240v AC
Thus the interpretation of the Electricity Specifications [...] Act
is that LV must be between 216.2v and 254v AC, single phase.
UKPN, in common with all other DNOs, would normally keep the LV supply at 240v.
That allows greater voltage-drop to occur before G98-certified equipment would remove itself from the grid.
The Electrical Networks Association (ENA) is discussing the possibility of reducing the notional grid voltage to actually be 230v.
That wouldn't require any additional legislation of course.
However, for appliances which adjust their electricity-demand based on watts, such as EV chargers, PCs, televisions and heat-pumps,
the grid current would increase to compensate for the lower voltage.
That creates problems on the 11kV level of the distribution grid...
... which might be reflected in more outages due to thermal overload.
There is no easy answer within the scope of DNOs.
Save energy... recycle electrons!
A quick check shows the Solis inverter includes G59/3, G98 and G99 settings.
Based on the fact that the DNO approved 8kW export (so over 32Amp), I understand that I should keep it set to G99.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
If the Solis inverter has a configuration setting labelled G99, then by all means leave it set for that.
But it's a misinterpretation of the regulations by Solis.
Their inverter can't 'know' what other in-house devices are counting towards the export levels approved by a DNO.
This is the sort of detail I feed back to manufacturers.
In this case it would perfectly satisfactory to have configuration 'G98' because that's what they were required to test the inverter for.
Provided that setting still allows you to configure export levels above 16A/phase, then there is no reason why there should be an option to define 'G99' in that field.
Save energy... recycle electrons!
Posted by: @transparentIf the Solis inverter has a configuration setting labelled G99, then by all means leave it set for that.
But it's a misinterpretation of the regulations by Solis.
Their inverter can't 'know' what other in-house devices are counting towards the export levels approved by a DNO.
This Solis inverter being rated 8kw and (I expect, as I did not test) also allowing export of max 8kw, it should be operating to g99 when connecting to the grid.
The solis does allow the voltage on the backup port to be independently set. But that is only effective when the grid port does not sense power and the port is fed from dc sources (perhaps also if the grid power is outside the expected parameters). In normal circumstances, the backup port power mirrors the grid input.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
So I hear the export MPAN that UKPN assigned should be put to use soon. 🙂
My learning in this process will be to argue more robustly (and immediately) when an electricians' firm (no matter how large) claims they can replace your consumer unit without notification.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
I feel that the topic of labelling an inverter installation correctly is important enough to justify adding it to this thread (since critical for safe work by any electrician working in your home in the future).
Posted by: @transparentPosted by: @batpredThe regulation mandates labels indicating that there are multiple generation sources in the site.
Would you care to say which regulation you're referring to?
When I was looking for the regs for labelling when introducing an inverter able to export, I started with some of the questions present in the G99 commissioning form like:
- Generator’s Installation satisfies the requirements of BS7671 (IET Wiring Regulations).
- Suitable lockable points of isolation have been provided between the PGMs and the rest of the Generator’s Installation.
- Labels have been installed at all points of isolation in accordance with EREC G99.
As I wanted to make sure the electrician would have the required labels, I bought a set of labels that was suitable for a PV installation in advance. A subset of these were then applied in and around the consumer unit and inverter. By this I mean something like the set below:
For guidelines and an overview of labelling, this IET article may help. Ultimately qualified electricians have access to the current regulations.
And of course, always make sure to use a registered electrician.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @bashHow was the process for getting Octopus to agree to export without an MCS certificate in the end? Did you have to pay anything?
We also don't have an MCS certificate and I am interested in exporting in the warmer months when our battery bank will have plenty of spare capacity.
Yes, it was a very reasonable payment. Less than 10% of the £3200 the full MCS service would have costed us (of course not directly comparable)!
Posted by: @batpredSo I submitted the SEG application to Octopus. Fingers crossed, perhaps it will not be tripped by any silly building regs "checking the checkers" process.
This is what worked with a few iterations.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@bash My DNO had already issued me with the MPAN.
So while the Octopus process was not a "no win no fee" type of process, it was a calculated risk. Before the summer it will have paid off. Hope that it works for you!
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 557 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago