Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Our journey through Octopus tariffs 2020-2025
Everyone will have a different setup, usage, needs etc but it still might help others to see our journey from oil heating to ashp that will likely see us import over 14500kWh and export around 7500kWh this year - at a net negative cost.
Background
Somerset based
Listed Grade 2 building with large modern extension. Approx 100sq m old building & 100 sq m modern, well insulated
LG Therma V 16kw ASHP Installed Aug 2020
Underfloor heating throughout downstairs + Rads Upstairs
Fixed flow first 2 years then changed to weather compensation in winter 2022. Reducing heat pump usage from circa 8000kWk/pa to 5800 - saving 27.5%
8.7kw pv solar (2.2kw on FIT 2015 south facing, 6.5kw installed 2021 on east facing, low pitch)
3 x 8.2kw GivEnergy batteries installed 2021
1 x GivEnergy Gen1 hybrid 5.0kw inverter. Important to note max charge/discharge rate 2.6kWh that limits ability to take full advantage of cheap charging etc.
Manual changeover EPS
MG4 EV From 2023
WonderWatt used to help manage imports and exports
Comparisons
Comparisons are not easy due to changes in usage as well as:
- we did not record previous oil usage or cost. At a guess 2500litres/pa
- Move to weather compensation ashp Dec 2022 from fixed flows
- EV from 2023
- 2025 move to Intelligent Go meant batteries used more over summer to maximise cheap overnight imports and maximise exports
Rough numbers:
- ASHP uses 5800kWh/pa
- Solar prod 6500kWh/pa (7000kWh in exceptional 2025 and shading reduced)
- Exports prior to 2025 ~2500kWh/pa
- Exports 2025 ~7500kWh with forced emptying batteries. Income £1125 + FIT
- Imports therefore changed a lot to include additional battery filling at night for forced exports in summer + EV etc
- EV charging at home ~2500kWh/pa
- Fixed tariffs 2020 - Feb 2023
- Tracker Feb 2023
- Agile Mar 2024
- Intelligent Go Jan 2025
- Tracker averaged 16.15p - saving at least 20% vs standard/fixed tariffs
- Agile averaged 12.03p - saving around 50% vs standard/fixed tariffs
- Intelligent Go so far this year has surprisingly averaged 7.5p. Vast majority imported at cheap rates (overnight plus extra slots). Cost for full year likely to be ~£1100
- Faff factor is important. Hence use of WonderWatt to capture cheap slots on IG. Also used it for Agile to help manage. Also helps manage exports to maximise without running batteries down too much.
- At a guess oil would cost us ~£1500 pa now if still using.
So net import/export cost for us this year is roughly zero. Obviously capital costs need to be factored in.
Fwiw the heat loss calcs for heat pump suggested
27597 kWh of which 23800 was heating & 3800 hot water
Actual usage of 8000kWh on fixed flows might suggest average SCOP of just over 3? Our heat pump does not record SCOP
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
That’s a great journey to read. We’ve all got different combinations of tech, purchased at different times. It clearly helps to have large roof areas pointing the right way!
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
@judith its interesting to see the 6.5kw array is at just 5deg pitch and facing east. I suspect they produce 90% or more of the production if they'd been optimal south facing on normal pitch. Luckily they're single storey high so i can clean them with brush and hose pipe. Dirt is therefore not an issue - if left uncleaned i suspect buildup of lichen and sahara dust etc would cause a problem over time.
The older array is south facing and around 40deg pitch
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441...
Dirt is therefore not an issue - if left uncleaned i suspect buildup of lichen and sahara dust etc would cause a problem over time.
...
Now that would be a really interesting point to get clarified. I've never cleaned our panels and they're pretty much as clean now as they were when first installed, since the rain, sleet and snow do a pretty good job of cleaning for me. However, with your panels at just 5 degrees I can understand why there might theoretically be a difference.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
I mentioned above
"2025 move to Intelligent Go meant batteries used more over summer to maximise cheap overnight imports and maximise exports"
A small reminder that there is a round trip loss caused by converting grid import to battery and re-export. I think most people suggest this is around 10%.
So with IOG imports at 7p+ vat and exported at 15p is still very worthwhile. Especially as i can do automatically for the most part. But of course will need to watch if export rates drop etc.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
-
Who's your electricity provider and what's your tariff?
1 week ago
-
EV+ Heat Pump Tarriff
4 months ago
-
Confusion over Octopus Tariffs
5 months ago
-
Octopus tariffs - a quick comparison
7 months ago
-
Agile: average import cost vs other tariffs?
12 months ago
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 282 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 4 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 4 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 4 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 5 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 6 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 7 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 9 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 9 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 11 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 14 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 17 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago