Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Type 11 vs Type 22 radiators with a 5 kW Vaillant aroTHERM plus heat pump
I had my heat pump installed in June 2026, so really my first winter season. It is a Valiant aerotherm Plus 5kw, in a 80sqm 80's bungalow estimated heat loss calculation of 5.62kw at -1,3c (Cornwall). it was a zero disrupt install, type 11 rads left in place, apart from 1 original type 22. I replaced the bathroom towel rad with one twice its size. On commissioning the system was set to Weather compensation (WC) of 4 with min flow of 20c and max of 45c. WC cut off outside temp 16c.Â
The first time it came on it was cycling for 30-40 mins and not increasing the inside temperature flow temp was 20c and left me thinking. The thoughts i came up with were that the type 11s didn't dump any heat into the house (or very little) returned to the pump which switched off thinking the house was up to temperature. but inside it wasn't 15-16c.
Long story short i have ended up with this setting, WC 6.5, min flow temp set to 33c max 45c, expanded thermostat setting at 19.5c with setback to 18.0c overnight. the Deg min setting up to 120 (max), in milder temps 12c outside still get 50-60 min cycles, DT on flow/return measured on the pump sensors of 2 to 2.5C, but coldest temp overnight of 1c to 5c yields run times of 3-4 hours at around 35-37c after initial start up and DT flow /return 3 to 3.5c.
On these colder days total daily electrical consumption is 10-14kwh cop of 3-3.5, milder days consumption of 6-8Kwh cop 3.5-4.0. Which doesn't seem bad. the bungalow is comfortable for me. it hasn't really been tested yet with an extended cold spell so still in Beta testing i guess.Â
I guess my question is and I can't find a lot about running on type 11s to compare too. is this acceptable? could it be improved? is it worth the cost to upgrade to type 22's? Anyone else running on type 11s?