Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
CTC EcoAir 510M heat pump cycling with a 4-port buffer tank - advice needed
Hi guys
we have a CTC system that was installed 4 years ago by our housing association’s contractors it comprises of a CTC Ecologic M Controller with a CTC EcoAir 510m heat pimp a Joules DHW cylinder (in loft) and a 4 port buffer tank (pic of tank etc below). We had a full repipe work and oversized rads fitted as part of installation with a CTC room sensor fitted in livingroom next to the TV on a sunny wall.
We are still having issues with the system not being very economical it also cycles quite a lot it seems to continually come on to heat the buffer tank which in turn means the flow to rads is always around 5* hotter than they should be which in turn means the house is hotter than the required room temperature. The heat pump seems to always run at higher speed/ rpm instead of low and slow it runs for a shorter time maybe 30 mins max then switch off. Then after maybe 20 mins comes back on and repeats. Also when the system heats the DHW after a shower or to top up the tank heat it runs flat out too. Also in the house a throbbing / vibration sound can be heard through the send and return pipes under the floor upstairs
we are also experiencing that the heat pump is becoming louder has a high pitched noise and also a low rumbling when it works hard.
We are currently waiting for the contractor to come back and have a look at the system to see what they think but to be honest its been a catalogue of disasters from day one with them and very frustrating.
Where we at now is I’m thinking the 4 port buffer tank is one of the main culprits for the system cycling as it seems to demand alot of heat / topping up heat when the system does require any and the rads are always hotter than they need to be.
would converting the 4 port buffer to a 2 port volumiser help or removing the buffer completely their argument is is the system needs 51l of water volume for the defrost cycle ?
we have a small 2 bedroom semi house.
Also would moving the room sensor to a different position away from the TV help its right next to our 65” oled. As it reads the temp there but the rest of the house can be alot cooler.
I’ll attach a pic of system in loft
We have previously had CTC out to have a look they found the trv valves were incorrectly sized (restricting flow rate) the original DHW had faulty coils, the ESBE valve was incorrectly set, 1 pump was incorrectly set and the control unit settings were incorrectly set. But since then our housing association engineers and contractors have been out maybe 20 times trying to rectify the issues including replacing faulty ESBE valve, they even fitted a 3rd party thermostat which controlled the system like gas central heating which continuously switched the system on/off - its been removed and now back on the CTC controller.
CTC technical support seem to only speak to engineers now and not end users which is frustrating I’d like to have a chat with them about the system or get them to come out and check everything over again since all the visits by housing association engineers etc.
It’s all very frustrating to be honest.
on a positive note my parents have just had a heat geek install of a Vaillant system with no buffer which is working great and very economical- which kinda makes us more frustrated as we can see what a well designed and installed system can be.
The contractor is coming next week so some advice would be greatly appreciated I’d like to be able to ask them the right questions and see if we can get system sorted.
Thank you
Richie
@retrorichretrorich
Sorry to hear you are having problems, I am sure you will get a few suggestions from those on the forum, what may prove more difficult is getting the installer to take any on board! Here are some starters:
The cycling may indicate that the heat pump is oversized. 10kW for a 'small 2 bed semi' is simply not plausible unless the insulation is exceptionally poor. Was a proper heat loss calculation done and do you have it? TBH even if it was done, with it being 4 years ago, there is a high probability it would have been overestimated as that was very common back then. At a guess your loss is 5kW or less and a 5-6kW heat pump will perform much better, but until we have some figures that is only a guess
In addition the buffer should probably re-plumbed as a 2 port volumiser in the flow only which retains the water they say they need for the defrost cycle (so their reason for not doing it is invalidated). However whilst you have a massively oversized heat pump you may find that there is insufficient flow to keep the pump happy.
Room sensors, if they are used, should be somewhere representative. Thats kinda obvious
Has weather compensation been set up properly and radiators balanced?
PS, the mention of TRVs has me thinking, has this been set up to run like a boiler with fixed flow temperature and control by the TRVs. If so thats all wrong and would account for both high running costs and the 'need' for a buffer.
Most or all of the TRVs need to be set above the desired temperature, or better still the heads removed. The room temperature sensor then needs to be set several degrees above the desired temperature, and then the weather compensation curve adjusted (slowly, over a period of several days )until the house is at the correct temperature, balancing the radiators if necessary. If this procedure, or something close, has not been carried out you will have higher bills than necessary and if all rads have operational TRVs you will get cycling and do need a buffer, which will further compromise performance.
Perhaps you could clarify how the system is run?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
thanks for reply
according to heat geek website our heatloss is estimated at 4.05kw but it’s probably around 5kw we have had a new roof, loft insulation and wall cavity all done recently too. I was wondering if the heat pump could be oversized as the heating demand / rad temp always runs around 5 degrees hotter than the controller asks for.
No the weather comp hasn’t been professionally set and we don’t know the flow temp really, the contractor said the system was designed for 55 degrees yet CTC set it at 43 and the weather comp at 45 - we’re still overheating the livingroom seems to sit at 22.5 degrees no matter how the flow temp etc is set.
The contractor did do a heatloss survey (twice) but they only measured the rooms that was all.
The rads were balanced by the contractor after install.
we have all TRV’s fully open except our bedroom which is on 3.5
I will contact the head guy at our housing association if we get no joy next week.