Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @trebor12345@jamespa Can I check something that I done some weeks ago.
My underfloor manifold is set via the 12 flow gauges to a total of 20 l/m. In the UI of the indoor unit I have reduced the primary pump from 28.5 l/m to 24.3 l/m.
Why did I do this. I was seeing a lot of mixing in the buffer tank. Reducing the primary pump flow rate to 24.3 l/m reduced the amount of mixing. Therefore the return temperature to the heat exchanger is reduced slightly (approx 0.5C). Hope this makes sence.
Yes this makes sense. Ideally you match flow either side of the buffer, at which point it is pointless (but that is anyway the case). Since a perfect match isn't possible its better to have slightly more flow in the primary than in the secondary. This should force the cold water to the bottom of the tank thus (hopefully) reducing the flow temperature loss across the buffer to near zero.
Posted by: @trebor12345Nothing really new, except that these Thermo Off periods are way tooooo long at 1hr 20 mins and 2hrs 20 mins.
Way too long based on what criterion. From what I recall from your earlier post the house wouldn't cool much in this time. So why does it matter?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaWay too long based on what criterion. From what I recall from your earlier post the house wouldn't cool much in this time. So why does it matter?
You always challenge my thinking! I don't specifically know why I think it's too long. My only thought is do other systems/users have that long time.
Yesterday it did take some time to get heat into building, the off's didn't help.
It was 0C over night, so when I turned the heating off at 11pm it was 22C, this morning it had dropped to 20.5C in the main living area (20sqm of glass), so a little cool for us.
2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3
Posted by: @trebor12345You always challenge my thinking! I don't specifically know why I think it's too long. My only thought is do other systems/users have that long time.
Its not so much challenging as seeking to understand. Your house cools very slowly so provided that the right amount of energy is put in over several hours (which, if the WC curve is correctly adjusted it should), you wont notice it. It is quite a long off time but that said my heat pump will do that in one of its modes. My house cools quicker than yours so I do notice it, and therefore dont operate in that mode preferring pure weather compensation instead.
I am reasonably sure that the key to getting this to work is 24x7 operation on WC, with no human intervention other than, not more than once a day and always in the same direction, adjusting the WC settings. Once thats set up then the various behavioural features of the heat pump and your house can be observed and optimised or adapted if necessary. Until it is set up you are operating with a (largely human based) control system which is inherently unstable because of the delayed response of your house and the fact that the control system stops working overnight, and is therefore impossible to diagnose.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I find having my thinking challenged is always a good thing 🙂
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyI find having my thinking challenged is always a good thing 🙂
I’m always pleasantly surprised when I find out I’ve been thinking in the first place. 😎
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok ‘Sometimes, I sits and thinks, other times, I just sits’. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles thinking is existing, or did I miss some thinking here?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
Posted by: @toodles@majordennisbloodnok ‘Sometimes, I sits and thinks, other times, I just sits’. Toodles.
"I think therefore I am" - René Descartes
"To be is to do" - Socrates
"To do is to be" - Jean-Paul Sartre
"Do be do be do" - Frank Sinatra
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok Tibby or not Tibby - anyone seen my cat?
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @jamespaYes this makes sense. Ideally you match flow either side of the buffer, at which point it is pointless (but that is anyway the case). Since a perfect match isn't possible its better to have slightly more flow in the primary than in the secondary. This should force the cold water to the bottom of the tank thus (hopefully) reducing the flow temperature loss across the buffer to near zero.
JamesPa. Thats one thing that I do have right. Cross that one off the list.
2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3
JamesPa Below is the plot of yesterdays run (30 Nov). Surprise NO THERMO OFFS. Ran for 10.5 hours. Im afraid it's a fluke!!!
I have always expressed the view that the HP is oversized, as you have found the Night/ECO setting, I turned it down to 50%. This is the result.
It's not a sustainable way to run the heating.
Does it tell us anything else?
I am looking at setting up the WC.
2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3
- 27 Forums
- 2,800 Topics
- 66.2 K Posts
- 2,703 Online
- 7,206 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
At this point, whenever someone mentions our heat pump,...
By Mars , 3 minutes ago
-
RE: Say hello and introduce yourself
@e-a-west as the good Major said, welcome to the forums...
By Mars , 24 minutes ago
-
RE: New Build 3 Phase or 1Phase
We are on three phase power because it's an enormous li...
By EtchedPixels , 38 minutes ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Yes I actually have a copy of a tool that whenever a ce...
By EtchedPixels , 9 hours ago
-
RE: How will removing the standing charge on gas bills benefit heat pumps?
The shoulder months are very difficult to judge COP on ...
By scrchngwsl , 11 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Hi, To resolve this, please tap on the A...
By Indevolt Tech , 17 hours ago
-
RE: Double or Triple Glazed Windows?
Posted by: @singlespeed With 9 years repairing windo...
By Rob of York , 1 day ago
-
@transparent we’re still running a secure version of PH...
By Mars , 2 days ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
Much longer than that here. The heating isn't even on. ...
By bobflux , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Obviously the weather is changeable but there's a defin...
By Singlespeed , 2 days ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@rob-of-york I must admit that when we had a Daikin hea...
By Toodles , 2 days ago
-
RE: Forum updates, announcements & issues
Get the Renewable Heating Hub heads-up on WhatsApp. I...
By Mars , 2 days ago
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
@editor I pointed out to the one of the Fuse execs that...
By dansus , 2 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews As well as loft insulation, there are othe...
By Rob of York , 2 days ago