@jamespa Here's an update to my previous post. Mitsubishi engaged a subcontractor to investigate the poor performance of my heat pump. He concluded that it was defective and that it should be replaced. The replacement was installed by another Mitsubishi subcontractor on 15 December. There is a very significant improvement in performance. However, it is still nowhere near meeting its specification. Initial indications are a COP of 3 at 9C OAT with a flow temperature of 35C and a flow rate of 19l/min. Mitsubishi quote a COP of 5.1 at 7C OAT with a flow temperature of 35C. Still a long way off meeting their specification.
Posted by: @ecosteThere is a very significant improvement in performance. However, it is still nowhere near meeting its specification. Initial indications are a COP of 3 at 9C OAT with a flow temperature of 35C and a flow rate of 19l/min. Mitsubishi quote a COP of 5.1 at 7C OAT with a flow temperature of 35C. Still a long way off meeting their specification.
Improvement is good. Lets explore where we are now. You should definitely be getting better than 3 at 9/35 (Can you confirm 35 measured at and by the heat pump, ditto COP, or are they independent measurements if so where and how?). That said mine at least seems to take a while to settle down. Is it cycling? If so with what on and off times.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @ecoste@jamespa Here's an update to my previous post. Mitsubishi engaged a subcontractor to investigate the poor performance of my heat pump. He concluded that it was defective and that it should be replaced. The replacement was installed by another Mitsubishi subcontractor on 15 December. There is a very significant improvement in performance. However, it is still nowhere near meeting its specification. Initial indications are a COP of 3 at 9C OAT with a flow temperature of 35C and a flow rate of 19l/min. Mitsubishi quote a COP of 5.1 at 7C OAT with a flow temperature of 35C. Still a long way off meeting their specification.
I've shared this table in one of my posts recently, as I have the same unit as you, but the 5.1 COP you refer to is only one number quoted within their table, and is the highest figure quoted within these, under the "Partload2" element of the testing, when the capacity is restricted to 5.8kW. The COP figures range from 3.67 to 5.10 at those temperatures within the table and these are from tests carried out in laboratory conditions, so about as 'real-life' as the MPG figures quoted for vehicle fuel efficiency.
This isn't to say that there's no room for improvement, as I've been investigating the COP of my own system and am in the process of trying various means to tweak any further COP efficiencies from it. The closest 'real-life' reference point I can provide at present is from 15th December, where my system had a reported heating COP of 3.42 on a day with average OAT of 9.2°C and an average flow rate of 33.88°C when running under weather compensation that day (figures provided via the Mel Pump app). These also fall short of any of the reported figures in the table, but these are being run on a retrofit installation, with 'real-life' performance inhibitors having an influence on what the true maximum is. I suspect there may be further tweaks available that will have a positive impact, but my gut feel for now is that 3.8 is likely a realistic maximum for my installation at those temperatures.
I would be inclined to disregard the 5.1 COP figure as being anything close to realistic. I found the table to be really helpful as a means to re-base my expectations in terms of questioning "what good looks like" for my own specific circumstances.
Good to hear that the faulty unit has been replaced.
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
@jamespa No cycling, flow temp varies by less than 2 degrees, return is very stable. Today it is running at 38C varying by less 2C, since water heating finished at about 5.00 this morning. So about 12 hours continuous running with OAT of 8C. It is providing about 3.5kW of heat from 1.3kW of electrical energy, COP of 2.7. Temperature measurements are close to the cylinder in the loft, about 20m from the heat pump. They are taken from the Mitsubishi controller, but are integer numbers, i.e. no decimal places so not great granularity. the flow rate is also taken from the Mitsubishi controller, still integer values. Electricity is taken from the Powervault App, allowing 300W for house usage, this is a generous figure based on observations over the last 2 years.
As an addendum to what @jamespa said, can you also let us know what the deltaT is as well, and whether or not there’s any defrosting going on (unlikely at that kind of OAT, but worth asking the question).
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Oh, and @ecoste, I don’t suppose by any stretch that you’re running Home Assistant, are you?
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @ecoste@jamespa No cycling, flow temp varies by less than 2 degrees, return is very stable. Today it is running at 38C varying by less 2C, since water heating finished at about 5.00 this morning. So about 12 hours continuous running with OAT of 8C. It is providing about 3.5kW of heat from 1.3kW of electrical energy, COP of 2.7. Temperature measurements are close to the cylinder in the loft, about 20m from the heat pump. They are taken from the Mitsubishi controller, but are integer numbers, i.e. no decimal places so not great granularity. the flow rate is also taken from the Mitsubishi controller, still integer values. Electricity is taken from the Powervault App, allowing 300W for house usage, this is a generous figure based on observations over the last 2 years.
OK 12 hours stable running should be enough to get a good reading.
Can you be more precise about where the flow and return temperature sensors which are being used to calculate COP are? Is there a buffer tank/LLH between them and the heat pump? What are the actual figures, because 1C error (integers only) can make quite a difference if its running at a DT of (eg) 2! Also temperature sensors are notoriously inaccurate, have you swapped them round/are they well attached to the pipes and insulated on the outside and/or provided with thermally conductive paste. Is it glycol or water in the system,
If its delivering 3.5kW at 19l/min means a DT of 2.7 (assuming pure water). Small errors in temp measurements can make a big difference to calculated COP/power.
Also according to the datasheet whats the expected COP under min load (3.5kW is near to min load)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @ecoste@jamespa No cycling, flow temp varies by less than 2 degrees, return is very stable. Today it is running at 38C varying by less 2C, since water heating finished at about 5.00 this morning. So about 12 hours continuous running with OAT of 8C. It is providing about 3.5kW of heat from 1.3kW of electrical energy, COP of 2.7. Temperature measurements are close to the cylinder in the loft, about 20m from the heat pump. They are taken from the Mitsubishi controller, but are integer numbers, i.e. no decimal places so not great granularity. the flow rate is also taken from the Mitsubishi controller, still integer values. Electricity is taken from the Powervault App, allowing 300W for house usage, this is a generous figure based on observations over the last 2 years.
My observations on this are less than 24 hours old, but the system flow rate reporting did something unexpected yesterday as part of this experimentation.
The system has consistently reported a delta T of 2-2.5°C, which a bit of background reading suggested was a bit lower than ideal. In an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact. The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected. However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min. Logically, this doesn't make sense in the context of the delta T having increased, so I'm currently unsure how accurate the Ecodan flow reporting data is. Regardless of what the system is doing it's consistently showing either 24-25l/min when running or zero when idle, with nothing much between the two at any time.
It's brand new data to me, so I can't conclude too much from it, but I'd expect to have seen both numbers change, not just one of them.
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
Posted by: @sheriff-fatmanIn an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact. The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected. However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min.
Have you got an LLH or buffer? If so which pump speed did you reduce and which flow rate are you measuring?
At moderate OAT expect deltaT to fall unless the heat pump modulates the water pump to maintain fixed deltaT. Some do, some dont, I dont know which camp Mitsubishi falls into
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @sheriff-fatmanIn an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact. The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected. However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min.
Have you got an LLH or buffer? If so which pump speed did you reduce and which flow rate are you measuring?
At moderate OAT expect deltaT to fall unless the heat pump modulates the water pump to maintain fixed deltaT. Some do, some dont, I dont know which camp Mitsubishi falls into
As far as I'm aware from discussions with the installation team, just a volumiser on the system within the pipework in the loft. No buffer or LLH. I've looked up there previously, out of intrigue, but literally have no idea what I was looking at in terms of deciphering the configuration prior to it feeding into the cylinder cupboard on the floor below.
The controls to amend the pump speed are within the installer settings, and there's a separate option to amend DHW and Heating pump speeds. I changed both to 3 for the purposes of the experiment. From a reporting perspective, the system shows "Pump 1" and "Pump 2" as active, but only Pump 1 has a visible speed setting. I suspect @majordennisbloodnok probably has better insight than me into what these figures are recording, based on his own analysis of the data provided by the Ecodan system.
Edit: Not trying to hijack @Ecoste's thread with discussion of my own system, but just thought that the observation of flow rate data was relevant to his own diagnosis.
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
Posted by: @jamespaPosted by: @sheriff-fatmanIn an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact. The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected. However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min.
Have you got an LLH or buffer? If so which pump speed did you reduce and which flow rate are you measuring?
At moderate OAT expect deltaT to fall unless the heat pump modulates the water pump to maintain fixed deltaT. Some do, some dont, I dont know which camp Mitsubishi falls into
It's generation dependent, the latest FTC7 (touchscreen) have the ability to modulate PWM based on OAT.
Mine is the FTC7, for info, if that sheds any light on things.
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 283 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 39 minutes ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
To answer this properly you need a heat loss calculatio...
By JamesPa , 42 minutes ago
-
RE: Running from backup generaor in powercut?
@batpred In our case, 3 times each day when the Octopus...
By Toodles , 1 hour ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Hi @sheriff-fatman Cycling at 5C and below is usuall...
By RobS , 1 hour ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
The diagram describes what happens inside the Solis. Al...
By Batpred , 3 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Here's the latest Fogstar ready built pack....
By Bash , 3 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick yes, even though the current system is ru...
By Tim441 , 3 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Solis confirmed that the S6 works with a single battery...
By Batpred , 4 hours ago
-
RE: Who has a V2G EV installation
I am wondering if in any V2X, would the car battery eve...
By Batpred , 4 hours ago
-
RE: Setback savings - fact or fiction?
Yes, by calculating it manually from the minute data, w...
By cathodeRay , 6 hours ago
-
Fan unit Making terrible noise HELP!!
One of a pair of fan units on an Earth Save Classic II ...
By GutoFfowc , 6 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
OK. I think your system, which seems well designed, is...
By JamesPa , 8 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 21 hours ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 1 day ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 1 day ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 1 day ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 2 days ago