Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Mitsubishi Ecodan R290 10kW performance

65 Posts
8 Users
6 Reactions
17.4 K Views
(@ecoste)
Eminent Member Member
Joined: 1 year ago
Posts: 41
Your energy: 0 kWh
Topic starter  

@jamespa Here's an update to my previous post. Mitsubishi engaged a subcontractor to investigate the poor performance of my heat pump. He concluded that it was defective and that it should be replaced. The replacement was installed by another Mitsubishi subcontractor on 15 December. There is a very significant improvement in performance. However, it is still nowhere near meeting its specification. Initial indications are a COP of 3 at 9C OAT with a flow temperature of 35C and a flow rate of 19l/min. Mitsubishi quote a COP of 5.1 at 7C OAT with a flow temperature of 35C. Still a long way off meeting their specification.



   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5744
Your energy: 83 kWh
 

Posted by: @ecoste
↑

There is a very significant improvement in performance. However, it is still nowhere near meeting its specification. Initial indications are a COP of 3 at 9C OAT with a flow temperature of 35C and a flow rate of 19l/min. Mitsubishi quote a COP of 5.1 at 7C OAT with a flow temperature of 35C. Still a long way off meeting their specification.

Improvement is good.  Lets explore where we are now.   You should definitely be getting better than 3 at 9/35  (Can you confirm 35 measured at and by the heat pump, ditto COP, or are they independent measurements if so where and how?).  That said mine at least seems to take a while to settle down.      Is it cycling?  If so with what on and off times.


This post was modified 11 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@sheriff-fatman)
Reputable Member Member
Joined: 2 years ago
Posts: 224
Your energy: 0 kWh
 

Posted by: @ecoste
↑

@jamespa Here's an update to my previous post. Mitsubishi engaged a subcontractor to investigate the poor performance of my heat pump. He concluded that it was defective and that it should be replaced. The replacement was installed by another Mitsubishi subcontractor on 15 December. There is a very significant improvement in performance. However, it is still nowhere near meeting its specification. Initial indications are a COP of 3 at 9C OAT with a flow temperature of 35C and a flow rate of 19l/min. Mitsubishi quote a COP of 5.1 at 7C OAT with a flow temperature of 35C. Still a long way off meeting their specification.

I've shared this table in one of my posts recently, as I have the same unit as you, but the 5.1 COP you refer to is only one number quoted within their table, and is the highest figure quoted within these, under the "Partload2" element of the testing, when the capacity is restricted to 5.8kW.  The COP figures range from 3.67 to 5.10 at those temperatures within the table and these are from tests carried out in laboratory conditions, so about as 'real-life' as the MPG figures quoted for vehicle fuel efficiency.

Screenshot 2025 12 14 200658

This isn't to say that there's no room for improvement, as I've been investigating the COP of my own system and am in the process of trying various means to tweak any further COP efficiencies from it.  The closest 'real-life' reference point I can provide at present is from 15th December, where my system had a reported heating COP of 3.42 on a day with average OAT of 9.2°C and an average flow rate of 33.88°C when running under weather compensation that day (figures provided via the Mel Pump app).  These also fall short of any of the reported figures in the table, but these are being run on a retrofit installation, with 'real-life' performance inhibitors having an influence on what the true maximum is.  I suspect there may be further tweaks available that will have a positive impact, but my gut feel for now is that 3.8 is likely a realistic maximum for my installation at those temperatures.

I would be inclined to disregard the 5.1 COP figure as being anything close to realistic.  I found the table to be really helpful as a means to re-base my expectations in terms of questioning "what good looks like" for my own specific circumstances.

Good to hear that the faulty unit has been replaced.

 


This post was modified 11 months ago by Sheriff Fatman

130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit


   
ReplyQuote
(@ecoste)
Eminent Member Member
Joined: 1 year ago
Posts: 41
Your energy: 0 kWh
Topic starter  

@jamespa No cycling, flow temp varies by less than 2 degrees, return is very stable. Today it is running at 38C varying by less 2C, since water heating finished at about 5.00 this morning. So about 12 hours continuous running with OAT of 8C. It is providing about 3.5kW of heat from 1.3kW of electrical energy, COP of 2.7. Temperature measurements are close to the cylinder in the loft, about 20m from the heat pump. They are taken from the Mitsubishi controller, but are integer numbers, i.e. no decimal places so not great granularity. the flow rate is also taken from the Mitsubishi controller, still integer values. Electricity is taken from the Powervault App, allowing 300W for house usage, this is a generous figure based on observations over the last 2 years.



   
ReplyQuote

Majordennisbloodnok
(@majordennisbloodnok)
Mitsubishi Electric
Famed Member Moderator
Joined: 5 years ago
Posts: 2264
Your energy: 43 kWh
 

As an addendum to what @jamespa said, can you also let us know what the deltaT is as well, and whether or not there’s any defrosting going on (unlikely at that kind of OAT, but worth asking the question).


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Home Assistant to make it all play nicely together
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Mitsubishi Electric
Famed Member Moderator
Joined: 5 years ago
Posts: 2264
Your energy: 43 kWh
 

Oh, and @ecoste, I don’t suppose by any stretch that you’re running Home Assistant, are you?


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Home Assistant to make it all play nicely together
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5744
Your energy: 83 kWh
 

Posted by: @ecoste
↑

@jamespa No cycling, flow temp varies by less than 2 degrees, return is very stable. Today it is running at 38C varying by less 2C, since water heating finished at about 5.00 this morning. So about 12 hours continuous running with OAT of 8C. It is providing about 3.5kW of heat from 1.3kW of electrical energy, COP of 2.7. Temperature measurements are close to the cylinder in the loft, about 20m from the heat pump. They are taken from the Mitsubishi controller, but are integer numbers, i.e. no decimal places so not great granularity. the flow rate is also taken from the Mitsubishi controller, still integer values. Electricity is taken from the Powervault App, allowing 300W for house usage, this is a generous figure based on observations over the last 2 years.

OK 12 hours stable running should be enough to get a good reading.

Can you be more precise about where the flow and return temperature sensors which are being used to calculate COP are?  Is there a buffer tank/LLH between them and the heat pump?  What are the actual figures, because 1C error (integers only) can make quite a difference if its running at a DT of (eg) 2!  Also temperature sensors are notoriously inaccurate, have you swapped them round/are they well attached to the pipes and insulated on the outside and/or provided with thermally conductive paste.   Is it glycol or water in the system,

If its delivering 3.5kW at 19l/min means a DT of 2.7 (assuming pure water).  Small errors in temp measurements can make a big difference to calculated COP/power.

Also according to the datasheet whats the expected COP under min load (3.5kW is near to min load)


This post was modified 11 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@sheriff-fatman)
Reputable Member Member
Joined: 2 years ago
Posts: 224
Your energy: 0 kWh
 

Posted by: @ecoste
↑

@jamespa No cycling, flow temp varies by less than 2 degrees, return is very stable. Today it is running at 38C varying by less 2C, since water heating finished at about 5.00 this morning. So about 12 hours continuous running with OAT of 8C. It is providing about 3.5kW of heat from 1.3kW of electrical energy, COP of 2.7. Temperature measurements are close to the cylinder in the loft, about 20m from the heat pump. They are taken from the Mitsubishi controller, but are integer numbers, i.e. no decimal places so not great granularity. the flow rate is also taken from the Mitsubishi controller, still integer values. Electricity is taken from the Powervault App, allowing 300W for house usage, this is a generous figure based on observations over the last 2 years.

My observations on this are less than 24 hours old, but the system flow rate reporting did something unexpected yesterday as part of this experimentation.

The system has consistently reported a delta T of 2-2.5°C, which a bit of background reading suggested was a bit lower than ideal.  In an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact.  The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected.  However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min.  Logically, this doesn't make sense in the context of the delta T having increased, so I'm currently unsure how accurate the Ecodan flow reporting data is.  Regardless of what the system is doing it's consistently showing either 24-25l/min when running or zero when idle, with nothing much between the two at any time.

It's brand new data to me, so I can't conclude too much from it, but I'd expect to have seen both numbers change, not just one of them.

 


This post was modified 11 months ago by Sheriff Fatman

130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit


   
ReplyQuote

JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5744
Your energy: 83 kWh
 

Posted by: @sheriff-fatman
↑

In an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact.  The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected.  However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min.

Have you got an LLH or buffer?  If so which pump speed did you reduce and which flow rate are you measuring?

At moderate OAT expect deltaT to fall unless the heat pump modulates the water pump to maintain fixed deltaT.  Some do, some dont, I dont know which camp Mitsubishi falls into


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@sheriff-fatman)
Reputable Member Member
Joined: 2 years ago
Posts: 224
Your energy: 0 kWh
 

Posted by: @jamespa
↑

Posted by: @sheriff-fatman
↑

In an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact.  The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected.  However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min.

Have you got an LLH or buffer?  If so which pump speed did you reduce and which flow rate are you measuring?

At moderate OAT expect deltaT to fall unless the heat pump modulates the water pump to maintain fixed deltaT.  Some do, some dont, I dont know which camp Mitsubishi falls into

As far as I'm aware from discussions with the installation team, just a volumiser on the system within the pipework in the loft.  No buffer or LLH.  I've looked up there previously, out of intrigue, but literally have no idea what I was looking at in terms of deciphering the configuration prior to it feeding into the cylinder cupboard on the floor below.

The controls to amend the pump speed are within the installer settings, and there's a separate option to amend DHW and Heating pump speeds.  I changed both to 3 for the purposes of the experiment.  From a reporting perspective, the system shows "Pump 1" and "Pump 2" as active, but only Pump 1 has a visible speed setting.  I suspect @majordennisbloodnok probably has better insight than me into what these figures are recording, based on his own analysis of the data provided by the Ecodan system.

Edit: Not trying to hijack @Ecoste's thread with discussion of my own system, but just thought that the observation of flow rate data was relevant to his own diagnosis.


This post was modified 11 months ago by Sheriff Fatman

130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit


   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 1 year ago
Posts: 129
Your energy: 2 kWh
 

Posted by: @jamespa
↑

Posted by: @sheriff-fatman
↑

In an attempt to see what would happen I reduced the pump speed setting, which was set at the maximum of 5, to run at a pump speed of 3, to see if that had any impact.  The delta T subsequent to this does look to have increased to 3.5-4°C when the heating is running, which is the output that I had expected.  However, the flow rate reporting hasn't noticeably changed from the pump speed being reduced, and continues to show 24-25 l/min.

Have you got an LLH or buffer?  If so which pump speed did you reduce and which flow rate are you measuring?

At moderate OAT expect deltaT to fall unless the heat pump modulates the water pump to maintain fixed deltaT.  Some do, some dont, I dont know which camp Mitsubishi falls into

 

It's generation dependent, the latest FTC7 (touchscreen) have the ability to modulate PWM based on OAT.

 



   
ReplyQuote
(@sheriff-fatman)
Reputable Member Member
Joined: 2 years ago
Posts: 224
Your energy: 0 kWh
 

Mine is the FTC7, for info, if that sheds any light on things.


130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)