Ecodan unable to hit legionella target temp - what's the consensus?
@majordennisbloodnok ah! Yes, I did see this video. As per my reply to @rhh2348, we don't have that controller unfortunately. We have an older one, which has no legionella settings available.. If we had the one in the video, I think we'd be sorted!
mentions dipswitches to control legionella - one of the options is every 15 times DHW?
@rhh2348 ...maybe this option is what you want?
Alternatively the immersion heater may be controlled separately. If direct control is not required then DIP switch SW1- 4 should be turned OFF and the immersion can then be controlled via its own weekly timer as with FTC1.
UPDATE: Thanks everyone who commened with suggestions here - all really appreciated. For those interested, the issue was with the immersion thermostat itself, as some people suggested. The thermostat had been calibrated (for reasons unknown) to max out at 60 degrees, which meant it was physically impossible for the water temp to go beyond that. I broke the little plastic restricter off it, turned it an extra quarter turn, and the tank then succesfully heated to 65 degrees, satisfied the legionella cycle requirement and we're all good now! 🙂
@9jwr9 Hi, yes this is the issue with every (stand alone Ecodan) when mixed with an alternative cylinder, we set them all to 60 Deg C and just make them keep that heat level longer to cover the burn. If you use a Mitsubishi cylinder they do not have a control stat on the element only an overheat and all of the control is done through the contactor. What happens with the stand alone Ecodan and an alternative cylinder is the contactor is still used but has another stat inline as part of the element.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Ecodan with FTC7 - True Weather Compensation
2 hours ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
4 weeks ago
-
Ecodan consuming 100kwh per day in new build!!!
6 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
9 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
9 months ago
- 26 Forums
- 2,391 Topics
- 54.2 K Posts
- 377 Online
- 6,074 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
Both inverters would be limited by the max 16A export t...
By Batpred , 32 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
Of course it is not helpful to frogstar fan club member...
By Batpred , 45 minutes ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 2 hours ago
-
@steelbadger, I’ve pretty much decided now that there’s...
By Majordennisbloodnok , 2 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
That makes plenty of sense. Perhaps more importantly, O...
By Majordennisbloodnok , 3 hours ago
-
RE: Heat pump not reaching flow temperature
That doesn't make much sense as it should alter the flo...
By JamesPa , 5 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@downfield Likewise we are also retired and want a warm...
By Wally , 6 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
It does but it almost all applies to boiler systems and...
By JamesPa , 6 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
So theres a problem for starters. This means that the ...
By JamesPa , 7 hours ago
-
Daikin Atherma ASHP Cycling 6 Times an Hour?
I have a Daikin Atherma EDLQ07CAV unit and I've come he...
By John Marshall , 9 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
Shouldn’t your temp sensor be in the middle or lowest s...
By EcoBaker , 23 hours ago
-
RE: Insulating a pitched roof with kingspan, has anyone done it?
Thank you everyone for all of the information, it looks...
By TRBob , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@transparent Yep, they didn’t even mention it. When ...
By Papahuhu , 1 day ago
-
Air source heat pump circuit not operational
Hi - need some advice about one circuit on my heating s...
By Plummersknowe , 1 day ago
-
RE: Setback savings - fact or fiction?
They are lovely, and I feel lucky to live in one, but t...
By cathodeRay , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Worth adding that, for this tariff, the Octopus app has...
By Batpred , 1 day ago
-
RE: APP for remote Daikin ASHP Operation
Thanks, @newhouse87. Understood. I was only asking on...
By Majordennisbloodnok , 1 day ago
-
@mike-patrick A propos, I think my heat pump generates ...
By dr_dongle , 1 day ago
-
RE: Mitsu Zubadan flow temperature issue
Update: The flow temperature has now stabilized at 60C ...
By bontwoody , 1 day ago