Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
Hi,
I think I’m having some issues with my Ecodan ashp and the pumps, details are as follows:
11.2kw Outdoor Unit (PUZ-WM112VAA)
300L Indoor Unit (EHPT-UKHDW)
Flow Temp Controller (PAC-IF073B-E)
New Build Property
UFH downstairs
Rads Upstairs
Running on Temp Comp Curve (tcc)
I’ve attached some photos showing the current set up.
So the issue (I think) I’m currently having is that, when the compressor comes on the circulation pumps switch on - Happy days, but when the compressor shuts down so do the circulation pumps with a flow rate of 0.
The flow rate rises but then drops when the compressor shuts down, which then the return flow is higher than the flow rate, which slowly drops, only then does the compressor switch back on to increase the flow temp.
Am I correct in thinking that the most efficient way to run the tcc is for the circulation pumps to continuously run including the compressor but just at a low level?
Also I’m worried that because the circulation pumps down seem to be running that the t1+t2 sensors (they are on the correct way)
are just detecting stagnant glycol, hence the slow drop in return until it then switches back on?
Also does anyone know the optimum flow rates for my ashp?
Any help/guidance would be appreciated.
Thanks
I think this is one for Mr. Ecodan himself, @ashp-bobba
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained – use AUDIO50 at checkout for 50% off.
@editor Fingers crossed 🤞
I've tried to turn down the pump speed since they were maxed out.
The thing i really cant understand:
1. Why do the circulation pumps turn off soon after the compressor stops?
2. Why does a freeze stat keep occurring?
The flow temps are set to:
12°c = 20°c
-2°c = 32°c
I appreciate these are low but any higher and the house gets to warm, any higher it means having to use the room thermostats to knock off circuits (wasting energy), at the moment they are calling for 23°c but the rooms are balanced to 20~21°c.
This is a screenshot from this afternoon:
Thanks for any help 🙏
@patch321 did this just start recently? Clearly a control issue, and maybe @pirate-rich might have some thoughts.
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained – use AUDIO50 at checkout for 50% off.
@patch321 HI, I will try to jump on later tonight as I can see this will need some thought, but for now can you tell me which pumps stop, we need to label them as it looks like you have 7 pumps so I assume you have a zoning setup, most heat pumps prefer simple layout less zoning.
Try to work out which ones stop and which do not, in heating the left 2 Mitsi pumps should be running and the right not as this is the plate HX pump for hot water.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @ashp-bobbawe need to label them as it looks like you have 7 pumps
OMG, I never even spotted that. Why are there so many pumps? Yikes!
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained – use AUDIO50 at checkout for 50% off.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
@ashp-bobba hey Bobba+Mars, thanks for jumping on the thread.
Indeed, the two pumps which switch off are:
Heat Pump Circulating pump + Heat Zone 1 Circulating pump
That's was my understanding also, seems a lot of pumps, my understanding was you only needed extra pumps for >2 zones.
I think zone 1 is the ufh and zone 2 is the upstairs rads.
From what I can tell the white vertical pump is on the flow for zone 2.
Green vertical pump is for hot water in the upstairs bathroom (hot water recirculation system).
1. Why do the circulation pumps turn off soon after the compressor stops?
In compensation curve or fixed flow, the result of a flow temperature overshooting the flow setpoint (i.e. not enough heat dissipation or not modulating low enough) results in the ecodan operation mode becoming Off.
When the operation mode is off, as are the pumps.
When you are in Auto-Adapt, this occurrence will result in an outdoor unit pause. Until the thermo. Diff limit temperature limits are satisfied. Pumps do not stop as the operation mode remains 'heating'
2. Why does a freeze stat keep occurring?
When there is no demand for heat (operation mode is off) and the outdoor temperature is low, then if enabled, freeze stat will circulate water to prevent freezing.
Typically enabled only when Glycol is not present.
@f1p thanks for the post.
interesting, I wonder in that case its modulating down, I think the ashp is massively oversized for the heating demand for our house, I think it looses about 3-4kw but have a 11.2kw ashp.
Seems mad but do you think I need to increase my flow temps on the tcc to give it an “artificial demand” and then limit the room temp with room thermostats? Or is there any other way to prevent the modulating down?
Still non the wiser to why the pumps are laid out like they are though 😩
Here is the current chart:
You are going to have a bit of a fight on your hands I'm afraid if you are oversized and particularly in warm weather.
the Ecodan logic is to ramp up compressor speed to recover a difference between setpoint and actual, its not very quick at reducing it again - in many cases you will overshoot by the time it's ready to settle and then the 'cycle' (often short) begins again
You have one of the options, higher flow temperature
Auto adapt can work better often than fixed or compensation curve
There is another but it's not perfect either and complicated to implement
Posted by: @patch321Hi,
I think I’m having some issues with my Ecodan ashp and the pumps, details are as follows:
11.2kw Outdoor Unit (PUZ-WM112VAA)
300L Indoor Unit (EHPT-UKHDW)
Flow Temp Controller (PAC-IF073B-E)
New Build Property
UFH downstairs
Rads Upstairs
Running on Temp Comp Curve (tcc)
I’ve attached some photos showing the current set up.
So the issue (I think) I’m currently having is that, when the compressor comes on the circulation pumps switch on - Happy days, but when the compressor shuts down so do the circulation pumps with a flow rate of 0.
The flow rate rises but then drops when the compressor shuts down, which then the return flow is higher than the flow rate, which slowly drops, only then does the compressor switch back on to increase the flow temp.Am I correct in thinking that the most efficient way to run the tcc is for the circulation pumps to continuously run including the compressor but just at a low level?
Also I’m worried that because the circulation pumps down seem to be running that the t1+t2 sensors (they are on the correct way)
are just detecting stagnant glycol, hence the slow drop in return until it then switches back on?
Also does anyone know the optimum flow rates for my ashp?
Any help/guidance would be appreciated.
Thanks
Can you tell me if you have an FTC6 or FTC7
If you have muti zone system and the floor is off the 11.2kw system will not inverter effectively down to 3 or 4 rooms to this will cause some short cycling or over shoot, can you tell me if (FTC6 the PLAY Symbol) goes out (FTC7 if the home goes black or stays red) when the pumps stop
Lets find this out 1st.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
-
Issue with Samsung Cascade System
1 day ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
2 weeks ago
-
Surface mount or bury primaries for heat pump installation?
4 weeks ago
-
Design Of Cascade System Replacing Undersized ASHP
4 weeks ago
-
Mitsubishi Ecodan not good enough ?
3 months ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,733 Topics
- 64.2 K Posts
- 1,625 Online
- 7,139 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Questions about A2A for heating as well as cooling
Thank you for that very helpful and thorough response! ...
By donciccio , 6 hours ago
-
RE: Aircon - in listed buildings
@etchedpixels thanks for giving such a full and helpful...
By GrahamF , 21 hours ago
-
RE: Acond heat pump failed after four years - diagnostic quote £940 plus VAT
Another idea if the above don't work - there are compan...
By downfield , 23 hours ago
-
RE: Love veg, hate watering cans
They have their downsides but boreholes are great in th...
By ian33a , 24 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist The service engineer powered down the ex...
By Papahuhu , 1 day ago
-
RE: Issue with Samsung Cascade System
@jamespa It's a funny system, but was out only option l...
By Renewables345 , 1 day ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Thanks, I like the chart, very helpful and this will de...
By baroquebank , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Production resumed to normal once the issue ...
By MK4 , 2 days ago
-
RE: Digest of UK Energy Statistics
That sounds painful. It would be much better to charg...
By Transparent , 3 days ago
-
Hole diameter is small but hole length is also very sma...
By bobflux , 3 days ago
-
RE: Are Wind Turbines Really “Losers”?
We were sailing near a wind farm in the North Sea last ...
By Jeff , 3 days ago
-
@trebor12345 The idea is to ensure that Powerwall knows...
By Toodles , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
'hard limited' could be in 'admin' password protected s...
By JamesPa , 4 days ago