Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
Hi,
I think I’m having some issues with my Ecodan ashp and the pumps, details are as follows:
11.2kw Outdoor Unit (PUZ-WM112VAA)
300L Indoor Unit (EHPT-UKHDW)
Flow Temp Controller (PAC-IF073B-E)
New Build Property
UFH downstairs
Rads Upstairs
Running on Temp Comp Curve (tcc)
I’ve attached some photos showing the current set up.
So the issue (I think) I’m currently having is that, when the compressor comes on the circulation pumps switch on - Happy days, but when the compressor shuts down so do the circulation pumps with a flow rate of 0.
The flow rate rises but then drops when the compressor shuts down, which then the return flow is higher than the flow rate, which slowly drops, only then does the compressor switch back on to increase the flow temp.
Am I correct in thinking that the most efficient way to run the tcc is for the circulation pumps to continuously run including the compressor but just at a low level?
Also I’m worried that because the circulation pumps down seem to be running that the t1+t2 sensors (they are on the correct way)
are just detecting stagnant glycol, hence the slow drop in return until it then switches back on?
Also does anyone know the optimum flow rates for my ashp?
Any help/guidance would be appreciated.
Thanks
I think this is one for Mr. Ecodan himself, @ashp-bobba
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Fingers crossed 🤞
I've tried to turn down the pump speed since they were maxed out.
The thing i really cant understand:
1. Why do the circulation pumps turn off soon after the compressor stops?
2. Why does a freeze stat keep occurring?
The flow temps are set to:
12°c = 20°c
-2°c = 32°c
I appreciate these are low but any higher and the house gets to warm, any higher it means having to use the room thermostats to knock off circuits (wasting energy), at the moment they are calling for 23°c but the rooms are balanced to 20~21°c.
This is a screenshot from this afternoon:
Thanks for any help 🙏
@patch321 did this just start recently? Clearly a control issue, and maybe @pirate-rich might have some thoughts.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@patch321 HI, I will try to jump on later tonight as I can see this will need some thought, but for now can you tell me which pumps stop, we need to label them as it looks like you have 7 pumps so I assume you have a zoning setup, most heat pumps prefer simple layout less zoning.
Try to work out which ones stop and which do not, in heating the left 2 Mitsi pumps should be running and the right not as this is the plate HX pump for hot water.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobbawe need to label them as it looks like you have 7 pumps
OMG, I never even spotted that. Why are there so many pumps? Yikes!
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba hey Bobba+Mars, thanks for jumping on the thread.
Indeed, the two pumps which switch off are:
Heat Pump Circulating pump + Heat Zone 1 Circulating pump
That's was my understanding also, seems a lot of pumps, my understanding was you only needed extra pumps for >2 zones.
I think zone 1 is the ufh and zone 2 is the upstairs rads.
From what I can tell the white vertical pump is on the flow for zone 2.
Green vertical pump is for hot water in the upstairs bathroom (hot water recirculation system).
1. Why do the circulation pumps turn off soon after the compressor stops?
In compensation curve or fixed flow, the result of a flow temperature overshooting the flow setpoint (i.e. not enough heat dissipation or not modulating low enough) results in the ecodan operation mode becoming Off.
When the operation mode is off, as are the pumps.
When you are in Auto-Adapt, this occurrence will result in an outdoor unit pause. Until the thermo. Diff limit temperature limits are satisfied. Pumps do not stop as the operation mode remains 'heating'
2. Why does a freeze stat keep occurring?
When there is no demand for heat (operation mode is off) and the outdoor temperature is low, then if enabled, freeze stat will circulate water to prevent freezing.
Typically enabled only when Glycol is not present.
@f1p thanks for the post.
interesting, I wonder in that case its modulating down, I think the ashp is massively oversized for the heating demand for our house, I think it looses about 3-4kw but have a 11.2kw ashp.
Seems mad but do you think I need to increase my flow temps on the tcc to give it an “artificial demand” and then limit the room temp with room thermostats? Or is there any other way to prevent the modulating down?
Still non the wiser to why the pumps are laid out like they are though 😩
Here is the current chart:
You are going to have a bit of a fight on your hands I'm afraid if you are oversized and particularly in warm weather.
the Ecodan logic is to ramp up compressor speed to recover a difference between setpoint and actual, its not very quick at reducing it again - in many cases you will overshoot by the time it's ready to settle and then the 'cycle' (often short) begins again
You have one of the options, higher flow temperature
Auto adapt can work better often than fixed or compensation curve
There is another but it's not perfect either and complicated to implement
Posted by: @patch321Hi,
I think I’m having some issues with my Ecodan ashp and the pumps, details are as follows:
11.2kw Outdoor Unit (PUZ-WM112VAA)
300L Indoor Unit (EHPT-UKHDW)
Flow Temp Controller (PAC-IF073B-E)
New Build Property
UFH downstairs
Rads Upstairs
Running on Temp Comp Curve (tcc)
I’ve attached some photos showing the current set up.
So the issue (I think) I’m currently having is that, when the compressor comes on the circulation pumps switch on - Happy days, but when the compressor shuts down so do the circulation pumps with a flow rate of 0.
The flow rate rises but then drops when the compressor shuts down, which then the return flow is higher than the flow rate, which slowly drops, only then does the compressor switch back on to increase the flow temp.Am I correct in thinking that the most efficient way to run the tcc is for the circulation pumps to continuously run including the compressor but just at a low level?
Also I’m worried that because the circulation pumps down seem to be running that the t1+t2 sensors (they are on the correct way)
are just detecting stagnant glycol, hence the slow drop in return until it then switches back on?
Also does anyone know the optimum flow rates for my ashp?
Any help/guidance would be appreciated.
Thanks
Can you tell me if you have an FTC6 or FTC7
If you have muti zone system and the floor is off the 11.2kw system will not inverter effectively down to 3 or 4 rooms to this will cause some short cycling or over shoot, can you tell me if (FTC6 the PLAY Symbol) goes out (FTC7 if the home goes black or stays red) when the pumps stop
Lets find this out 1st.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Rodents! A word of warning for heat pump owners
2 weeks ago
-
Ecodan Zone 2 Mitshibishi thermostat Auto Adapt
2 weeks ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
1 month ago
-
Weather compensation- why you should use it
1 month ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,484 Topics
- 57.3 K Posts
- 2,192 Online
- 6,196 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
I get the question and what you are trying to do, I wil...
By JamesPa , 6 hours ago
-
@ch_18 downfield is completely correct but you should i...
By Judith , 6 hours ago
-
RE: Vaillant app under reporting flow temperature
No idea then, it's inconceivable that the app and live ...
By JamesPa , 7 hours ago
-
RE: Setback savings - fact or fiction?
That too is true of course, but sometimes we also need ...
By cathodeRay , 8 hours ago
-
RE: Rate the quality of your heat pump design and installation
Pretty awful had new heat pump dead on arrival followed...
By Keithb , 10 hours ago
-
Importance of choosing right installer
I had issues with my Bosch 2000awf installation from da...
By Keithb , 10 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
@smsm1 Thanks for your interest. At the time that I l...
By DavidAlgarve , 11 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
Dear Mars, Thanks for writing this postI'm trying to g...
By Alex , 12 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
Thanks for the pictures, they tell quite a story but no...
By JamesPa , 12 hours ago
-
@majordennisbloodnok Thanks very much, that's cleared t...
By Boycey , 12 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna I've DM'd you the details. Please click in the...
By Mars , 13 hours ago
-
If you want to find your own activity on the forums, re...
By Mars , 13 hours ago
-
RE: Warranty Repairs- An Un Eddi fying experience!
@bornagain Those staff redundancies were possibly linke...
By Toodles , 17 hours ago
-
RE: Midea ASHP – how to set weather compensation
Happily reporting back after 2+ weeks of operation: com...
By MK4 , 18 hours ago
-
RE: Help needed to adjust weather compensation on Vaillant air source heat pump
The micro climate effect is only going to matter if, as...
By JamesPa , 18 hours ago
-
RE: Tell us about your Solar (PV) setup
@upnorthandpersonal thank you for sharing details of yo...
By Old_Scientist , 19 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@petch I’ve not come across anyone yet that’s used thes...
By Mars , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
Yep- already done that....nothing novel as such but som...
By benson , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils Similar here, though it has been very mild. I...
By KevH , 2 days ago
-
RE: Home energy storage & battery register
@toodles thankfully we have a range of tariffs to meet ...
By TechnoGeek , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor thanks Mars! I'll contact them.
By kevinmc1970 , 2 days ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@heymikey thanks for the update and sorry to hear that ...
By Mars , 2 days ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
@jamiejones85mespa your comments are spot on with my th...
By AgentGeorge , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Must of knocked a load of crud through when they added ...
By Burtis , 2 days ago
-
@mkz, yes I have other installers... can you please sen...
By Mars , 3 days ago