Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Is the "divide by 2900" rule still valid?

2 Posts
2 Users
0 Reactions
11 Views
(@andrewj)
Reputable Member Member
Joined: 2 years ago
Posts: 237
Topic starter   [#3141]

Brother in law has recently had a survey completed with the heat loss estimated at 9.73kW, a recommended 12kW Arotherm and a flow temp of 50c at -3c for a SCOP of 3.97.  There seems to be some suggestion of requiring a 30% oversize (a new thing recommended within the last 2 months - by whom, Vaillant??) because the units weren't tested with the UKs' high humidity so they struggled on cold days.  Obviously I don't know if that is oversized, I'm always a bit wary of a solution that involves a heat pump > 7kW so I'm trying to sanity check it.  On a separate survey, Octopus ended up recommending a 15kW unit but I don't know what they calculated the heat loss at.  

All the calculations were made for the standard, mental, MCS temps across rooms in the house but he quite rightly wants it to achieve 21c across the house with 22c in the bathrooms. Available space for radiator sizes looks like it is restricted in some rooms.  There may be some issue with microbore piping in some rooms hinting at "maybe need a buffer to achieve flow rate through these rooms which we'll have to determine during further investigation and site survey.  The Vaillant pump tends to offer less head room in which case we would include a buffer."  It's worth mentioning that they have stated that on any installation they would only include a buffer or volumiser where needed and they explained the purposes of both of these - in other words, it doesn't seem that they always bung these in for their customers because...  

From his bill he has an *estimated* 21,056kWh of annual usage of which approximately 2700kWh is hot water production.  I've struggled to get him to work out an actual usage value (perhaps I'm not explaining myself well enough) but it doesn't matter for the purposes of this question so much.  Given then the 21,056 - 2700 = 18,256kWh usage for heating: 18,256 / 2900 =6.295kW, approximately half the determined heat pump size, certainly within the range of a 7kW unit.

It's not clear exactly how he runs his gas central heating system but it would seem to be a couple of hours in the morning and a couple of hours in the evening; in winter it may get put on at additional times as well.

How accurate is the /2900 rule really and how does that reflect a more time slot-based usage vs say a boiler set to run 24/7 (controlled by the thermostat of course)?

 



   
Quote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5307
 

Posted by: @andrewj

Brother in law has recently had a survey completed with the heat loss estimated at 9.73kW, a recommended 12kW Arotherm and a flow temp of 50c at -3c for a SCOP of 3.97.  There seems to be some suggestion of requiring a 30% oversize (a new thing recommended within the last 2 months - by whom, Vaillant??) because the units weren't tested with the UKs' high humidity so they struggled on cold days.  Obviously I don't know if that is oversized, I'm always a bit wary of a solution that involves a heat pump > 7kW so I'm trying to sanity check it.  On a separate survey, Octopus ended up recommending a 15kW unit but I don't know what they calculated the heat loss at.  

There is a thread on openenergymonitor which does suggest that the Vaillant Arotherm plus 7kW in particular doesn't deliver the (typically, depending on FT) 8.5kW it claims during defrost, and is more like its sticker capacity of 7kW, with the 5kW likewise delivering closer to its sticker output during defrost than the higher output stated in the capacity tables.

Dividing by 2900 is based on typical degree days in (I think) the South East of the UK.  If the house is allowed to cool a lot for a long time it will be an underestimate, but if it only cools by a degree or two for a few hours a day then the difference that makes is small.  Also factor in boiler efficiency.  If the boiler is fairly new and run at 55C or less then it might be more than 100% 'efficient', up to 110% in fact, sol the calculation based on 2900 may be an underestimate.  If its old and run at 75C cycling madly most of the time it will be a lot less efficient, so the calculation based on 2900 will be an overestimate.   If all the corrections are in the same direction then they can be worth worrying about, if they arent all in the same direction then less so..

Posted by: @andrewj

The Vaillant pump tends to offer less head room in which case we would include a buffer."

er how does that help?

My total gas usage was 20-22MWh/year when I heated part time at 75C, controlled on thermostat and trvs.  It dropped to just over 18MWh/year when I heated full time at 50C (still controlled on thermostat and TRVs although the TRVs weren't doing much).  The 7kW Vaillant Arotherm plus is just about right for me.  It works fine down to -5 (we dont currently get colder here for any amount of time).  The figures include DHW but we dont use much of that and in summer DHW was heated from solar.

Depending on how your brother in law heats his house he may be a bit more than mine so possibly a bit too marginal for the 7kW unless he is prepared to use a bit of supplementary heating on the coldest days.  The simplest pption to squeeze 7-10% more out is just to heat DHW on the immersion on the coldest days instead of on the heat pump.  That said the Arotherm plus models seem not to lose too much in efficiency if they are oversized, judging by the data I have seen (but I couldn't quantify that statement).

if he has half hourly meter readings plot average daily use against degree days or average OAT and look peaks of usage over 3, 6 and 12 hours like the attached, which is in essence how my heat pump was sized.

Note that the new Arotherm pros have not yet been submitted to the same scrutiny so far as I am aware.

 

Hope that helps.  Without some more data he is definitely taking a fairy high risk going with the 7kW.  The new 12kW pro is, I think, single fan so its less of a bugbear visually to jump from 7 to 12 than it was with the plus range.

Another question worth asking - is there any opportunity to shave a kW off with insulation?  If so I would be tempted to run the numbers and consider that!

 


This post was modified 17 minutes ago by JamesPa
This post was modified 2 minutes ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   