Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Mitsubishi Ecodan Auto Adaption trial to stop cycling.
We have a 11.2 kWh over sized heat pump, ufh downstairs and rads upstairs. We have been running on WC cold end 41⁰ @-4⁰, warm end 30⁰ @7⁰and got the curve pretty spot on but the unit would cycle at oat over 9⁰. House built 2020 well insulated.
Only way to stop cycling was to keep turning the unit off, let it settle and turn back on as oat temps dropped.
Changed over to auto adaption 11 days ago, a bit reticent to do this due to comments of auto adaption not working well with ufh.
Made changes on FTC5 changed the interval to 60mins and thermo diff from +5/-5 to +3/-9 no idea 🤔this was just guess work, but thought I could just play with the numbers.
We have 2 mitsibishi wifi stats.
The unit has settled, I assume this is algorithm learning.
Yesterday it ran smoothly most of the day see images from Mel pump Mel cloud. It ran yesterday from 1:10pm to 9.25 am this morning with one cycle.
I've managed to drop the curve to 39⁰@-2 cold end and 27⁰ @10⁰ warm end, never been able to do this before as it would cycle. It runs at 29⁰ which it could do on WC, unfortunately won't go lower but at least it seems to have stopped cycling.
Rads warm rooms @29⁰ we don't heat up water to heat rads, then cool uhf. We keep upstairs wifi stat in master bedroom which is over unheated garage and we can get this up to 20.5⁰ but mainly 18.5⁰ /19.5⁰, all other bedrooms go over 21.5⁰. downstairs stat is in the hall, we have rewired to just have one stat downstairs this is set to 21.5⁰ but over shoots to 22.5⁰ which is our perfect room temp.
We run ashp 24/7.
It's early days, not been very cold since changeover so will be interested to see how it copes in cold weather. Not sure it's saved money and never been able to read COP but at least it seems to have reduced cycling which was my aim.
The interval you talk of, i think, will be 60min for any thermostat changes to take effect - which might not be exactly what you want.
E.g. you turn the thermostat down from 20 to 18 at night, this means the controller wont actually take action on the 18C until 60min after it happened
Thermo Diff i think has made the big difference here, it allows your Flow Temperature to Overshoot the Flow Setpoint by +3C and then not restart again until it drops until -9C
Usually you would want the +5C as its more likely to overshoot in warmer weather
A little further down in MELPump you will see "Target heating temperature" which is the Flow Setpoint that Mitsi AA has chosen.
Impressive low frequency there though!
- 27 Forums
- 2,819 Topics
- 66.8 K Posts
- 1,520 Online
- 7,232 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
@davec 47kwh for 3 days is very low, compared to what I...
By johnd , 5 minutes ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
The pool heat exchanger looks like one of thes...
By Singlespeed , 10 minutes ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
Actually, good point. Yesterday was sunny for a good c...
By AndrewJ , 17 minutes ago
-
I opted to buy sets of 16 bare LiFePO₄ cells and place ...
By Transparent , 41 minutes ago
-
RE: Why don't people choose heat pumps?
This topic is straying into useful observations about t...
By Transparent , 3 hours ago
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
This opening sentence stopped my reading right at the s...
By QdsdHxJX9PFLfi7 , 4 hours ago
-
RE: Our 10 year old Grant heat pump failed
As I understand it it was working then stopped. More l...
By JamesPa , 4 hours ago
-
@pipcart, Wattson is back... please go to the homepage ...
By Mars , 5 hours ago
-
Do heat pump defrost cycles impair heat pump efficiency (COP values)?
The short answer is no, as far as I can see from data f...
By cathodeRay , 5 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That is a good approach and an excellent result. For co...
By Judith , 23 hours ago
-
RE: Say hello and introduce yourself
Good to see you here, @claytonbrowne, and welcome to th...
By Mars , 1 day ago
-
RE: Issues with Samsung heat pump – high running costs and house dropping to 11C overnight
It looks very much like a radiator balancing i...
By hml1827 , 2 days ago
-
I have, @transparent, but chose to pose the question he...
By Majordennisbloodnok , 2 days ago