Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Homely setup on daikin heat pump
Posted by: @craighinstallers were more than pathetic, I've still got air in my radiators now after bleeding them many times and also I had to sort the external pipe insulation out as there was great big holes by the valves and the joints weren't sealed properly, I don't want the installers anywhere near my house though.
Sounds like my installation…
I found the manual for the Dixell controller only on a retailer website for MKM Building Supplies.
This should have been easier to find from Daikin.
It’s essential that you check the set point on that controller as it controls when your secondary pump kicks in and I found the factory setting way too high at 37degC.
(press the set button)
The effect is that the heat pump starts up by only warming the buffer tank. With no heat being lost to the radiator circuit it overshoots its target flow temperature and shuts down. This happens repeatedly until the buffer tank reaches the set point temperature. Only then does the water start circulating through the radiators and the system have some chance of achieving a steady heat transfer to the house.
I have mine set to 25degC so that I get water flowing in the radiators as soon as possible after the heat pump is starting up. This has effectively eliminated start up cycling.
(press and hold set and adjust with arrows when the display is blinking; press set again to save)
Also, the Madoka is not just a dumb thermostat. It supports modulation and allows you to get the best of the efficiency from LWT control whilst allowing some real world feedback. It can go slightly above or below the weather curve to account for temporary changes to the heat loss e.g. solar gain or someone leaves a door open for too long.
If it wasn’t for DHW and the occasional defrosting, this keeps my pump running permanently in winter and maintains a comfortable temperature.
I hope that helps.
Morning @majordennisbloodnok
Can I ask your take on the smart+ subscription? @toodles has given me a really good insight into the homely system but he's recommended to ask your advice on whether the subscription is worth doing and it maybe pays for itself?
You gave me some great advice a few weeks ago on another subject, you were a bit worried you'd waffled on😴, but your advice were spot on thank you and at a level I could understand clearly.👍
I'm past the point of trying to sort the efficiency manually so getting a homely installed seems a great idea after reading a lot of posts on this website, I've got the hub pack and the d-com units on it's way, I'm not an electrician but certainly capable of having a go at installing it all in a safe manner if pointed in the right direction, as I mentioned to Toodles the installation manuals not the clearest, I'd like to know how to power the d-com unit and can I buy the cabling at somewhere like Screwfix mainly but any advice on the the whole install is greatly appreciated.
Thank you
Regards
Craig
@craigh Hello again, I meant to indicate that @majordennisbloodnok uses automation and that I think, uses the Agile tariff. What I was trying to suggest was the Major may be able to provide a comparison and whether the Agile tariff still works out cheaper for his uses than Cosy might. All these comparisons are very difficult though as every variable complicates any comparison. Times of demand, storage capability, willingness to apply attention to automation or manual faffing etc., is there an EV in the equation and so on. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@craigh, @toodles, sorry for the delay in responding.
Yes I do use Octopus Agile incoming and yes I do automate stuff with Home Assistant. I also have tried Agile outgoing although I’m just on their standard variable Outgoing at the moment.
I can’t comment on whether or not Cosy would be better or worse for us since we have a relatively small battery (6.5 kWh). The really cheap off peak rates for Cosy, Flux and Go tend to be at their most beneficial when you can store enough power to tide you over the relatively long peak price times whereas Agile only tends to have two relatively short peaks - the main one being 4pm-7pm. In addition, none of the other tariffs ever get negative pricing which, whilst rare, can and does happen with Agile.
Our usage patterns are all over the place so the regularity of the other ToU tariffs isn’t ideal for us and Agile combined with rules for exploiting time shifting, opportunistic pricing and saving sessions is a much better fit. However, in order to make Agile work for you, you really do need to get away from set scheduling or manual tinkering and that’s not for everyone.
As for Homely, Havenwise and the like, the main thing they can do over and above ensuring you’re running on weather compensation is to overheat your home at times of cheap energy and throttle back when leccy is expensive. In effect, it’s turning your home into a heat battery and that can certainly increase your savings a bit. However, the tradeoff is that you have to accept wider temperature swings and that’s something my wife and I don’t like.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@djp01 you've done well finding anything out about that Dixell unit. Lol. Daikin and even the manufacturers of mine heat world couldn't tell me how to set it up, what a contraption to put on a heat pump. By the sounds of it it needs to be set up at different target temperatures at different times of the year, there'll be a lot of people out there unaware of this I would of thought. If you press set+down at the same time you can go into the settings (if you dare) as theres a few tweaks you can try, just take pics or something of your original settings. The 1st one that comes up is hy(hysteresis), you can trial bumping that up a bit to stop the secondary pump starting and stopping every 2 mins if that's happening, AC(anti short cycle) increasing that valve forces the compressor to rest for longer, you can also set an offset if you think your buffer temp calibration is different to the heap pumps but I'm not sure what on this one but its called Ot on the menu. I'm by far no expert though, I've just been dropped in it and spent hours and hours trying to find stuff out. I didn't have a moments hassle with my 13 year old baxi boiler, it just did its thing and I did mine, I'm praying @toodles knows his stuff and the Homely system can save me from spending the foreseeable in a straitjacket, I wouldn't mind but I much prefer being cool, the missus is loving all this heat 24/7 heat though, 19.5⁰c seems even her limit though so how you do 22.5⁰c @toodles I'll never know. Lol. Thank you @majordennisbloodnok for your reply too, always good to get your take when you need some top notch advice. Thanks everybody.
Craig
@craigh I refer to our somewhat elevated temperature of 22.5 deg. C as our ‘comfort level’ for good reason; this is the temperature at which both of us are comfortable.
This I think is the result of medical conditions and possibly to a certain extent, our *ages. Though speaking for myself alone, come the summer when we will probably have the global warming ‘Phew, what a Scorcher’ weather again, I will be quite comfortable as I don’t seem to have any problems. My wife finds it a bit on the warm side though, however, we have blinds on all windows; the ability to shut them on the sunny aspects of the house and change these later in the day as the big yellow thing swings round to the south and then west. We manage to keep the house cool enough with judicious use of some fans.😉
*As a youngster, I was happy with 19-20 degrees and when working in precision engineering, this was just as well as all measurements are supposed to be made at 20 deg. C. anyway. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
-
Homely for Daikin Altherma 3 - Petersfield Area
4 months ago
-
Heat pump monitoring
5 months ago
-
Warm weather and heat pumps.
12 months ago
-
Oversized Daikin 9kw
1 year ago
-
alternative to Homely - HavenWise. Anyone used it?
1 year ago
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 613 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
Your topic raises my interest for a couple of reasons. ...
By DavidB , 25 minutes ago
-
@batpred frost protection £632 ??? That is taking t...
By MartinRobinson , 47 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Interesting questions. If the answer to either ...
By ChandyKris , 58 minutes ago
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 8 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 9 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 10 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 12 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 13 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 14 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 16 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 19 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 22 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago