Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Oversized Daikin 9kw
Evening all, I wonder if someone can share any thoughts on my situation?
I sent the below email to Octopus in January which was the first opportunity when I could see how my 9kw Daikin installed last June was performing at or below the design temperature. I'm now in a situation where the Octopus heat loss design estimates my heat loss at ~8.5kw and my own Heat Punk heat loss is 6.6kw with more accurate inputs and air changes (not all rooms in my house have trickle vents on windows, the kitchen doesn't have an extractor which extracts externally etc). The measured heat loss from EmonCMS is ~4-5kw to maintain 21*C at an average outdoor temperature of -4*C. I spoke to Octopus today and they are waiting on MCS to confirm whether 'measured heat loss' is a suitable substitute to the various heat loss calculation methodologies / standards that exist. Having read some of the MCS standards I believe they focus solely on designed heat loss, not measured heat loss (the latter of course being more accurate). Octopus stated today their survey doesn't allow modifying any air changes/hr for each room so they are limited to the standard assumptions (which of course can lead to inaccurate results).
I'd welcome any insights or advice from others - I'd like Octopus to swap the 9kw high capacity unit (which is a software limited 16kw unit) with the 8kw low capacity unit which can modulate down lower to prevent cycling.
Monitoring available here:
"Good evening,
My thoughts are - good luck, you seem to have a reasonable argument for the replacement. That said Im not sure you could prove the current one is unfit for purpose so they may well decline, but worth a go.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks, it's way off of the MCS performance estimate and I think if it ended up in Court I could construct a sound case to justify it's not fit for purpose (based on efficiency, wording on the contract etc)
@big_si As has been mentioned you are not the first with this problem. Several 🐙 clients have had Daikin 9s changed for Daikin 8s. The first was Matt Drummer who is over on OE Monitor.
The 9kw is a 16 kw restricted by software and is famously juicy although there are people running them very efficiently. The restriction means they don't have the modulation range which is a pain.
The 4/6/8 are the same - all are 8s restricted by software but for some reason it doesn't have the same impact. All 3 modulate down very nicely. I have the 6kw Daikin and I am very happy with it. I run it on pure weather compensation and the compressor never turns off and it runs low without complaining or cycling.
Key for you is building a case with evidence so do talk to the other guys over on the OEM forum. Best of luck. 🐙 are pretty good if you make a strong, logical case.
@lucia thanks for the reply, I think I've now got sufficient evidence that it needs replacing particularly OEM data when it was operating at design temperature which I did not have last year when Octopus refused to replace it at my first request. I've since raised with NAPIT and MCS as additional levers. I just want the system to perform as intended and the 9kw isn't meeting expectations in that regard and hopefully Octopus learn from this with future surveys to reduce rework and increase customer satisfaction.
9kw monster swapped with the 8kw unit today - it's whisper quiet and running a treat so far! Well worth persevering with NAPIT as Octopus were reluctant to swap out the 9kw. Had to tweak the EmonCMS flow temperature sensor to before backup heater (as the 8kw doesn't have a backup heater) and updated the details on heatpumpmonitor.org
Looking forward to seeing how it performs next winter 🙂
@big_si thanks for the update. It’s still forecast to be unseasonably chilly for a few more days so you may get some insights. But good to hear you’re happy with the new smaller unit. Keep us updated.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
Homely setup on daikin heat pump
3 months ago
-
Is Your 6kW Air Source Heat Pump Really a 6kW?
1 year ago
-
Warm weather and heat pumps.
1 year ago
-
Is your gut better than Math
1 year ago
-
Daikin COP / energy used measurement from MMI
2 years ago
- 26 Forums
- 2,647 Topics
- 61.8 K Posts
- 1,391 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
MCS aren't involved in commercial a2a installations whi...
By JamesPa , 49 minutes ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Interesting. Perhaps wait and see how things develop! ...
By JamesPa , 52 minutes ago
-
Any readers with an interest in Solar Farm generation i...
By Toodles , 1 hour ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
Yup! Summer in Spring. Wonder if Summer will last unt...
By Majordennisbloodnok , 2 hours ago
-
RE: Solar Produced vs Home Consumed
It's worth adding that if you have a hot water tank and...
By JamesPa , 3 hours ago
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
@editor Sorry Mars, I didn’t see a notification about ...
By Toodles , 4 hours ago
-
RE: Hitachi Heat Pump being replaced with Vaillant
Yes to be configured as a volumiser. The pump is to be...
By trebor12345 , 4 hours ago
-
RE: Anyone concerned about GivEnergy?
So it seems subscription day has finally arrived for Gi...
By TechnoGeek , 6 hours ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 8 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 8 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 21 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago