Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
-20c room temperature on Ecodan with P1 code
That is the target room temperature and if its showing -20C then its not getting a temperature signal from the thermistor.
Are you using the main controller to measure the temperature, i.e. the unit in your image or do you have a wireless controller as well?
If you are using the main controller go to initial settings, then into room sensor settings, sensor settings and it should show MAIN RC, if its showing something else then that is what you have changed and its needs changing back to MAIN RC.
@gary Firstly thanks for you reply. Iv been in a bit of a panic as apparently I fiddle too much according the the better half and that one day I’m genna muck something up😉
I do have a wireless controller that I control the room temperature from and I’m using auto adapt.
When browsing through the settings I’m sure it was on TH1 but I have this morning tried already the MAIN RC and right now everything seems fine.
Watch this space!!👍
And fair play to Mitsubishi support as they’ve already replied to my email from last night with the reply below.
A P1 error where the controller is looking for a sensor which doesn’t exist on the system, it’s a default setting which normally takes place if there has been a power cut
Carry out a power reset on the system to clear the fault from the indoor & outdoor unit
Power reset here
Ask the caller
What is controlling the Zone? The main controller, 3rdparty controller, Mitsubishi wireless stat or a thermistor (A thermistor is a cable which is connected to the system to read the temperature)
- Press and hold the POWER/HOLIDAY button in the bottom right hand corner of the Mitsubishi controller until SYSTEM SHUTDOWN comes up and select YES
- Press the bottom left MENU button
- Using the directional arrows highlight the INITIAL SETTINGS icon and select with the TICK button
- Scroll down to the option ROOM SENSOR SETTING and select with the tick button
- Select the SENSOR SETTING in the options with the tick button
If it’s a 2 zone set up, an extra setting will show up here to select which zone
- Select the SENSOR SETTING option with the tick button
- Change the sensor option by pressing the cycle button until it displays either
MAIN RC – If using the main controller or any third party thermostats
ROOM RC (1 to 8) – If using a Mitsubishi wireless thermostat
TH1 – If using a thermistor (This will default after a power cut, we don’t normally use it in the UK)
- Confirm using the TICK button
- Once confirmed use the back button to exit the menu and turn the system back on with the Power/briefcase button
- Make sure the heating mode is correct Changing Heating Modes
If the ROOM RC isn't there, it needs dipswitch SW1-8 by your installers. If that’s on go into ROOM RC Select and make sure the appropriate zone is selected
If you have a Mitsubishi wireless controller then it should be set to Room RC not Main RC, if you use Main RC it will now be using the main controller's temperature to control the house temp where as before it sounds like it was using the wireless controller.
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,066 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 3 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 17 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago