Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
In light of the recent buffer tank/warranty comments in this topic, I’ve written this piece below. It’s a 10 minute read, but I think it warrants a dedicated video/podcast, because there’s a lot of ambiguity and grey areas here that need clarification.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@potatoman As no one seems to be obliging, I attach a diagram. The idea is that only bypass flow goes through the tank when necessary so it is undisturbed by main flow. Connection to tank must be closely coupled.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heatgeek is it that this design satisfies the manufacturers? its still (although balance by bypass) a double hydronic volumiser/buffer with 2 pumps
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba I am afraid that you are talking to the wrong person about manufacturers preferences. However, as far as I can see, it functions the same as a 4 port buffer except that flow doesn't go through the top of the tank causing mixing, therefore I would have thought that it is a perfectly acceptable alternative to a 4-port.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heatgeek Oh agreed, its a slightly better and slightly less resistive solution, perhaps even the middle ground of no buffer V buffer.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@potatoman hi, the scheme detailed is 2 pumps, one for the ASHP (primary) and 1 for the secondary circuits.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@potatoman No, the installation is exactly the same as a 4 port buffer with primary and secondary pumps except that the output flow bypasses the top of tank so as not to disturb the stratification of the tank. This removes some of the inefficiency problems associated with 4 port buffer tanks, like output temperature being reduced by mixing.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Note a key point here though. The primary pump is connected in the return pipe while the secondary pump is connected in the flow pipe after the buffer tank to provide good hydronic separation between the primary and secondary pumps.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Only the difference in flow between the heat pump and the emitters passes through the tank. This lower flow helps to preserve the stratification of the tank so that dilution of temperature to the emitters is minimised.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Apologies. Poor choice of words. Delete "dilution of temperature to emitters is minimised".
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @heatgeekNote a key point here though. The primary pump is connected in the return pipe while the secondary pump is connected in the flow pipe after the buffer tank to provide good hydronic separation between the primary and secondary pumps.
That all sounds very believable. Presumably mixing of return water with flow water to the emitters (and thus a reduction of ft to emitters) will however still occur if the primary pump throughput is less than the secondary, so the requirement to set up properly remains albeit that it is less sensitive than a 4 port.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Hot water tank lose heat rapidly on random days
3 weeks ago
-
Heat pump done right first time? Installation in Kent.
3 weeks ago
-
British Gas Heat Pump Installation Complaint
5 months ago
-
Heating Turned Off but Radiators Still Warm
6 months ago
-
Samsung Heat pump with Yonos Pico circulating pump running all the time
6 months ago
Currently viewing this topic 5 guests.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 947 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 6 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 10 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 12 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 12 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 15 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 21 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 21 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago