Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
In light of the recent buffer tank/warranty comments in this topic, I’ve written this piece below. It’s a 10 minute read, but I think it warrants a dedicated video/podcast, because there’s a lot of ambiguity and grey areas here that need clarification.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@potatoman As no one seems to be obliging, I attach a diagram. The idea is that only bypass flow goes through the tank when necessary so it is undisturbed by main flow. Connection to tank must be closely coupled.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heatgeek is it that this design satisfies the manufacturers? its still (although balance by bypass) a double hydronic volumiser/buffer with 2 pumps
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba I am afraid that you are talking to the wrong person about manufacturers preferences. However, as far as I can see, it functions the same as a 4 port buffer except that flow doesn't go through the top of the tank causing mixing, therefore I would have thought that it is a perfectly acceptable alternative to a 4-port.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heatgeek Oh agreed, its a slightly better and slightly less resistive solution, perhaps even the middle ground of no buffer V buffer.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@potatoman hi, the scheme detailed is 2 pumps, one for the ASHP (primary) and 1 for the secondary circuits.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@potatoman No, the installation is exactly the same as a 4 port buffer with primary and secondary pumps except that the output flow bypasses the top of tank so as not to disturb the stratification of the tank. This removes some of the inefficiency problems associated with 4 port buffer tanks, like output temperature being reduced by mixing.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Note a key point here though. The primary pump is connected in the return pipe while the secondary pump is connected in the flow pipe after the buffer tank to provide good hydronic separation between the primary and secondary pumps.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Only the difference in flow between the heat pump and the emitters passes through the tank. This lower flow helps to preserve the stratification of the tank so that dilution of temperature to the emitters is minimised.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Apologies. Poor choice of words. Delete "dilution of temperature to emitters is minimised".
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @heatgeekNote a key point here though. The primary pump is connected in the return pipe while the secondary pump is connected in the flow pipe after the buffer tank to provide good hydronic separation between the primary and secondary pumps.
That all sounds very believable. Presumably mixing of return water with flow water to the emitters (and thus a reduction of ft to emitters) will however still occur if the primary pump throughput is less than the secondary, so the requirement to set up properly remains albeit that it is less sensitive than a 4 port.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Microbore heat pump installs
2 weeks ago
-
Hot water tank lose heat rapidly on random days
3 weeks ago
-
Heat pump done right first time? Installation in Kent.
2 months ago
-
British Gas Heat Pump Installation Complaint
6 months ago
-
Heating Turned Off but Radiators Still Warm
7 months ago
Currently viewing this topic 4 guests.
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 896 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
Hi @ian33a you could do your own heat loss calculation ...
By Judith , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@djh ah, I have never seen this before, interesting ide...
By ASHP-BOBBA , 4 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 5 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa — this version may be marginally better: &nb...
By cathodeRay , 7 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 8 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 13 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 15 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 17 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 20 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 20 hours ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
That would be abnormal but I cant see from your charts ...
By JamesPa , 20 hours ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago