Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Why Buffer Tanks & Low-Loss Headers Can Sabotage Your Heat Pump's Efficiency
@ch_18, welcome to the forums.
On the principle first: converting a 4-port buffer into a 2-pipe volumiser on the return is a logical step if your goal is to reduce mixing losses and improve emitter temperature consistency.
On your question about port orientation, in a true volumiser configuration (not decoupled) you’re not trying to achieve stratification in the same way as a buffer. So keeping both the emitter return and the heat pump return on the lower ports can be acceptable, provided the flow path through the vessel is continuous and you’re not inadvertently short-circuiting the top section.
In practice, like @judith alluded to, this is the more conventional way of plumbing in a volumiser.
On the pump question, a 7 kW Vaillant’s internal pump is generally capable of handling a typical single open circuit system provided the hydraulic resistance is reasonable. The fact that it’s currently circulating 1200 litres (I assume you mean system volume, not flow rate) is less relevant than the required flow rate and head. What's important here is whether, once you remove the secondary pump and decoupling effect of the buffer, the internal pump can achieve the required design flow at the actual system resistance. If it can't, you'll drown in flow errors.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editorSo keeping both the emitter return and the heat pump return on the lower ports can be acceptable, provided the flow path through the vessel is continuous and you’re not inadvertently short-circuiting the top section.
Without doing some horrendous modelling, or fabricating some transparent tanks, I would think that there is quite a significant risk that the upper section is effectively short circuited if both connections are at the bottom, particularly if the erstwhile buffer tank was designed to encourage stratification.
There will be some turbulence of course, and a bit of a convection current (hopefully not much if the tank is well insulated) but not a lot really to stir it up. So personally I would go in at the top and out at the bottom even if it makes the plumbing more difficult.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@editor Thanks for the reply. Yeah I thought in at the top, out of the bottom would be the best solution for converting to volumiser but was hoping to minimise repiping, just incase it doesn't work for example if the internal heat pump circulation pump can't cope.
If you look, I have a spare 2 ports on the left hand side of the buffer. One is about 2/3 of the way up. Would this be a better option? Or does it have to go to the top nozzle?
I have 2 circuits, both open loop. One is supplying approx 120m2 of UFH circuits and the other is supplying upstairs (2 floors) of rads? You think the pump would struggle supplying enough flow?
Thanks again
-
Hypothetical House Design
2 weeks ago
-
Heat pump done right first time? Installation in Kent.
1 month ago
-
Microbore heat pump installs
3 months ago
-
Hot water tank lose heat rapidly on random days
3 months ago
-
British Gas Heat Pump Installation Complaint
9 months ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,716 Topics
- 63.6 K Posts
- 421 Online
- 7,116 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
For cooling a whole building, or even a big room with l...
By EtchedPixels , 10 minutes ago
-
This 'story' is indeed fast moving. NESO has just rel...
By Transparent , 12 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
The updated draft seems to be fairly good although I th...
By EtchedPixels , 14 minutes ago
-
RE: Comms and power cabling to outside unit
@old_scientist 100%, the cover is for warrantied unit...
By Papahuhu , 28 minutes ago
-
I don't remember the manufacturer name, but I saw simil...
By bobflux , 2 hours ago
-
RE: Weather compensated secondary circuits with Biomass
UFH is ideal to get max efficiency with a heat pump, bu...
By bobflux , 2 hours ago
-
RE: Vaillant Arotherm Pro vs new Plus
when our system was installed in September 2 years ago ...
By Judith , 17 hours ago
-
RE: Rate the quality of your heat pump design and installation
I had a Heat Geek lead install by Green Heat Norfolk. T...
By Orlando , 1 day ago
-
RE: Mitsubishi Ecodan FTC6 settings
While @F1p's dongles are great, the FTC can do this its...
By RobS , 2 days ago
-
RE: Samsung heat pump - data cable issue
If it's a data cable, current will be minuscule, voltag...
By bobflux , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
I got hit with an RHI audit in 2022. It was far from c...
By Abernyte , 2 days ago
-
RE: Electricity price predictions
@papahuhu Groucho Marx had something to say about no...
By Toodles , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa haha very true, although the engineer yesterda...
By swwils , 2 days ago
-
RE: What a difference a few degrees make.
Wow. Having accepted the challenge, I ran the cold tap ...
By Old_Scientist , 3 days ago