Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @kevhPosted by: @editor@swwils I guess the true test will be November/December when it cranks up to run full speed.
To be fair to Octopus, TJ is quoted as advising that hush mode is not appropriate to peak demand season. 😀
If it's like every other quiet/night/noise reduction/silent/hush mode, it simply limits compressor modulation and/or fan speed. This reduces max output. Thus if your heat pump needs to operate at or near max at times, it's not suitable for these times.
As a concrete example I use low noise mode on my Valiant, but its programmed to apply at night only. It's a courtesy to the neighbours as the heat pump can get a bit noisy immediately after defrost, although I'm far from sure the courtesy in necessary because I doubt they can hear it given that they will have the windows closed whenever its cold and damp enough for defrost to be necessary.
If it's -temps outside the house cools by about a degree overnight, because it can't recover from defrost as fast as it normally would. It takes a few hours to recover completely during the morning once noise reduction turns off at 7am. I could compensate by overheating early evening, but the cooling is not enough to bother. The rest of the season low noise mode makes no noticeable difference to the performance.
For me this is very acceptable. It's impossible to give definitive instructions that will suit everyone because it will vary from house to house. For many houses with a heat pump that is oversized low noise will work throughout the season, for others like mine where it is critically sized it does cause a hit at the height of the season. If you remain aware what it actually does then you can adapt accordingly!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @andrewjPosted by: @kevhPosted by: @editor@swwils I guess the true test will be November/December when it cranks up to run full speed.
To be fair to Octopus, TJ is quoted as advising that hush mode is not appropriate to peak demand season. 😀
To be fair to Octopus customers, it would be better if we could get detailed information from a more official channel and less cryptic source than a Social Media manager on Facebook. I appreciate that he helps resolve service problems but it’s frustrating that we can’t get more info from technical sources - it would help if there was consistency of advice as well.
And that is precisely the point I have made following a couple of TJ's pearls of wisdom on FB.
There WAS an official email issued, setting out that hush mode was merely a reduced output mode, and therefore of little value in winter. Ironically of course it is in winter when the pump is at its noisiest.
I am totally with you on the lack of a decent and comprehensive user interface.
Posted by: @andrewjPosted by: @kevhPosted by: @editor@swwils I guess the true test will be November/December when it cranks up to run full speed.
To be fair to Octopus, TJ is quoted as advising that hush mode is not appropriate to peak demand season. 😀
To be fair to Octopus customers, it would be better if we could get detailed information from a more official channel and less cryptic source than a Social Media manager on Facebook. I appreciate that he helps resolve service problems but it’s frustrating that we can’t get more info from technical sources - it would help if there was consistency of advice as well.
And that is precisely the point I have made following a couple of TJ's pearls of wisdom on FB.
There WAS an official email issued, setting out that hush mode was merely a reduced output mode, and therefore of little value in winter. Ironically of course it is in winter when the pump is at its noisiest.
I am totally with you on the lack of a decent and comprehensive user interface.
Posted by: @kevhThere WAS an official email issued, setting out that hush mode was merely a reduced output mode, and therefore of little value in winter. Ironically of course it is in winter when the pump is at its noisiest.
That is what everybody else's hush/quiet mode is so almost certainly, they cant do magic!. See my comments above on how I successfully use Vaillant's equivalent in winter which as you say is when its needed. House dependent unfortunately
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @kevhThere WAS an official email issued, setting out that hush mode was merely a reduced output mode, and therefore of little value in winter. Ironically of course it is in winter when the pump is at its noisiest.
That is what everybody else's hush/quiet mode is so almost certainly, they cant do magic!. See my comments above on how I successfully use Vaillant's equivalent in winter which as you say is when its needed. House dependent unfortunately
Yes, totally understand how you can manage the Vailant, and that output reduction is commonplace, it makes total sense. I like how you utilise it.
Octopus will catch up sooner rather than later. With a Cosy, hush mode is a simple on/off option, with no scheduling possible.
Which means that it can't be set for overnight use unless one sets a bedside alarm ⏰
i am not overly critiquing Octopus here, they do have room to improve the operability of the Cosy and it is promising that these little tweeks (remember the liwering of the minimum flow temperature a couple of months back) are introduced.
Posted by: @kevhWith a Cosy, hush mode is a simple on/off option, with no scheduling possible.
Ah, not so useful then
Posted by: @kevhOctopus will catch up sooner rather than later.
For sure, hopefully before next winter!
On the Vaillant, programming NR mode (both on/off and hours of operation) is an installer level option. I think this 'decision' varies from manufacturer to manufacturer. I can understand the reluctance to make it a user option given the side-effect. Fortunately the installer password in 00, pre-programmed into the interface.
There is even the option (buried deeper in installer mode) to change the magnitude of the limit. The range you can select is itself limited though, ideally I would like to reduce the output and noise by less than the minimum reduction permitted (ie make the effect less severe), but this is not possible and not likely to be possible because, unlike Octopus, Vaillant dont do remote firmware updates.
It will be costing me a bit (when it actually affects house temperature) to run NR mode at night, because it means that it will have to work harder in the morning to catch up. It also displaces use from nighttime to daytime tarrif. However in practice its only for a few days each season that the overnight cooling effect occurs so Im not too bothered.
Lets hope Octopus implement timed NR mode soon.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Octopus emailed though a new cosy guide that has way more info that might satisfy people here.
It says hush mode caps compressor and fan at 60% so to get 8.3kW heat out is quite the achievement.
@swwils sounds interesting. Would be interested to see this. Can you email it to me?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
I have had my Cosy 9 installed and running for a year on 8th May. My house, to recap, is a Finnish timber frame design, 164sqM, detached over two floors with a total of 15 heated spaces (11 rooms and 4 open plan, distinct spaces.) Even though it's 1980s technology it is designed for their winters (good wall insulation and under floor insulation) and has been upgraded with 300mm loft insulation, 0.7u triple glazing throughout, and PassivHaus standards external doors. One thing I think it may suffer from is a lack of thermal mass compared to more traditional builds. All internal walls are plasterboard stud walls; external walls are similarly plasterboard on the internal face with insulation then, I suspect, some form of weatherboard followed by timber or brick cladding for aesthetics. There is no block or brick work internally and my impression is that the walls tend not to radiate much heat so it's the air that carries the comfort.
These are the figures for the year:
SPF (SCOP): 3.91
Input Power: 3.39 MWh
Output Power: 12.88MWh
I think the headline takeaway I have is that these figures are pretty good. First season so it needed tuning in and this thread highlights some of the issues I've had. The design as presented by Octopus was for a SCOP of 3.6 at a variety of room temps (supposed MCS required temps) with a heat loss of 8.5kW and a flow temp of 50c at -3.2c.
Overall, I would say I'm mostly happy:
- we haven't been cold through the winter and have maintained temps at 22c or above (and early days, very above!) which suits my wife very well.
- Octopus service has been (mostly) good. Sometimes a little slow to respond but they did engage with the overheating problem and with radiator replacement for two rooms that were incorrectly sized.
- Installation was great although they didn't allow the team enough time to do it in one visit. Certainly no real problems and redecorating was minimal - really just painting copper pipes which they adjusted for larger radiators.
- The price of £6.5k seemed reasonable for the installation given it involved taking out a radiator and changing 14. Anyway, Heat Geek wanted me to stump up £18.5k for the same job!
It's not perfect though:
- Although we maintained temperatures, I'm disappointed that Octopus install with a thermostat and have it running under the same approach as for a gas boiler. So, one small area of the house is "at temp" whilst the rest of the house warm and cool based on that area's heat loss. This specifically was a problem I wanted to do away with by installing an ASHP. I don't truly understand their thinking behind this approach - they state running costs - and especially their argument that involves wording along the lines of "when the house reaches temperature the Cosy turns off": clearly "the house" doesn't reach temperature, one small area of it does.
- Control was very difficult. With the thermostat in the living area, the rest of the house was either too cold or too warm. I found that placing the thermostat in the downstairs toilet, the smallest room in the house with two outside walls and a small window, allowed for the "best" control. However, control wouldn't be the best term: I could set the required temperature to be 19c, 20c, 21c (and I would guess any temp) and regardless, the rest of the house was maintained at 22c - 23c. In other words, it would seem the rate of heat loss of the downstairs toilet is sufficiently high that regardless of the called for temperature the Cosy would operate enough that a nice stable temperature was maintained elsewhere in the house. I have had to turn down 3 TRVs and put a decorators cap on another; most, if not all, of the radiators have their LSVs set to about half a turn. The landing radiator never comes on because its always too warm in that space (it does work, we were reaching 26c with the TRV fully open.)
- It's extremely difficult to speak to someone technical to help work through problems, despite asking. I'm pretty sure that I could tune this better with that sort of input. It's needed because the amount of data we have access to as customers is extremely limited: OAT, Input Power and Output Power on an aggregated or averaged hour basis.
- The heat loss survey was redone and was calculated at 7.5kW, so -1kW over the original calculation. A new radiator schedule was generated which gave a total heat output of +1kW over the original schedule. So basically, my heat loss reduces but heat output increases, and the re-survey was undertaken because the house was overheating! I queried whether anyone sanity checked this but got no answer. I've sort of lost trust in them a bit to be honest, especially as the general feeling is that they are overly pessimistic with the heat loss calculation.
- They won't share the data used behind the heat loss calculation so it's not possible to perform a sanity check based on gas usage say (I had no inclination to get to grips with heat loss software.)
- The whole ASHP experience is a science project for the home owner and it shouldn't be - this is an industry issue not an Octopus one though. I spent around 3 months trying to get this system operating to a point where we weren't too hot before calling it a day for this year. I feel sorry for homeowners who are less able to do this.
The future:
Anyone who has followed this thread may remember that I was able to make an adjustment so the flow temperature is 50 at -10c, further pointing to an incorrect heat survey. Subsequently, Octopus have changed their app to allow Cold Temp WC control to be set down to 46c at -10c and have added a quiet mode. When next season rolls around I still want to get this running without thermostatic influence, purely on WC, something I couldn't do this season because I couldn't adjust the WC low enough until too far through. I feel it should be possible given the ease at which the Cosy was able to raise IAT to 22c and it ought to make it even more comfortable and more efficient.
@andrewj i refused a daikin 8kW as it was over powered for the heat loss calcs I did
their calcs were 20% higher until I challenged them to redo them.
they got 2 radiators transposed as the survey numbered the bedrooms opposite to the way they were used.
i swapped 2 radiators and fixed their issue, easier than battling the press 1 for idiots or 2 for numpties
i turned every TRV to full open and ran the system full on and turned down the lock valves until the output of each radiator matched the heat loss of the room.
took around 2 months tweaking to get a balance
i run it with a master cosy pod in the lounge and a slave pod in the master bedroom
ive been improving the insulation for the past 6 months and have 1 final stretch of outside wall to add 50mm of rockwool to to make the lounge/kitchen cosy; it’s currently 1C under temp but i can cope with that as i don't have a fussy partner that cant put a sweater on :-
my cop has improved from 3.5 to 4.8, and the UFH is best thing to have paired with a heat pump
G
I am seeing a cop of 5.44 at 33C flow at 11C outside on my cosy 9. The latest round of updates and hush mode have really settled it in far more than previously.
I do see the logic in oversizing these, I'm glad I have the 9.
Overall this is fantastic, sorry I haven't posted much, but I do feel like I need to post to say it's great, in order to give other people the confidence, especially if you are comming from an oversized boiler.
In reality numbers/stats mean not as much as people think and decisions are made on if someone else has it working well, which is the case here 👍.
- 26 Forums
- 2,643 Topics
- 61.7 K Posts
- 75 Online
- 7,043 Members
Join Us!
Latest Posts
-
Mentally you have to separate the ac side and the DC si...
By JamesPa , 3 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 5 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 12 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
Hopefully the ambient temperature sensor drives a weath...
By JamesPa , 1 day ago
-
RE: How many people are happy with their ASHP and do you believe them?
Im looking into these and my figures. The think that I...
By JamesPa , 1 day ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 1 day ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
Yes - we use our Mitsi 14kW unit for cooling. I have j...
By downfield , 1 day ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 1 day ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 2 days ago
-
Hard to tell but I think I have placed the arrow on wha...
By ASHP-BOBBA , 2 days ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Great. My guess is that you will need to re-adjust yo...
By JamesPa , 2 days ago
-
RE: UK warm homes plan - how can it be delivered?
I know it is not as simple as going from a fossil fuel ...
By Batpred , 3 days ago
-
@editor this is great news.
By ASHP-BOBBA , 4 days ago
-
RE: Daikin Altherma 3 with Fan Coils in Puglia (Italy)… Sanity Check on System Operation
AH (Absolute humidity) is grams of moisture per volume ...
By bobflux , 4 days ago